<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><DIV>My two cents..</DIV>
<DIV> </DIV>
<DIV>Before you make two Detailed Edit Models (one baseline, one proposed), make sure you have all the correct schedules and ancillary loads the same in ONE Detailed Edit model. You have quite rudimentary schedules in the Wizards (probably developed on Mars), so you need to insure any additional schedules (or schedule changes) and load additions are made.</DIV>
<DIV> </DIV>
<DIV>THEN make your two Detailed Edit models.</DIV>
<DIV> </DIV>
<DIV><BR>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><A name=_MailAutoSig><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>John R. Aulbach, PE, CEM<?xml:namespace prefix = o ns = "urn:schemas-microsoft-com:office:office" /><o:p></o:p></FONT></SPAN></A></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>Senior Energy Engineer<o:p></o:p></FONT></SPAN></SPAN></P>
<DIV style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #17365d; mso-fareast-font-family: 'Times New Roman'; mso-no-proof: yes"><FONT face=Calibri>
<HR style="COLOR: #17365d" align=left SIZE=2 width="30%" noShade>
</FONT></SPAN></SPAN></DIV>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: navy; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Partner</SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: green; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"> </SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: #006600; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Energy</SPAN><SPAN style="FONT-VARIANT: small-caps; COLOR: navy; mso-no-proof: yes"><o:p></o:p></SPAN></B></SPAN></FONT></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri>1990 E. Grand Avenue, El Segundo, CA 90245<BR>W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745<o:p></o:p></FONT></SPAN></SPAN></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"></SPAN><A href="http://www.ptrenergy.com/"><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">www.ptrenergy.com</SPAN></SPAN><SPAN style="mso-bookmark: _MailAutoSig"></SPAN></FONT></A><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT face=Calibri> </FONT></SPAN></SPAN><A href="mailto:%7C%20jaulbach@ptrenergy.com"><FONT face=Calibri><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">| jaulbach@ptrenergy.com</SPAN></SPAN><SPAN style="mso-bookmark: _MailAutoSig"></SPAN></FONT></A><SPAN style="mso-bookmark:
 _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><o:p></o:p></SPAN></SPAN></P><SPAN style="mso-bookmark: _MailAutoSig"></SPAN>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><o:p><FONT face=Calibri> </FONT></o:p></SPAN></P></DIV>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><BR>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><FONT size=2 face=Tahoma>
<HR SIZE=1>
<B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B> Peter Hillermann <e190984026@exchange.1and1.com><BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> Paul Buchheit <paul.buchheit@eesinet.com>; Omar Katanani <omar@ecoconsulting.net>; equest-users@lists.onebuilding.org<BR><B><SPAN style="FONT-WEIGHT: bold">Sent:</SPAN></B> Fri, June 11, 2010 11:11:21 AM<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> Re: [Equest-users] Baseline Modeling<BR></FONT><BR>
<STYLE><!--
 
 _filtered {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}
 _filtered {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;}
 _filtered {font-family:"ITC Avant Garde Gothic Demi";panose-1:0 0 0 0 0 0 0 0 0 0;}
 _filtered {font-family:"ITC Avant Garde Std Md";panose-1:0 0 0 0 0 0 0 0 0 0;}
 _filtered {font-family:"ITC Avant Garde Std Bk";panose-1:0 0 0 0 0 0 0 0 0 0;}
 
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:"serif";}
a:link, span.MsoHyperlink
        {color:blue;text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;text-decoration:underline;}
p
        {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:"serif";}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {margin:0in;margin-bottom:.0001pt;font-size:8.0pt;font-family:"sans-serif";}
span.BalloonTextChar
        {font-family:"sans-serif";}
span.emailstyle17
        {font-family:"sans-serif";color:windowtext;}
span.EmailStyle21
        {font-family:"sans-serif";color:#1F497D;}
span.EmailStyle22
        {font-family:"sans-serif";color:#1F497D;}
.MsoChpDefault
        {font-size:10.0pt;}
 _filtered {margin:1.0in 1.25in 1.0in 1.25in;}
div.WordSection1
        {}
 
ol
        {margin-bottom:0in;}
ul
        {margin-bottom:0in;}
--></STYLE>
