<DIV><!-- Converted from text/plain format --><FONT face=Arial color=#0000ff
size=2>I just went through a review process for this!</FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2>I initially interpreted it the same
way the Cam says below however the LEED reviewer disagreed with me and said I
should model it as Sam describes below.</FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2>I think the catch is this: on page 6
it says " For such projects the secondary equipment within the building is
modeled as described in table 3 above (i.e., the same way as in step 1" it also
says "The proposed case modeling requirements differ from those in ASHRAE
90.1-2004 Appendix G; however, the baseline case is modeled as instructed in
Appendix G."... I think what this means is that the baseline models should be
the same in both case 1 and case 2... and everything should be modeled as
described in appendix G except the specific type of system as listed in table
3.</FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2>if the above sounds confusing feel
free to call me.</FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2>
<DIV align=left>
<DIV class=Section1>
<DIV>
<P style="MARGIN: 0in 0in 0pt" align=left><STRONG><SPAN
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><FONT color=#800080>Heather
Hardie-Hill<?xml:namespace prefix = o ns =
"urn:schemas-microsoft-com:office:office"
/><o:p></o:p></FONT></SPAN></STRONG></P>
<P style="MARGIN: 0in 0in 0pt"><STRONG><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: gray; FONT-FAMILY: Arial">EIT,
LEED</SPAN></STRONG><STRONG><SUP><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 6pt; COLOR: gray; FONT-FAMILY: Arial">TM</SPAN></SUP></STRONG><STRONG><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: gray; FONT-FAMILY: Arial">
AP</SPAN></STRONG></P>
<P style="MARGIN: 0in 0in 0pt"><STRONG><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: gray; FONT-FAMILY: Arial"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial"><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: gray; FONT-FAMILY: Arial"><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: gray; FONT-FAMILY: Arial"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial">Advanced Design and
Simulation</SPAN></SPAN></SPAN></SPAN></SPAN></STRONG></P>
<P style="MARGIN: 0in 0in 0pt"><STRONG><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: gray; FONT-FAMILY: Arial"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial"><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: gray; FONT-FAMILY: Arial"><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: gray; FONT-FAMILY: Arial"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial"></SPAN></SPAN></SPAN></SPAN></SPAN></STRONG> </P>
<P style="MARGIN: 0in 0in 0pt"><EM><B style="mso-bidi-font-weight: normal"><SPAN
style="FONT-SIZE: 10pt; COLOR: purple; FONT-STYLE: normal; FONT-FAMILY: Arial; mso-bidi-font-style: italic"><SPAN
style="FONT-SIZE: 10pt; COLOR: purple; FONT-STYLE: normal; FONT-FAMILY: Arial; mso-bidi-font-style: italic"><FONT
color=#808080>CH2M HILL</FONT></SPAN></SPAN></B></EM></P>
<P style="MARGIN: 0in 0in 0pt"><EM><B style="mso-bidi-font-weight: normal"><SPAN
style="FONT-SIZE: 10pt; COLOR: purple; FONT-STYLE: normal; FONT-FAMILY: Arial; mso-bidi-font-style: italic"><SPAN
style="FONT-SIZE: 10pt; COLOR: purple; FONT-STYLE: normal; FONT-FAMILY: Arial; mso-bidi-font-style: italic"></SPAN><FONT
color=#808080>Industrial & Advanced
Technologies</FONT></SPAN></B></EM></P>
<P style="MARGIN: 0in 0in 0pt"><?xml:namespace prefix = st1 ns =
"urn:schemas-microsoft-com:office:smarttags" /><st1:Street
w:st="on"><st1:address w:st="on"
ns1_x003a_style="BACKGROUND-POSITION: left bottom; BACKGROUND-IMAGE: url(res://ietag.dll/#34/#1001); BACKGROUND-REPEAT: repeat-x"
ns1_x003a_tabIndex="0"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial">2020 SW Fourth
Ave</SPAN></st1:address></st1:Street><SPAN
style="FONT-FAMILY: Arial"><o:p></o:p></SPAN></P>
<P style="MARGIN: 0in 0in 0pt"><st1:place w:st="on"><st1:City w:st="on"><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial">Portland</SPAN></st1:City></st1:place><SPAN
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial">, <st1:State
w:st="on">OR</st1:State> <st1:PostalCode
w:st="on">97201</st1:PostalCode></SPAN><SPAN
style="FONT-FAMILY: Arial"><o:p></o:p></SPAN></P>
<P style="MARGIN: 0in 0in 0pt"><SPAN lang=PT-BR
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-ansi-language: PT-BR">ph:
(503).872.4509</SPAN><SPAN lang=PT-BR
style="mso-ansi-language: PT-BR"><o:p></o:p></SPAN></P>
<P style="MARGIN: 0in 0in 0pt"><SPAN lang=PT-BR
style="FONT-SIZE: 10pt; COLOR: gray; FONT-FAMILY: Arial; mso-ansi-language: PT-BR">e:
heather.hardie-hill@ch2m.com<o:p></o:p></SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN lang=PT-BR
style="mso-ansi-language: PT-BR"> <o:p></o:p></SPAN></P></DIV></DIV></DIV></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><BR>-----Original
Message-----<BR>From: equest-users-bounces@lists.onebuilding.org [</FONT><A
href="mailto:equest-users-bounces@lists.onebuilding.org"><FONT face=Arial
