Excellent. Thanks James. And yes, it's up to us to figure out how to use it, which I think qualifies as "no support". I'm sure the programmers responsible for the software are perfectly competent, and I did not mean to suggest otherwise. I suppose what I really meant to say was that the software has no customer support, which is understandable because it's free. <div>
<br></div><div>Now back to the model. So one would have to go into the detailed mode in order to change this parameter? If one was to work with a model only via the DD wizard as we sometimes do for order of magnitude estimates, would it be OK to leave ecnono-low-limit unused? or would this result in inaccurate results?<br>
<br><div class="gmail_quote">On Thu, Aug 26, 2010 at 12:22 PM, James Hansen <span dir="ltr"><<a href="mailto:JHANSEN@ghtltd.com">JHANSEN@ghtltd.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">See below. Also, the technical support isn’t “very
poor”, it’s just that the people working on technical issues are
actually programmers. It’s up to us to figure out how to use it
properly.</span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><img width="762" height="563" src="cid:image003.png@01CB4521.F8C52CA0"></span><span style="font-size:11.0pt;color:#1F497D"></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;color:teal">GHT Limited<br>
</span></b><b><span style="font-size:11.0pt"><span style="color:black">James Hansen</span></span></b><b><span style="font-size:11.0pt;color:black">, PE,
LEED AP</span></b></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;color:black">Senior Associate</span></b><b><span style="font-size:11.0pt;color:black"></span></b></p>
<p class="MsoNormal"><span style="font-size:7.5pt"><span style="color:black">1010 N. Glebe Rd, Suite 200</span></span><span style="font-size:11.0pt;color:#1F497D"></span></p>
<p class="MsoNormal"><span style="font-size:7.5pt"><span style="color:black">Arlington</span><span style="color:black">, </span><span style="color:black">VA</span><span style="color:black"> </span><span style="color:black">22201-4749</span></span><span style="font-size:11.0pt;color:black"></span></p>
<p class="MsoNormal"><span style="font-size:7.5pt;color:black">703-338-5754 (Cell)</span><span style="font-size:11.0pt;color:black"></span></p>
<p class="MsoNormal"><span style="font-size:7.5pt;color:black">703-243-1200 (Office)</span><span style="font-size:11.0pt;color:black"></span></p>
<p class="MsoNormal"><span style="font-size:7.5pt;color:black">703-276-1376 (Fax)</span><span style="font-size:11.0pt;color:black"></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:teal"><a href="http://www.ghtltd.com/" target="_blank"><span style="font-size:10.0pt">www.ghtltd.com</span></a></span></p>
<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#31849B"> </span></b></p>
<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>
<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">
<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Adrian
Gurga<br>
<b>Sent:</b> Thursday, August 26, 2010 1:13 PM</span></p><div class="im"><br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Warning: ECONO-LOW-LIMIT = *UNUSED*</div><p></p>
</div>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Carol,</p><div><div></div><div class="h5">
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal">With all due respect, "<span><span style="font-size:10.0pt">Only to input the
temperature and to look at your help screen." is not a complete sentence.
Please reply using English if you'd like to post on a listserv. If
you have advice on how to address this warning, please provide it.
Additionally, "F</span></span>laming" (<a href="http://www.urbandictionary.com/define.php?term=flaming" target="_blank">http://www.urbandictionary.com/define.php?term=flaming</a>) is
a behavior typically reserved for prepubescents on chat forums, not
professional listservs. Please show some professional courtesy in
your responses. Now, let's move forward amicably and discuss the
actual topic of the post.</p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal">All,</p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal">We all know that as eQUEST is free software, it has very
poor technical support which is why listservs like this exist.
Here is the research I've done so far. Inputting a seach for
"econo-low-limit" or even just "econo" in the eQUEST
helpfile produces no results. Are there "pull down help menus"
which discuss this topic as Carol suggests? If so, please direct me to
them. Googling "econo-low-limit" produces one relevent hit
other than this listserv, a user poses the same question I have, but is issue
is never resolved (<a href="http://www.energymodelhelp.com/SMF/index.php?topic=107.0" target="_blank">http://www.energymodelhelp.com/SMF/index.php?topic=107.0</a> ).
A search of "econo-low-limit" on this listserv will yield five
results. In four of these, "econo-low-limit" is simply listed
as an input, in the fifth, it is suggested as a way of manipulating the model.
