<table cellspacing="0" cellpadding="0" border="0" ><tr><td valign="top" style="font: inherit;"><DIV>Hi Carol,</DIV>
<DIV> </DIV>
<DIV>I have attached two inp files, one for Air cooled condenser model with EER 9.9 and another one for Evap Cooled condenser with EER 11.</DIV>
<DIV> </DIV>
<DIV>I created these files with eQuest Wizard mode. If you move forward to detailed mode, you will find "Cooling Electric Input Ratio" is 0.2911 btu/btu in EER 9.9 model and 0.2580 btu/btu in EER 11 model. </DIV>
<DIV> </DIV>
<DIV>If you run simulation, the result for EER 9.9 air cooled model is $242,752 and for evap Cooled model is $243,127. (I did not change the data on "Cooling Electric Input Ratio".)</DIV>
<DIV> </DIV>
<DIV>If I change the data in the field of "Cooling Electric Input Ratio" as 0.3444 for EER 9.9 air cooled model and 0.3100 for EER 11 evap cooled model. The result is $245,342 for EER 11 Evap cooled model and $244,726 for EER 9.9 Air Cooled model.</DIV>
<DIV> </DIV>
<DIV>The conclusion is EER 11 evap cooled model is worse than EER 9.9 air cooled model.</DIV>
<DIV> </DIV>
<DIV>Can you help figure it out?<BR></DIV>
<DIV>Best regards,</DIV>
<DIV> </DIV>
<DIV>James</DIV>
<DIV> </DIV>
<DIV>I believe that there are many Guru in the web. Thanks for your time!</DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV><BR>--- On <B>Sun, 9/12/10, Carol Gardner <I><cmg750@gmail.com></I></B> wrote:<BR></DIV>
<BLOCKQUOTE style="BORDER-LEFT: rgb(16,16,255) 2px solid; PADDING-LEFT: 5px; MARGIN-LEFT: 5px"><BR>From: Carol Gardner <cmg750@gmail.com><BR>Subject: Re: [Equest-users] Question on eQuest Modeling DX Cooling, with Bug?<BR>To: "Guoguang Le" <jamesle_tx@yahoo.com><BR>Cc: equest-users@lists.onebuilding.org<BR>Date: Sunday, September 12, 2010, 9:11 PM<BR><BR>
<DIV id=yiv2112753993>Not likely. Send a copy of your .inp and .pd2 files for help.<BR><BR>Carol<BR><BR>
<DIV class=yiv2112753993gmail_quote>On Sun, Sep 12, 2010 at 6:10 PM, Guoguang Le <SPAN dir=ltr><<A href="http://us.mc501.mail.yahoo.com/mc/compose?to=jamesle_tx@yahoo.com" rel=nofollow target=_blank ymailto="mailto:jamesle_tx@yahoo.com">jamesle_tx@yahoo.com</A>></SPAN> wrote:<BR>
<BLOCKQUOTE style="BORDER-LEFT: rgb(204,204,204) 1px solid; MARGIN: 0pt 0pt 0pt 0.8ex; PADDING-LEFT: 1ex" class=yiv2112753993gmail_quote>
<TABLE border=0 cellSpacing=0 cellPadding=0>
<TBODY>
<TR>
<TD vAlign=top>
<DIV><BR>To all,</DIV>
<DIV>I have two energy models on DX cooling for a same building, one is with air cooled and another with evaporation cooling. The EER is 9.9 for air cooled condenser and 11 for evaporation cooled condenser. The final result I got is that it is the low cost to run air cooled condenser DX with EER 9.9 than evaporation cooled condenser DX with EER 11. I am wondering whether eQuest has bug or not. Anyone could figure it out?</DIV>
<DIV>Best regards,</DIV>
<DIV>James</DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV><BR>--- On <B>Sun, 9/12/10, <A href="http://us.mc501.mail.yahoo.com/mc/compose?to=equest-users-request@lists.onebuilding.org" rel=nofollow target=_blank ymailto="mailto:equest-users-request@lists.onebuilding.org">equest-users-request@lists.onebuilding.org</A> <I><<A href="http://us.mc501.mail.yahoo.com/mc/compose?to=equest-users-request@lists.onebuilding.org" rel=nofollow target=_blank ymailto="mailto:equest-users-request@lists.onebuilding.org">equest-users-request@lists.onebuilding.org</A>></I></B> wrote:<BR></DIV>
