<div>Make two modeled chiller and pump combinations in eQuest, one that will match your summer operating strategy, and use a second chiller and pump combination to match your winter strategy. The modeled chiller in each combo will reflect your actual chiller under those conditions.</div>
<div> </div>
<div>You can either allow equest to decide when each would run, or else schedule them to be available seasonally if that would more accurately reflect the actual use.</div>
<div> </div>
<div>David</div>
<div><a href="http://www.grummanbutkus.com/">http://www.grummanbutkus.com</a></div>
<div><br><br> </div>
<div class="gmail_quote">On Thu, Sep 16, 2010 at 9:44 AM, <span dir="ltr"><<a href="mailto:Michael.C.Allison@jci.com">Michael.C.Allison@jci.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote"><br><font size="2" face="sans-serif">Can a model be developed for one chiller that has two primary pumps. 20 hp runs summer and 5 hp runs winter. If so how<br>
</font><font size="3"></font><font size="2" face="sans-serif"><br></font><font size="3"></font>
<p></p>
<table>
<tbody>
<tr>
<td valign="top">
<td valign="top"><font size="1" face="Arial"><b>Michael Allison, CEM, CEA, LEED AP</b></font> <br><font size="1" face="Arial">Energy Solutions Development Engineer</font> <br><font size="1" face="Arial">Building Efficiency</font> <br>
<font size="3"> </font> <br><font color="#002f80" size="1" face="Arial"><b>Johnson Controls </b></font><br><font size="1" face="Arial">Southeast Energy Solutions Group</font> <br><font size="1" face="Arial">Tallahassee, Florida 32308</font> <br>
<font size="1" face="Arial">Cell : 850-210-2952</font> <br><font size="1" face="Arial">Email : </font><a href="mailto:michael.c.allison@jci.com" target="_blank"><font color="blue" size="1" face="Arial"><u>michael.c.allison@jci.com</u></font></a><font size="1" face="Arial"> </font><br>
<font size="1" face="Arial">URL : </font><a href="http://www.johnsoncontrols.com/" target="_blank"><font color="blue" size="1" face="Arial"><u>http://www.johnsoncontrols.com/</u></font></a>
<td><font size="3"> </font>
<p><font size="3"> </font></p></td></td></td></tr></tbody></table><br>
<p><font size="3" face="Times New Roman"> </font> <br>
<p></p>
<p></p>
<p></p><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></p></blockquote></div><br>