<DIV class=WordSection1>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Thanks Paul,</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Someone later told me I was incorrect and I’ll be changing the way I do it as well. Starting proposed and working backwards.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Thanks,</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 10pt" lang=DE>PETER HILLERMANN</SPAN></B></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 10pt" lang=DE> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt" lang=DE><A href="mailto:peterh@westallarchitects.com" rel=nofollow target=_blank ymailto="mailto:peterh@westallarchitects.com">peterh@westallarchitects.com</A></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 10pt" lang=DE> </SPAN></P>
<P style="LINE-HEIGHT: 75%" class=MsoNormal><B><SPAN style="LINE-HEIGHT: 75%; FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 14pt" lang=DE>westall</SPAN></B><SPAN style="LINE-HEIGHT: 75%; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 14pt" lang=DE></SPAN></P>
<P style="LINE-HEIGHT: 75%; MARGIN-LEFT: 4pt" class=MsoNormal><B><SPAN style="LINE-HEIGHT: 75%; FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 14pt">architects</SPAN></B><SPAN style="LINE-HEIGHT: 75%; FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 14pt"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 10pt">3404 pierce drive</P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 10pt">chamblee, georgia 30341</SPAN></P></SPAN>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt">o 770.458.4113</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt">f  770.458.5352</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt">c 678.898.2936</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt"><A href="http://westallarchitects.com/" target=_blank>westallarchitects.com</A></SPAN><SPAN style="LETTER-SPACING: 1pt; COLOR: #1f497d"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><IMG id=_x0000_i1030 border=0 alt=e-signature src="cid:1.155196273@web52801.mail.re2.yahoo.com" width=160 height=87><IMG id=_x0000_i1029 border=0 alt=USGBC-Logo src="cid:2.155196273@web52801.mail.re2.yahoo.com" width=92 height=90></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<DIV>
<DIV style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> Paul Buchheit [mailto:paul.buchheit@eesinet.com] <BR><B>Sent:</B> Friday, June 11, 2010 1:23 PM<BR><B>To:</B> Peter Hillermann; 'Omar Katanani'; equest-users@lists.onebuilding.org<BR><B>Subject:</B> Re: [Equest-users] Baseline Modeling</SPAN></P></DIV></DIV>
<P class=MsoNormal> </P>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">Hello Omar,</SPAN></P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">These are the steps I suggest you follow to complete the proposed building and the baseline building models most efficiently:</SPAN></P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">1) Model the proposed building first. Do everything you can in wizard. Keep a copy of the model at this stage so that you can easily go back to this state of your model if necessary.</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">2) Save two new copies of your model- one for the proposed model to be completed in the detailed editor and one for the baseline model.</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">3) Complete the proposed model in detail editor</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">4) Go back to the model you saved in step 2 of this process as the baseline model and change your selections in the wizard to comply with ASHRAE 90.1. This is quicker and easier than changing all the values manually.Keep a copy of the model at this stage so that you can easily go back to this state of your model if necessary.</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">5) Save a new copy of the baseline model and complete it in the detailed editor. </SPAN></P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">This process allows you to do everything you can in the wizard for both the baseline and proposed building models. It also helps to ensure that schedules and other aspects shared by the two buildings are modeled the same as required by ASHRAE 90.1. </SPAN></P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">I hope this helps,</SPAN></P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">Paul</SPAN></P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal>Paul Buchheit <BR>Mechanical Engineer<BR>EESI<BR>phone: 541-754-1062<BR>fax: 541-753-3948<BR><A href="mailto:paul.buchheit@eesinet.com" rel=nofollow target=_blank ymailto="mailto:paul.buchheit@eesinet.com">paul.buchheit@eesinet.com</A></P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<BLOCKQUOTE style="BORDER-BOTTOM: medium none; BORDER-LEFT: black 1.5pt solid; PADDING-BOTTOM: 0in; MARGIN: 5pt 0in 5pt 3.75pt; PADDING-LEFT: 4pt; PADDING-RIGHT: 0in; BORDER-TOP: medium none; BORDER-RIGHT: medium none; PADDING-TOP: 0in">
