What if there are a number of different fan schedules in the
building?  Do you multiply the 2% from BEPS for all systems? 
What if only one zone on one system has unmet hours - how do you use the
BEPS report to calculate which zone and for how many hours?<br><br>
It seems to me that the SS-R report provides the most useful information
for determining which systems/zones are under heated/cooled. 
<br><br>
In Andrew's case, I believe the reviewer is off his/hers rocker - asking
that the SS-R and BEPS report match.  <br><br>
At 03:28 PM 7/6/2010, Otto Schwieterman wrote:<br>
<blockquote type=cite class=cite cite="">Content-class:
urn:content-classes:message<br>
Content-Type: multipart/alternative;<br>
<x-tab>        </x-tab>
boundary="----_=_NextPart_001_01CB1D41.6F180506"<br><br>
Andrew,<br>
 <br>
I would write a narrative explaining how eQUEST calculates unmet hours.
You take the % of hours outside throttling range on your BEPS or BEPU
report and multiply it by the number of hours your fan is on (SS-E
report). <br>
 <br>
The SS-R report shows room-by-room unmet hours. You should not take the
sum of these hours because 10 rooms may be unmet at 3:00-5:00  and
the BEPS report calculates this as 2 hours while the sum of the SS-R
report calculates it as 20 hours (10 rooms x 2 hours).<br>
 <br>
Otto <br>
 <br>
<b>From:</b> Andrew T McMurray
[<a href="mailto:amcmurray@pacollinspe.com" eudora="autourl">
mailto:amcmurray@pacollinspe.com</a>] <br>
<b>Sent:</b> Tuesday, July 06, 2010 2:17 PM<br>
<b>To:</b> equest-users@lists.onebuilding.org<br>
<b>Subject:</b> [Equest-users] (no subject)<br>
 <br>
Hello Everyone,<br>
 <br>
I am trying to finalize a building model for a LEED submission but am
having difficulty getting the BEPS report "percent of hours any
system zone outside of throttling range" to match the SS-R reports
"zone under heated" and "zone under cooled"
hours.  This was a complaint from the LEED reviewer.<br>
 <br>
The building has three systems and all spaces are conditioned.  The
BEPS report lists hours outside of throttling range at 2% (175hrs), but
the SS-R report lists under heated and cooled hours of 280 (3.2%). 
<br>
 <br>
I consider myself fairly familiar with equest but am unable to get these
two numbers to match.  Has anyone run into this problem in the past
or have any ideas of where I should be focusing my attention?<br>
 <br>
Many Thanks,<br>
 <br>
 <br>
Andrew McMurray, EIT<br>
P. A. Collins PE Consulting Engineers<br>
15 West 26th Street, 5th Floor<br>
New York, NY 10010<br>
 <br>
tel: 212.696.5294<br>
fax: 212.696.5295<br>
<a href="http://www.pacollinspe.com">www.pacollinspe.com</a><br><br>
<pre>
________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission
(including any attachments) only to the
designated individual or entity.   If you received this message
in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure
no viruses are present in the
electronic mail.  Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful.   Any information included in
this transmission that is not related to contracts with our
authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability
insurance. 


_______________________________________________

Equest-users mailing list

<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>

To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG

</blockquote>
<x-sigsep><p></x-sigsep>

Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3.
Tel.  416-203-7465
Fax. 416-946-1005

</body>
</html>