<FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'>If you have any DX units and have allowed crankcase heating (which is a checkbox in the DD wizard if you used the wizard to set up HVAC equipment initially), that will show up as aux. energy. <BR>
<BR>
<BR>
On 6/15/10 1:27 PM, "Sam Mason" <<a href="sam.mason@atelierten.com">sam.mason@atelierten.com</a>> wrote:<BR>
<BR>
</SPAN></FONT><BLOCKQUOTE><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><FONT COLOR="#1F497D">Heather,<BR>
I hope your first EAc1 review doesn’t discourage you and I understand reaching out for guidance. <BR>
<BR>
1. It sounds like you did indeed model frames so I would just provide the additional information on the conductance of the frames and build a Window5 model to determine the assembly U-value and include both for the reviewer. <BR>
</FONT><BR>
<FONT COLOR="#1F497D">2. While not the strangest comment I’ve seen the GBCI, it is up there for random and your response seems okay. However, is the percentage of lighting end-use energy extremely high for the project or is there another reason they state for making this comment? Just be thorough in your response.<BR>
</FONT><BR>
<FONT COLOR="#1F497D">3. Pumps and auxiliary energy includes at least three things: pumps, furnace pilot lights, and internal energy sources defined as a space load that use electricity or natural gas. Without seeing your inp files, hard to say though.<BR>
</FONT><BR>
<FONT COLOR="#1F497D"> <BR>
Good luck. It is hard to provide much more help without knowing more about the project but hopefully this will get you started.<BR>
<BR>
Sam<BR>
</FONT><BR>
</SPAN></FONT><FONT COLOR="#1F497D"><FONT SIZE="2"><FONT FACE="Consolas, Courier New, Courier"><SPAN STYLE='font-size:10pt'>--<BR>
Sam Mason<BR>
Atelier Ten<BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'> <BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Tahoma, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:10pt'><B>From:</B> <a href="equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a> [<a href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>] <B>On Behalf Of </B><a href="Heather.Hardie-Hill@CH2M.com">Heather.Hardie-Hill@CH2M.com</a><BR>
<B>Sent:</B> Tuesday, June 15, 2010 1:09 PM<BR>
<B>To:</B> <a href="eQUEST-users@onebuilding.org">eQUEST-users@onebuilding.org</a><BR>
<B>Subject:</B> [Equest-users] LEED review comments<BR>
</SPAN></FONT></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>Hello eQuest Users!<BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> </SPAN></FONT><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>I realize that this is an eQuest users forum and not necessarily a LEED help forum but from reading past posts it sound like many of you have quite a few LEED projects under your belts and I could really use some advice/help. I just received my first EAc1 LEED review back and there are 16 comments. Is that normal? I want to make sure that I understand how eQuest is working for a few of these comments so that I can answer them completely and correctly.<BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>so here are my review comment/questions:<BR>
</SPAN></FONT></FONT><OL><LI><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>"The Proposed windows were modeled with a U-value of 0.29, which does not appear to account for the impact of the window frames on the whole assembly as required by ASHRAE modeling protocol." <BR>
</SPAN></FONT></FONT><UL><LI><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>The U-Value of 0.29 is indeed the center of glass U-Value however I included frame conductance and frame width in the model.
</SPAN></FONT></FONT><LI><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>Is that enough to account for the "whole assembly" U-Value?
</SPAN></FONT></FONT><LI><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>or do I need to find a published whole assembly U-Value for the specified window?
</SPAN></FONT></FONT><LI><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>If I do need the whole assembly U-Value, then should I remove the frame information from the model?</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'> <BR>
</SPAN></FONT></UL><LI><SPAN STYLE='font-size:11pt'><FONT FACE="Trebuchet MS">"</FONT></SPAN><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>Please confirm that the energy consumption attributed to “Area Lights” on Table 1.8.1 and 1.8.2 represents internal lighting energy consumption and demand or provide a narrative describing any alternative uses."</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'> <BR>
</SPAN></FONT><UL><LI><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>the area lights information came from the "Ambient Lights" column of the Annual Enduse Summary... so I would say yes, it represents the lighting energy consumption and demand. Right? <BR>
</SPAN></FONT></FONT></UL><LI><FONT FACE="Arial"><SPAN STYLE='font-size:11pt'>"</SPAN><FONT SIZE="2"><SPAN STYLE='font-size:10pt'>Please provide a narrative to describe the end use for the modeled “Pumps & Auxiliary” as shown on Table 1.8.1 and 1.8.2"</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'> <BR>
</SPAN></FONT><UL><LI><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>I have not been able to figure out exactly what is contributing to this load (besides the pumps of course). What, according to eQuest, is considered "Auxiliary"?</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'> <BR>
</SPAN></FONT></UL></OL><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>I think that is it for now... I'm sure as I start making adjustments that I will have additional questions. (The building runs off of a central chiller plant so I've used the "Required Treatment of District Thermal Energy in LEED-NC version 2.2" document as a guideline and haven't quite wrapped my head around the comments related to that)<BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>I know that one of the first things you might ask is to see my .inp and .pd2 files... unfortunately it is for a confidential client and I am unable to share that information.<BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>One more quick thing... Although I do not regularly contribute to the forum I try to read all of the threads as they come through (admittedly, I'm a little behind right now). It is comforting to know that I am not the only one having issues with energy modeling and eQuest. It is also comforting knowing that I can ask you questions and I don't have to bang my head against a wall trying to figure it all out on my own! so, thanks in advance for the help!!!!<BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT COLOR="#800080"><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'><B>Heather Hardie-Hill<BR>
</B></SPAN></FONT></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT COLOR="#808080"><FONT SIZE="1"><FONT FACE="Arial"><SPAN STYLE='font-size:8pt'><B>EIT, LEED</B></SPAN><B><SPAN STYLE='font-size:6pt'>TM</SPAN><SPAN STYLE='font-size:8pt'> AP<BR>
</SPAN></B></FONT></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT COLOR="#808080"><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'><B><I>CH2M HILL<BR>
</I></B></SPAN></FONT></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT COLOR="#808080"><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'><B><I>Industrial & Advanced Technologies<BR>
</I></B></SPAN></FONT></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT COLOR="#808080"><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>Portland, OR 97201<BR>
</SPAN></FONT></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT COLOR="#808080"><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>e: <a href="heather.hardie-hill@ch2m.com">heather.hardie-hill@ch2m.com</a><BR>
</SPAN></FONT></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
<BR>
________________________________________________________________________<BR>
This e-mail has been scanned for all viruses by Star. The<BR>
service is powered by MessageLabs. For more information on a proactive<BR>
anti-virus service working around the clock, around the globe, visit:<BR>
<a href="http://www.star.net.uk">http://www.star.net.uk</a><BR>
________________________________________________________________________<BR>
<BR>
______________________________________________________________________<BR>
This email has been scanned by the MessageLabs Email Security System.<BR>
For more information please visit <a href="http://www.messagelabs.com/email">http://www.messagelabs.com/email</a> <BR>
______________________________________________________________________<BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
<HR ALIGN=CENTER SIZE="3" WIDTH="95%"></SPAN></FONT><FONT SIZE="1"><FONT FACE="Monaco, Courier New"><SPAN STYLE='font-size:9pt'>_______________________________________________<BR>
Equest-users mailing list<BR>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><BR>
To unsubscribe from this mailing list send a blank message to <a href="EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><BR>
</SPAN></FONT></FONT></BLOCKQUOTE>
</BODY>
</HTML>