<font face="Times New Roman, Times, serif">By default equest will
assign a ahu system to each floor</font>. Save a copy of the files,
PD2, INP, and open the copied project. On the action tab to the left
click building creation wizard, ignore the warnings and go back, you
have a disposable copy right? Get to the project navigator tab. If
you have everything done right you will have your zones under the
building shell components and under the air side system types you from
the sound of it you will have HVAC system 1. You can create your new
systems using the tab below. Create what ever systems you need. Press
finish. Get into your waterside HVAC tab, it is better explained as
your system tab. Look down on the left in your component tree and you
will see air-side systems. All you ahu's should be there. Just cut
and paste your zones out of HVAC system 1 into the air handlers you
want them in. If you empty HVAC 1 of zones delete it. Ideally you
should now have all your zones where you want them. If not save again,
go back into the building creation wizard and try again. Good luck.<br>
Bruce Easterbrook P.Eng.<br>
Abode Engineering<br>
<br>
On 09/07/2010 07:09 PM, Derek Huang wrote:
<blockquote
cite="mid:594A4EBE9B49844097AD42ED8516ECCD01EDED0B@sjxbe01.alfatech.net"
type="cite">
<meta http-equiv="Content-Type"
content="text/html; charset=ISO-8859-1">
<meta name="Generator" content="Microsoft Word 11 (filtered medium)">
<!--[if !mso]>
<style>
v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style>
<![endif]--><o:smarttagtype
namespaceuri="urn:schemas-microsoft-com:office:smarttags"
name="address">
<o:smarttagtype
namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="Street"><o:smarttagtype
namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="place">
<o:smarttagtype
namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="City"><o:smarttagtype
namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="State">
<o:smarttagtype
namespaceuri="urn:schemas-microsoft-com:office:smarttags"
name="PostalCode"><!--[if !mso]>
<style>
st1\:*{behavior:url(#default#ieooui) }
</style>
<![endif]-->
<style>
<!--
/* Font Definitions */
@font-face
{font-family:"Gill Sans MT";
panose-1:2 11 5 2 2 1 4 2 2 3;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman";}
a:link, span.MsoHyperlink
{color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{color:purple;
text-decoration:underline;}
span.EmailStyle17
{mso-style-type:personal-compose;
font-family:Arial;
color:windowtext;}
@page Section1
{size:8.5in 11.0in;
margin:1.0in 1.25in 1.0in 1.25in;}
div.Section1
{page:Section1;}
-->
</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="Section1">
<p class="MsoNormal"><font face="Arial" size="2"><span
style="font-size: 10pt; font-family: Arial;">Hi all,<o:p></o:p></span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span
style="font-size: 10pt; font-family: Arial;"><o:p> </o:p></span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span
style="font-size: 10pt; font-family: Arial;">I’m working on a energy
model for a data center in <st1:city w:st="on"><st1:place w:st="on">Seattle</st1:place></st1:city>.
The data center
is served by 10 packaged rooftop units. The adjacent Transformer rooms,
UPS
room and RO room are conditioned by transfer air from the data center.
I
actually divide the data center, the transformer room and RO room into
10
average pieces so each roof packaged serves (4) areas and these areas
are not
connected together. So in DD Wizard mode under Zone Pattern (page 2 of
25), I
outline (4) different spaces (not connected together) as a group. The
program
then assigned one system for each area even though I have assigned one
system
for each Zone Group in page 14 of 25. How could that be ?<o:p></o:p></span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span
style="font-size: 10pt; font-family: Arial;"><o:p> </o:p></span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span
style="font-size: 10pt; font-family: Arial;">Thanks,<o:p></o:p></span></font></p>
<p class="MsoNormal"><font face="Arial" size="2"><span
style="font-size: 10pt; font-family: Arial;"><o:p> </o:p></span></font></p>
<p class="MsoNormal"><strong><b><font color="#181b53"
face="Gill Sans MT" size="3"><span
style="font-size: 12pt; font-family: "Gill Sans MT"; color: rgb(24, 27, 83);">Derek
Huang,
LEED AP,
CPD
<o:p></o:p></span></font></b></strong></p>
<p class="MsoNormal"><strong><b><font color="#181b53"
face="Gill Sans MT" size="3"><span
style="font-size: 12pt; font-family: "Gill Sans MT"; color: rgb(24, 27, 83); font-weight: normal;">Mechanical
Engineer</span></font></b></strong><strong><b><font color="#181b53"
face="Gill Sans MT" size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(24, 27, 83); font-weight: normal;"><o:p></o:p></span></font></b></strong></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span
style="font-size: 12pt;"><o:p> </o:p></span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span
style="font-size: 12pt;"><img id="_x0000_i1025"
src="cid:part1.09000302.06050102@bellnet.ca" height="36" width="181"><o:p></o:p></span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span
style="font-size: 12pt;"><o:p> </o:p></span></font></p>
<p class="MsoNormal"><st1:street w:st="on"><st1:address w:st="on"><font
color="#67917d" face="Gill Sans MT" size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(103, 145, 125);">97
E. Brokaw Road</span></font></st1:address></st1:street><font
color="#67917d" face="Gill Sans MT" size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(103, 145, 125);">,
No 300<o:p></o:p></span></font></p>
<p class="MsoNormal"><st1:place w:st="on"><st1:city w:st="on"><font
color="#67917d" face="Gill Sans MT" size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(103, 145, 125);">San
Jose</span></font></st1:city><font color="#67917d" face="Gill Sans MT"
size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(103, 145, 125);">,
<st1:state w:st="on">CA</st1:state> <st1:postalcode w:st="on">95112</st1:postalcode></span></font></st1:place><font
color="#67917d" face="Gill Sans MT" size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(103, 145, 125);"><o:p></o:p></span></font></p>
<p class="MsoNormal"><b><font color="#67917d" face="Gill Sans MT"
size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(103, 145, 125); font-weight: bold;">Direct</span></font></b><font
color="#67917d" face="Gill Sans MT" size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(103, 145, 125);">:
408
487-1305<o:p></o:p></span></font></p>
<p class="MsoNormal"><b><font color="#67917d" face="Gill Sans MT"
size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(103, 145, 125); font-weight: bold;">Fax:</span></font></b><font
color="#67917d" face="Gill Sans MT" size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(103, 145, 125);">
408
436-1511<o:p></o:p></span></font></p>
<p class="MsoNormal"><font color="#221b53" face="Gill Sans MT"
size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(34, 27, 83);"><a
moz-do-not-send="true" href="http://www.atce.com/">www.atce.com</a><o:p></o:p></span></font></p>
<p class="MsoNormal"><font color="#221b53" face="Gill Sans MT"
size="2"><span
style="font-size: 10pt; font-family: "Gill Sans MT"; color: rgb(34, 27, 83);"><a class="moz-txt-link-abbreviated" href="mailto:derek.huang@atce.com">derek.huang@atce.com</a><o:p></o:p></span></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span
style="font-size: 12pt;"> </span><o:p></o:p></font></p>
<p class="MsoNormal"><font face="Times New Roman" size="3"><span
style="font-size: 12pt;"><o:p> </o:p></span></font></p>
</div>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></o:smarttagtype></blockquote>
</body>
</html>