<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman,new york,times,serif;font-size:10pt"><div>Dear eQuesters:<br><br>I have an unusual building to model and request feedback on the most accurate way to accomplish this task. <br><br>An 8,500 office area/research lab area, about 1/2 of the first floor, of a 5 story building is being renovated.<br><br>A MAU with a steam preheat, DX and a steam reheat coil that supplies minimum air to all the areas and also conditions the main corridor area of 1,700 sq.ft. is being specified. This is a 100% outside air unit. The exhaust air is vented by a separate common building exhaust fan. The MAU design CFM is 7,500.<br><br>The labs require 8 ACH occupied and 4 ACH unoccupied, about 1200 CFM total. Each lab has one fume hood with an exhaust of 600 CFM when the sashes are open and 300 CFM when the sashes are closed.
There will be air valves to modulate the volume of makeup air to each lab area depending on occupancy.<br><br>All the areas, with the exception of the main corridor area are conditioned by VRV heat pump cassette units with one main condensing unit. The system chosen, a Mitsubishi Y-Series does not appear capable of transferring heat from one area to another. The engineering manual states that the R-2-Series can provide this function.<br><br>One sticking point in my model is the exhaust air. I have added an exhaust fan in each lab with a fractional schedule. How do I go about exhausting the rest of the air from each lab, about 600 CFM occupied, and the exhaust air from the office areas through the common building exhaust fan?<br><br>Any suggestions would be greatly appreciated,<br><br>Paul Diglio<br></div>
</div></body></html>