<BLOCKQUOTE style="BORDER-LEFT: rgb(16,16,255) 2px solid; PADDING-LEFT: 5px; MARGIN-LEFT: 5px"><BR>From: <A href="http://us.mc501.mail.yahoo.com/mc/compose?to=equest-users-request@lists.onebuilding.org" rel=nofollow target=_blank ymailto="mailto:equest-users-request@lists.onebuilding.org">equest-users-request@lists.onebuilding.org</A> <<A href="http://us.mc501.mail.yahoo.com/mc/compose?to=equest-users-request@lists.onebuilding.org" rel=nofollow target=_blank ymailto="mailto:equest-users-request@lists.onebuilding.org">equest-users-request@lists.onebuilding.org</A>><BR>Subject: Equest-users Digest, Vol 30, Issue 19<BR>To: <A href="http://us.mc501.mail.yahoo.com/mc/compose?to=equest-users@lists.onebuilding.org" rel=nofollow target=_blank ymailto="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</A><BR>Date: Sunday, September 12, 2010, 2:03 PM<BR><BR>
<DIV>Send Equest-users mailing list submissions to<BR> <A href="http://us.mc501.mail.yahoo.com/mc/compose?to=equest-users@lists.onebuilding.org" rel=nofollow target=_blank>equest-users@lists.onebuilding.org</A><BR><BR>To subscribe or unsubscribe via the World Wide Web, visit<BR> <A href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel=nofollow target=_blank>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</A><BR><BR>or, via email, send a message with subject or body 'help' to<BR> <A href="http://us.mc501.mail.yahoo.com/mc/compose?to=equest-users-request@lists.onebuilding.org" rel=nofollow target=_blank>equest-users-request@lists.onebuilding.org</A><BR><BR>You can reach the person managing the list at<BR> <A href="http://us.mc501.mail.yahoo.com/mc/compose?to=equest-users-owner@lists.onebuilding.org" rel=nofollow
target=_blank>equest-users-owner@lists.onebuilding.org</A><BR><BR>When replying, please edit your Subject line so it is more specific<BR>than "Re: Contents of Equest-users digest..."<BR></DIV>
<DIV>Today's Topics:<BR><BR> 1. Re: eQUEST 3.64 - Modeling Procedures Quick Reference Guide<BR> (Chris Jones)<BR> 2. Re: eQUEST 3.64 - Modeling Procedures Quick Reference Guide<BR> (Brian Fountain)<BR></DIV>
<DIV>_______________________________________________<BR>Equest-users mailing list<BR><A href="http://us.mc501.mail.yahoo.com/mc/compose?to=Equest-users@lists.onebuilding.org" rel=nofollow target=_blank>Equest-users@lists.onebuilding.org</A><BR><A href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel=nofollow target=_blank>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</A><BR></DIV></BLOCKQUOTE></TD></TR></TBODY></TABLE><BR><BR>_______________________________________________<BR>Equest-users mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" rel=nofollow target=_blank>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</A><BR>To unsubscribe from this mailing list send a blank message to <A href="http://us.mc501.mail.yahoo.com/mc/compose?to=EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" rel=nofollow target=_blank
ymailto="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR><BR></BLOCKQUOTE></DIV><BR><BR clear=all><BR>-- <BR>Carol Gardner PE<BR>
<DIV style="DISPLAY: inline; VISIBILITY: hidden" id=yiv2112753993avg_ls_inline_popup></DIV>
<STYLE type=text/css>#yiv2112753993 #yiv2112753993avg_ls_inline_popup {padding:0px 0px;margin-left:0px;margin-top:0px;width:240px;overflow:hidden;word-wrap:break-word;color:black;font-size:10px;text-align:left;line-height:13px;}</STYLE>
</DIV></BLOCKQUOTE></td></tr></table><br>