However, I cannot find anywhere on this listserv where the warning
"econo-low-limit" = unused has been discussed. Therefore, I
assume it's a reasonable to post and and I hope it will be helpful to future
users. </p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal">I can't figure out where to specify an econo-low-limit in
the DD wizard, if I need to go into the detailed edit to address this, please
let me know where that variable is edited. I have attempted to edit the
files manually in notepad to specify an econo-low-limit, so far have had no
luck, but truthfully I'm not too experienced with manual edits. If anyone
could provide some assistance with where to edit this parameter, it would
be appreciated. Alternatively, if this warning does not have detrimental
impact on the outputs, I will just ignore it.</p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal">Thanks for your thoughts and comments.</p>
</div>
<div>
<p class="MsoNormal"> </p>
</div>
<div>
<p class="MsoNormal">-- <br>
<span style="font-size:10.0pt;color:#888888">Adrian
Gurga<br>
Smart Energy Design Assistance Center<br>
University of Illinois - Urbana-Champaign<br>
<a href="http://www.sedac.org/" target="_blank"><span style="color:#0658B5">www.sedac.org</span></a><br>
(217) 244-4671<br>
(800) 214-7954</span></p>
</div>
<p class="MsoNormal"> </p>
<div>
<p class="MsoNormal">On Thu, Aug 26, 2010 at 11:08 AM, Carol Gardner <<a href="mailto:cmg750@gmail.com" target="_blank">cmg750@gmail.com</a>> wrote:</p>
<p class="MsoNormal">That was polite, Jason. Users of this list need to be
responsible enough to at least look at the pull down help menus before asking a
question on the listserv, It is impolite and wasteful of everyone's time to not
do so. I have sympathy for someone who is learning but if they really care to
learn this skill and be in the business they need to learn to at least try to
find the answers they need. Perhaps the college systems have changed, which
would be a shame, but when I was in school I had to research and find my own
answers. Since I'm older than dirt we didn't have listservs, Google, or any of
those useful tools that now make finding answers so much easier.<br>
<br>
I rest my case,<br>
<br>
Carol</p>
<div>
<div>
<p class="MsoNormal" style="margin-bottom:12.0pt"> </p>
<div>
<p class="MsoNormal">On Thu, Aug 26, 2010 at 8:11 AM, Jason Glazer <<a href="mailto:jglazer@gard.com" target="_blank">jglazer@gard.com</a>> wrote:</p>
<p class="MsoNormal">Carol,<br>
<br>
The eQUEST-user mailing list is for users of all experience levels:<br>
<br>
"The eQUEST-users mailing list is for everyone that uses the eQUEST
program. Users at every experience level are encouraged to join this mailing
list and share their questions and knowledge. Users of the DOE-2.2 and D2Comply
are also welcome. The mailing list will be a user-to-user support forum for
eQUEST, DOE-2.2, and D2Comply."<br>
<br>
We appreciate your contribution but please either reply politely or not at all.<br>
<br>
Jason</p>
<div>
<p class="MsoNormal"><br>
<br>
On 8/26/2010 9:29 AM, Carol Gardner wrote:</p>
</div>
<blockquote style="border:none;border-left:solid #CCCCCC 1.0pt;padding:0in 0in 0in 6.0pt;margin-left:4.8pt;margin-right:0in">
<div>
<p class="MsoNormal">Only to input the temperature and to look at your help
screen. This is<br>
something you really should be able to figure out yourself. If you can't<br>
try another profession.<br>
<br>
Carol<br>
<br>
On Tue, Aug 24, 2010 at 11:55 AM, Adrian Gurga <<a href="mailto:gurga@illinois.edu" target="_blank">gurga@illinois.edu</a></p>
</div>
<div>
<p class="MsoNormal"><mailto:<a href="mailto:gurga@illinois.edu" target="_blank">gurga@illinois.edu</a>>>
wrote:<br>
<br>
I am working with a model and am working with the following
warning<br>
whenever it runs the BDL Load File Log<br>
<br>
Line 1336: Warning Encountered:<br>
INPUT-TYPE COEFFICIENTS ..<br>
ECONO-LOW-LIMIT = *UNUSED*<br>
<br>
Any ideas?<br>
<br>
--<br>
Adrian Gurga<br>
Smart Energy Design Assistance Center<br>
University of Illinois - Urbana-Champaign</p>
</div>
<p class="MsoNormal"> <a href="http://www.sedac.org" target="_blank">www.sedac.org</a>
<<a href="http://www.sedac.org/" target="_blank">http://www.sedac.org/</a>></p>
<div>
<p class="MsoNormal"><br>
(217) 244-4671<br>
(800) 214-7954<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message
to<br>
<a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>
</div>
<p class="MsoNormal"> <mailto:<a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>></p>
<div>
<p class="MsoNormal"><br>
<br>
<br>
<br>
<br>
--<br>
Carol Gardner PE<br>
<br>
<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>
</div>
</blockquote>
<p class="MsoNormal"><span style="color:#888888"><br>
-- <br>
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair<br>
Admin for <a href="http://onebuilding.org" target="_blank">onebuilding.org</a> building
performance mailing lists</span></p>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
<br>
</p>
</div>
</div>
<p class="MsoNormal"><span style="color:#888888">-- <br>
Carol Gardner PE</span></p>
</div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
<br>
<br>
</p>
</div></div></div>
</div>
<p align="left"><font size="2"><font face="Tahoma"><font color="#0000ff">
</font></font></font></p><font size="2"><font face="Tahoma"><font color="#0000ff"><hr>
</font></font><font color="#0000ff"><font color="#000000"><font face="Arial">The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to </font><a href="mailto:ght@ghtltd.com" target="_blank"><font face="Arial">ght@ghtltd.com</font></a><font face="Arial">, and destroy this communication and all copies thereof, including all attachments. Thank you.</font></font><font face="Tahoma" color="#000000"></font></font></font><p>
</p>
</blockquote></div><br><br clear="all"><br>-- <br><span style="font-family:arial, sans-serif;font-size:13px;border-collapse:collapse"><font color="#888888">Adrian Gurga<br>Smart Energy Design Assistance Center<br>University of Illinois - Urbana-Champaign<br>
<a href="http://www.sedac.org/" style="color:rgb(6, 88, 181)" target="_blank">www.sedac.org</a><br>(217) 244-4671<br>(800) 214-7954</font></span><br>
</div>