Chris,<br><br>You are exactly right. Two curves, twice the work!<br><br>Carol<br><br><div class="gmail_quote">On Thu, Aug 12, 2010 at 1:55 PM, Chris Jones <span dir="ltr"><<a href="mailto:cj@enersave.ca">cj@enersave.ca</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">I haven't looked in the manual but isn't there two curves in your equation: EIRt=COOLING-EIR*COOL-EIR-FT*(EWB,ODB)*COOL-EIR-FPLR (PLR)<br>

You have curve 1: COOL-EIR-FT - EWB, ODB and curve 2: COOL-EIR-FPLR - PLR.  I believe you have to define both curves - COOL-EIR-FT and COOL-EIR-FPLR.<div class="im"><br>
<br>
At 05:15 PM 09/07/2010, you wrote:<br>
</div><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;"><div class="im">
I have a CURVE-FIT question (yes, the same darn project). I am creating curve data for some Daikin VRV using the raw data. The capacity curves are no problem. The governing equation for cooling is: CAPt=Cooling-Capacity*COOL-CAP-FT (EWB,ODB). I have really good data tables that provide the capacity at about 6 entering web bulb temperatures and 20 outdoor dry bulb temperatures so I'm good to go there,. All the capacities have been normalized to the ARI conditions and the curves entered as BI-QUADRATIC-T. The problem I'm having is with the cooling EIR curves. The governing equation here is EIRt=COOLING-EIR*COOL-EIR-FT*(EWB,ODB)*COOL-EIR-FPLR (PLR). There is no handy example to refer to like there is for the capacity curves. At first I just proceeded as I did with the capacity curve data: called it a BI-QUADRATIC-T and normalized the EIRs as a function of the entering wet bulb and outdoor dry bulb to the ARI EIR. But what about the PLR? Isn't it a third independent variable? Has anyone had experience with this and if so please enlighten me as to what equation type did you use and how did you include the PLR.<br>

<br>
--<br>
Carol Gardner PE<br></div>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote>
<br>
<br>
Chris Jones<br>
14 Oneida Avenue<br>
Toronto, ON M5J 2E3.<br>
Tel.  416-203-7465<br>
Fax. 416-946-1005<br>
<br>
<br>
</blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; display: inline;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup {  position:absolute;  z-index:9999;  padding: 0px 0px;  margin-left: 0px;  margin-top: 0px;  width: 240px;  overflow: hidden;  word-wrap: break-word;  color: black;  font-size: 10px;  text-align: left;  line-height: 13px;}</style>