size=2>mailto:equest-users-bounces@lists.onebuilding.org</FONT></A><FONT
face=Arial color=#0000ff size=2>] On Behalf Of Cam Fitzgerald<BR>Sent: Thursday,
July 08, 2010 9:11 AM<BR>To: Sam Mason; Mohammad Almasri;
eQUEST-users@onebuilding.org<BR>Subject: Re: [Equest-users] Baseline Modeling as
per LEED districtcoolingrequirements<BR><BR>All:<BR><BR>I hate to disagree with
Sam's response, but on page 6 of the USGBC DES document the description of the
Model for Step 2 states, "The proposed case modeling requirements differ from
those in ASHRAE 90.1-2004 Appendix G; however, the baseline case is modeled as
instructed in Appendix G." So for step 2 the baseline HVAC systems for the
residential spaces would be PTHP, not AHU's as required for step 1.<BR><BR>Hope
this helps!<BR><BR>Cam S. Fitzgerald, PE, LEED AP<BR><BR>Energy Opportunities,
LLC<BR>a 7group company<BR><BR> -----Original Message-----<BR>From:
equest-users-bounces@lists.onebuilding.org [</FONT><A
href="mailto:equest-users-bounces@lists.onebuilding.org"><FONT face=Arial
size=2>mailto:equest-users-bounces@lists.onebuilding.org</FONT></A><FONT
face=Arial color=#0000ff size=2>] On Behalf Of Sam Mason<BR>Sent: Wednesday,
July 07, 2010 9:50 AM<BR>To: Mohammad Almasri;
eQUEST-users@onebuilding.org<BR>Subject: Re: [Equest-users] Baseline Modeling as
per LEED districtcoolingrequirements<BR><BR>Mohammad,<BR>You will keep the same
the same system from step 1 to step 2 - fan coils with hot water boiler - per
Table 3 in the DES guidelines. In step 2, you will create a minimally compliant
cooling plant based on Appendix G modeling parameters and attach the fan coils
to the plant.<BR><BR>Sam<BR>--<BR>Sam Mason<BR>Atelier
Ten<BR><BR><BR>-----Original Message-----<BR>From:
equest-users-bounces@lists.onebuilding.org [</FONT><A
href="mailto:equest-users-bounces@lists.onebuilding.org"><FONT face=Arial
size=2>mailto:equest-users-bounces@lists.onebuilding.org</FONT></A><FONT
face=Arial color=#0000ff size=2>] On Behalf Of Mohammad Almasri<BR>Sent:
Wednesday, July 07, 2010 8:38 AM<BR>To: eQUEST-users@onebuilding.org<BR>Subject:
Re: [Equest-users] Baseline Modeling as per LEED district
coolingrequirements<BR><BR>Hi all,<BR><BR>I Am working now on a Residential
tower supplied by a district cooling plant . The proposed design completed as
per the LEED required treatment of district cooling . and two model performed
(one with virtual chillers and the other one with chilled water meter to reflect
the chilled water cost).<BR><BR>The problem that I have now is in the
baseline.<BR><BR>In step one (modeled as cost neutral), the document say that
the system will be based on table 3 instead of ASHRAE appendix G , system 2 (FCU
will be use instead of PTHP).<BR><BR>Now for step two , what the system will be
; it should be a PTHP or a FCU with a chillers ?<BR><BR>Please I need your
advice .<BR><BR>Best regards,<BR><BR>Mohammad Al-Masri<BR>Simulation
Engineer<BR>CAPM,LEED AP
BD+C<BR><BR><BR><BR><BR><BR>_______________________________________________<BR>Equest-users
mailing list<BR></FONT><A
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"><FONT
face=Arial
size=2>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</FONT></A><BR><FONT
face=Arial color=#0000ff size=2>To unsubscribe from this mailing list send
a blank message to
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR><BR>________________________________________________________________________<BR>This
e-mail has been scanned for all viruses by Star. The service is powered by
MessageLabs. For more information on a proactive anti-virus service working
around the clock, around the globe, visit:<BR></FONT><A
href="http://www.star.net.uk"><FONT face=Arial
size=2>http://www.star.net.uk</FONT></A><BR><FONT face=Arial color=#0000ff
size=2>________________________________________________________________________<BR><BR>______________________________________________________________________<BR>This
email has been scanned by the MessageLabs Email Security System.<BR>For more
information please visit </FONT><A href="http://www.messagelabs.com/email"><FONT
face=Arial size=2>http://www.messagelabs.com/email</FONT></A><FONT face=Arial
color=#0000ff size=2>
______________________________________________________________________<BR>_______________________________________________<BR>Equest-users
mailing list<BR></FONT><A
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"><FONT
face=Arial
size=2>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</FONT></A><BR><FONT
face=Arial color=#0000ff size=2>To unsubscribe from this mailing list send
a blank message to
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR>_______________________________________________<BR>Equest-users
mailing list<BR></FONT><A
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"><FONT
face=Arial
size=2>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</FONT></A><BR><FONT
face=Arial color=#0000ff size=2>To unsubscribe from this mailing list send
a blank message to
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR></DIV></FONT></BODY></HTML>