1 - zonal exhaust bypasses heat recovery and goes directly outside.
Only central exhaust goes through the heat recovery.<br>
<br>
2. - yes, the cooling effect due to ventilation is included but as you
pointed out it is hard to isolate in the .sim reports. You can prove
it to yourself by "turning off" your economizer (OA-control set to
fixed fraction) and looking at impact on space cooling.<br>
<br>
sinan senel wrote:
<blockquote cite="mid:254118.77191.qm@web30602.mail.mud.yahoo.com"
type="cite">
<style type="text/css"><!-- DIV {margin:0px;} --></style>
<div
style="font-family: times new roman,new york,times,serif; font-size: 12pt;">
<div
style="font-family: times new roman,new york,times,serif; font-size: 12pt;">
<div>Dear all,<br>
<br>
I have two questions regaridng the balanced mechanical ventilation with
heat recovery (no air heating, only for ventilating the house):<br>
<br>
1. Is the exhaust air flow defined in the zone levels supplied to the
heat recovery unit or does it fow directly to outside?<br>
2. I cannot see the cooling effect of the ventilation air in the zones.
I checked hourly reports and under thermal zone category there is an<br>
item called 'heat extraction due to venting', however they are all zero
although I can see exhaust and supply air flows. Is this normal? Does
eQUest calculate the cooling effect of the ventilation air?<br>
<br>
I saw this kind of a discussion in the previous messages but they were
not clearly concluded.<br>
<br>
Thanks in advance.<br>
<br>
Regards<br>
<br>
Sinan Senel<br>
</div>
</div>
</div>
<br>
<pre wrap="">
<hr size="4" width="90%">
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
<pre wrap="">
<hr size="4" width="90%">
No virus found in this incoming message.
Checked by AVG - <a class="moz-txt-link-abbreviated" href="http://www.avg.com">www.avg.com</a>
Version: 9.0.839 / Virus Database: 271.1.1/3009 - Release Date: 07/16/10 02:35:00
</pre>
</blockquote>
<br>
</body>
</html>