<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META content="text/html; charset=us-ascii" http-equiv=Content-Type>
<META name=GENERATOR content="MSHTML 8.00.6001.18943"></HEAD>
<BODY>
<DIV dir=ltr align=left><SPAN class=287243314-03092010><FONT color=#0000ff 
size=2 face=Arial>Nick,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=287243314-03092010><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=287243314-03092010><FONT color=#0000ff 
size=2 face=Arial>I have put together a number of hotel models, like you are 
discussing, where I modeled all the rooms on like 15 floors with the same 
exposure all together.  Of course the top floor and the ground floor were 
split off and modeled independently, since they have different exposures.  
Also, the corner rooms, with four different exposures, for the most 
accurate modeling, can be split off and modeled separately.  The internal 
heat gains should be similar on all these rooms to model properly.  I added 
up all the CFM's, KW fan loads, outside air, and the heating and cooling 
capacity of the equipment for all the rooms all together.  These 
models modeled accurately compared to actual historical energy use data of the 
hotels.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=287243314-03092010><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=287243314-03092010><FONT color=#0000ff 
size=2 face=Arial>
<DIV align=left>
<DIV align=left><STRONG><EM><FONT color=#0000ff size=6 
face="Bradley Hand ITC">David A. Bastow </FONT></EM></STRONG></DIV>
<DIV align=left><STRONG><EM><FONT face="Rockwell Extra Bold">McClure 
Engineering, Inc.  
</FONT></EM></STRONG></DIV></DIV></FONT></SPAN></DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> equest-users-bounces@lists.onebuilding.org 
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Nicholas 
Lander<BR><B>Sent:</B> Thursday, September 02, 2010 9:51 PM<BR><B>To:</B> 
equest-users@lists.onebuilding.org<BR><B>Subject:</B> [Equest-users] Equest, fan 
coils and Ashrae<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV dir=ltr><FONT class=Apple-style-span 
face="verdana, sans-serif">Folks,</FONT> 
<DIV><FONT class=Apple-style-span face="verdana, sans-serif">This may be a 
stupid question but it has me stumped. I'm primarily concerned with fan coil 
units, but any HVAC system raises similar issues:</FONT></DIV>
<DIV><FONT class=Apple-style-span face="verdana, sans-serif"><BR></FONT></DIV>
<DIV><FONT class=Apple-style-span face="verdana, sans-serif">ASHRAE Appendix G 
lets you group zones together into thermal blocks as long as they have the same 
HVAC systems and loads and orientation. So, for example, hotel rooms can be 
grouped as each is identical to the next. The question is, how do you model the 
HVAC of this thermal block?</FONT></DIV>
<DIV><FONT class=Apple-style-span face="verdana, sans-serif"><BR></FONT></DIV>
<DIV><FONT class=Apple-style-span face="verdana, sans-serif">For example, hotel 
rooms use fan coil units for cooling. A single FCU uses X-amount of energy based 
on fan size and pressure drop. So how do you accurately model fan energy when 
grouping several zones, and hence several FCUs, together?</FONT></DIV>
<DIV><FONT class=Apple-style-span face="verdana, sans-serif"><BR></FONT></DIV>
<DIV><FONT class=Apple-style-span face="verdana, sans-serif">Thanks</FONT></DIV>
<DIV><FONT class=Apple-style-span 
face="verdana, sans-serif">Nick</FONT></DIV></DIV></BODY></HTML>