Nick,<br><br>For occupancy sensors, I have always reduced the % on in the lighting schedules, never the installed LPD. Here&#39;s a thread from way back discussing how to do this:<a href="http://www.gard.com/ml/bldg-sim-archive/msg02168.html">http://www.gard.com/ml/bldg-sim-archive/msg02168.html</a>. <br>
<br>If the methodology has changed to reducing the LPD by 15% I&#39;d like to know. It would be much easier and I&#39;d love to be wrong!<br><br>How are others doing this?<br><br>Carol<br><br><div class="gmail_quote">On Mon, Jul 12, 2010 at 7:42 AM, Nick Caton <span dir="ltr">&lt;<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">









<div link="blue" vlink="purple" lang="EN-US">

<div>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">A small correction – the reduction (0-15%) is modifying
the installed LPD (W/SF), not the schedules.  The reduction amount does
vary based on the table Carol referenced in 90.1 Appendix G.  </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">This is easiest to do in the wizards: there’s an overall
multiplier, defaulted to 1.00, on the bottom of lighting load screen.  In
detailed it would require you to modify the space LPD values in the spreadsheet
view, under the Internal Loads tab.</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Agreeing with Carol’s premise though – the way your
question is worded suggests you weren’t clear on the contents Appendix G. 
For your own sake, definitely avoid relying on others to tell you what’s
within 90.1 or you might find yourself in hot water down the road ;).</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">~Nick</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"><img src="cid:image001.jpg@01CB21A4.AA8AFE20" alt="cid:489575314@22072009-0ABB" width="119" height="37"></span><b><span style="font-size: 11pt; color: rgb(45, 77, 94);"></span></b></p>


<p class="MsoNormal"><b><span style="font-size: 11pt; color: rgb(45, 77, 94);"> </span></b></p>

<p class="MsoNormal"><b><span style="font-size: 11pt; color: rgb(45, 77, 94);">NICK CATON, E.I.T.</span></b><b><span style="color: rgb(45, 77, 94);"></span></b></p>

<p class="MsoNormal"><span style="font-size: 7.5pt; color: rgb(204, 153, 0);">PROJECT ENGINEER</span><span style="font-size: 7.5pt; color: rgb(204, 153, 0);"></span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">25501 west valley parkway</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">olathe ks 66061</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">direct 913 344.0036</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">fax 913 345.0617</span></p>

<p class="MsoNormal"><i><span style="font-size: 10pt; color: rgb(45, 77, 94);">Check out our new web-site @ </span></i><span style="font-size: 11pt; color: rgb(31, 73, 125);"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size: 10pt;">www.smithboucher.com</span></a></span><u><span style="font-size: 10pt; color: blue;"> </span></u><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>


<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">

<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Carol
Gardner<br>
<b>Sent:</b> Sunday, July 11, 2010 5:27 PM<br>
<b>To:</b> Derek Huang<br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Lighting Control - Occupancy Sensor</span></p>

</div><div class="im">

<p class="MsoNormal"> </p>

<p class="MsoNormal" style="margin-bottom: 12pt;">For the spaces that don&#39;t
require occupancy sensors you can show savings by modifying the lighting
schedule. I think a 15% reduction is allowed, but verify that by looking in
Appendix G where it tells you what you can do and when. In fact it would be good
for you to make a practice of researching the answers to these types of
questions yourself and save the more complicated questions for the listserv. It
is important to respect everyone&#39;s time and do diligence by trying to find the
answers yourself. I know it&#39;s a lot to process at first but you will benefit
from the study.<br>
<br>
Regards,<br>
Carol</p>

</div><div><div class="im">

<p class="MsoNormal">On Sat, Jul 10, 2010 at 6:21 PM, Derek Huang &lt;<a href="mailto:Derek.Huang@atce.com" target="_blank">Derek.Huang@atce.com</a>&gt; wrote:</p>

</div><div>

<div><div class="im">

<p class="MsoNormal"><span style="font-size: 10pt;">Does anyone know if
there is a spot for Occupancy Sensor lighting controls ? In both of DD Wizard
mode and Detailed Data Edit mode, I didn’t see any.</span></p>

<p class="MsoNormal"><span style="font-size: 10pt;"> </span></p>

<p class="MsoNormal"><span style="font-size: 10pt;">Thanks,</span></p>

<p class="MsoNormal"><span style="font-size: 10pt;"> </span></p>

<p class="MsoNormal"><b><span style="font-family: &quot;Gill Sans MT&quot;; color: rgb(24, 27, 83);">Derek Huang, LEED AP,
CPD                                      
</span></b></p>

<p class="MsoNormal"><span style="font-family: &quot;Gill Sans MT&quot;; color: rgb(24, 27, 83);">Mechanical Engineer</span></p>

<p class="MsoNormal"> </p>

</div><p class="MsoNormal"><b>Error!
Filename not specified.</b></p><div class="im">

<p class="MsoNormal"> </p>

<p class="MsoNormal"><span style="font-size: 10pt; font-family: &quot;Gill Sans MT&quot;; color: rgb(103, 145, 125);">97 E. Brokaw
Road, No 300</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; font-family: &quot;Gill Sans MT&quot;; color: rgb(103, 145, 125);">San Jose, CA
95112</span></p>

<p class="MsoNormal"><b><span style="font-size: 10pt; font-family: &quot;Gill Sans MT&quot;; color: rgb(103, 145, 125);">Direct</span></b><span style="font-size: 10pt; font-family: &quot;Gill Sans MT&quot;; color: rgb(103, 145, 125);">: 408
487-1305</span></p>

<p class="MsoNormal"><b><span style="font-size: 10pt; font-family: &quot;Gill Sans MT&quot;; color: rgb(103, 145, 125);">Fax:</span></b><span style="font-size: 10pt; font-family: &quot;Gill Sans MT&quot;; color: rgb(103, 145, 125);">     
408 436-1511</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; font-family: &quot;Gill Sans MT&quot;; color: rgb(34, 27, 83);"><a href="http://www.atce.com/" target="_blank">www.atce.com</a></span></p>

<p class="MsoNormal"><span style="font-size: 10pt; font-family: &quot;Gill Sans MT&quot;; color: rgb(34, 27, 83);"><a href="mailto:derek.huang@atce.com" target="_blank">derek.huang@atce.com</a></span></p>

<p class="MsoNormal"> </p>

<p class="MsoNormal"> </p>

</div></div>

</div><div class="im">

<p class="MsoNormal" style="margin-bottom: 12pt;"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>

</div></div><font color="#888888">

<p class="MsoNormal"><br>
<br clear="all">
<br>
-- <br>
Carol Gardner PE</p>

</font></div>

</div>


</blockquote></div><br><br clear="all"><br>-- <br>Carol Gardner PE<br>
<div style="visibility: hidden; display: inline;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup {  position:absolute;  z-index:9999;  padding: 0px 0px;  margin-left: 0px;  margin-top: 0px;  width: 240px;  overflow: hidden;  word-wrap: break-word;  color: black;  font-size: 10px;  text-align: left;  line-height: 13px;}</style>