<div>On some models, I have had quite a few warning messages, such as "space XX might have insufficient heating capacity" where the space in question was modeled with the design heating equipment and showed no unmet hours.  For warnings like this, I usually include a little explanation in the LEED documentation stating "XX warnings are of the form: 'space may have insufficient heating capacity'  As the space shows no unmet load hours, we feel that this is ok..."<br>
</div>
<div>But, if your windows aren't on the correct wall, this could be a problem.  Look at the warnings though, it could be that your glass and frame area is larger than the actual wall area, so the issue may not be position, but size.</div>

<div> </div>
<div>--</div>
<div>Karen</div>
<div><br> </div>
<div class="gmail_quote">On Wed, Sep 22, 2010 at 1:26 PM, Jeff Seger <span dir="ltr"><<a href="mailto:Jeff.Seger@megroup.com">Jeff.Seger@megroup.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-US" vlink="#606420" link="blue">
<div>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt">Omar,</span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt"> </span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt">As long as your window dimensions and floor to floor/floor to ceiling heights are correct,  AND you document the warnings in a comments section, LEED reviewers should be OK with it, though it could depend on the warning.  What does it say exactly?</span></p>

<div>
<p class="MsoNormal"><b><span style="COLOR: black; FONT-SIZE: 10pt"> </span></b></p>
<p class="MsoNormal"><b><span style="COLOR: black; FONT-SIZE: 10pt">Jeff Seger  </span></b><b><span style="LETTER-SPACING: 1.2pt; COLOR: #4a9054; FONT-SIZE: 9pt">EI</span></b><b><span style="COLOR: #006086; FONT-SIZE: 10pt"></span></b></p>

<p class="MsoNormal"><b><span style="COLOR: black; FONT-SIZE: 10pt">M.E. GROUP </span></b><b><span style="COLOR: black; FONT-SIZE: 8pt">/</span></b><b><span style="COLOR: black; FONT-SIZE: 10pt"> </span></b><b><span style="LETTER-SPACING: 1.2pt; COLOR: #006086; FONT-SIZE: 9pt">design</span></b><b><i><span style="LETTER-SPACING: -1.4pt; COLOR: #1f497d; FONT-SIZE: 9pt"> </span></i></b><b><span style="LETTER-SPACING: -1.4pt; COLOR: black; FONT-SIZE: 6.5pt">+</span></b><b><i><span style="LETTER-SPACING: 1.2pt; COLOR: #1f497d; FONT-SIZE: 6.5pt"> </span></i></b><b><span style="LETTER-SPACING: 1.2pt; COLOR: #4a9054; FONT-SIZE: 9pt">green</span></b><b><span style="COLOR: black; FONT-SIZE: 10pt"></span></b></p>

<p class="MsoNormal"><span style="COLOR: black; FONT-SIZE: 10pt">t: 816.531.2121 x3123</span></p>
<p class="MsoNormal"><span style="COLOR: black; FONT-SIZE: 10pt">c: 314.623.5170</span></p>
<p class="MsoNormal"><a href="http://www.megroup.com/" target="_blank"><span style="COLOR: #1f497d; FONT-SIZE: 10pt; TEXT-DECORATION: none"><img border="0" alt="LOGO_COMBINEDb" width="175" height="54"></span></a><span style="COLOR: #1f497d; FONT-SIZE: 10pt"></span></p>
</div>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt"> </span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt"> </span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt"> </span></p>
<div>
<div style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">From:</span></b><span style="FONT-SIZE: 10pt"> Omar Katanani [mailto:<a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a>] <br><b>Sent:</b> Wednesday, September 22, 2010 11:08 AM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] A lot of warning messages!</span></p></div></div>
<div>
<div></div>
<div class="h5">
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB">Dear all,</span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB"> </span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB">I have 248 warning messages and most of them are due to the position of windows. I honestly do not want to correct every single window!</span><span lang="EN-GB"></span></p>

<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB"> </span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB">Will the LEED reviewers comment on this? My model is running perfectly with reasonable numbers (I have 0 errors).</span><span lang="EN-GB"></span></p>

<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB"> </span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB">Many thanks!</span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB">Omar</span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="FONT-SIZE: 10pt" lang="EN-GB"> </span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB">___________________________</span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB">Omar Katanani<br>Sustainable Design Engineer</span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB">Email: <a href="mailto:omar@ecoconsulting.net" target="_blank">omar@ecoconsulting.net</a></span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy" lang="EN-GB"> </span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 7.5pt">EcoConsulting (Lebanon)</span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 7.5pt">Nahas Building, 4<sup>th</sup> floor</span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 7.5pt">4 St-Maron Street / Georges Haddad Avenue</span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 7.5pt">Postal Code: 2028 5806 SAIFI</span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 7.5pt">Beirut, Lebanon</span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 7.5pt">Tel:          </span><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-GB">+961 (0) 1 971 266<br>Mobile:    +961 (0) 3 045 045</span><span lang="EN-GB"></span></p>

<p class="MsoNormal"><span lang="EN-GB"> </span></p>
<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-GB">EcoConsulting (UK) Ltd<br>28 Marshalsea Road<br>London, SE1 1HF<br>Tel:  +44 (0) 207 939 0989<br>Fax:  +44 (0) 207 939 0981</span><span lang="EN-GB"></span></p>

<p class="MsoNormal"><span style="COLOR: navy; FONT-SIZE: 7.5pt" lang="EN-GB">Website: <a href="http://www.ecoconsulting.net/" target="_blank">www.ecoconsulting.net</a></span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span lang="EN-GB"> </span></p>
<p style="MARGIN: 0in 0in 0pt"><span style="COLOR: navy; FONT-SIZE: 10pt" lang="EN-GB"> <img border="0" width="870" height="102"></span><span lang="EN-GB"></span></p>
<p class="MsoNormal"><span lang="EN-GB"> </span></p></div></div></div><br>
<hr>
<font color="gray" size="1" face="Arial">CONFIDENTIALITY NOTICE: This e-mail and any attached file(s) are intended only for the use of the individual or entity to whom or to which it is addressed and may contain information that is privileged, confidential, proprietary, and trade secret. If the reader of this message is not the intended recipient or an employee or agent responsible for delivering the message to the intended recipient, you are hereby notified that any dissemination, distribution, or reproduction of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately and discard the original message and any attachment(s).<br>
</font></div><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>