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">----- Original Message ----- </SPAN></P></DIV>
<DIV>
<P style="BACKGROUND: #e4e4e4" class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> <A title=e190984026@exchange.1and1.com href="mailto:e190984026@exchange.1and1.com" rel=nofollow target=_blank ymailto="mailto:e190984026@exchange.1and1.com">Peter Hillermann</A> </SPAN></P></DIV>
<DIV>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">To:</SPAN></B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> <A title=omar@ecoconsulting.net href="mailto:omar@ecoconsulting.net" rel=nofollow target=_blank ymailto="mailto:omar@ecoconsulting.net">'Omar Katanani'</A> ; <A title=equest-users@lists.onebuilding.org href="mailto:equest-users@lists.onebuilding.org" rel=nofollow target=_blank ymailto="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</A> </SPAN></P></DIV>
<DIV>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">Sent:</SPAN></B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> Friday, June 11, 2010 9:26 AM</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">Subject:</SPAN></B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> Re: [Equest-users] Baseline Modeling</SPAN></P></DIV>
<DIV>
<P class=MsoNormal> </P></DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Omar,</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">You need to start with the baseline then enter you efficient values. Yes you need to enter ASHRAE standards manually.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Thanks,</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 10pt" lang=DE>PETER HILLERMANN</SPAN></B></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 10pt" lang=DE> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt" lang=DE><A href="mailto:peterh@westallarchitects.com" rel=nofollow target=_blank ymailto="mailto:peterh@westallarchitects.com">peterh@westallarchitects.com</A></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 10pt" lang=DE> </SPAN></P>
<P style="LINE-HEIGHT: 75%" class=MsoNormal><B><SPAN style="LINE-HEIGHT: 75%; FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 14pt" lang=DE>westall</SPAN></B><SPAN style="LINE-HEIGHT: 75%; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 14pt" lang=DE></SPAN></P>
<P style="LINE-HEIGHT: 75%; MARGIN-LEFT: 4pt" class=MsoNormal><B><SPAN style="LINE-HEIGHT: 75%; FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 14pt">architects</SPAN></B><SPAN style="LINE-HEIGHT: 75%; FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 14pt"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 10pt">3404 pierce drive</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 10pt">chamblee, georgia 30341</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt">o 770.458.4113</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt">f  770.458.5352</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt">c 678.898.2936</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'serif'; LETTER-SPACING: 1pt; COLOR: #1f497d; FONT-SIZE: 8pt">westallarchitects.com</SPAN><SPAN style="LETTER-SPACING: 1pt; COLOR: #1f497d"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><IMG id=Picture_x0020_1 border=0 alt=e-signature src="cid:3.155196273@web52801.mail.re2.yahoo.com" width=160 height=87><IMG id=Picture_x0020_2 border=0 alt=USGBC-Logo src="cid:2.155196273@web52801.mail.re2.yahoo.com" width=92 height=90></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<DIV>
<DIV style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt"> <A href="mailto:equest-users-bounces@lists.onebuilding.org" rel=nofollow target=_blank ymailto="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</A> [mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Omar Katanani<BR><B>Sent:</B> Friday, June 11, 2010 11:48 AM<BR><B>To:</B> equest-users@lists.onebuilding.org<BR><B>Subject:</B> [Equest-users] Baseline Modeling</SPAN></P></DIV></DIV>
<P class=MsoNormal> </P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt" lang=EN-GB>Dear all,</SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt" lang=EN-GB> </SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt" lang=EN-GB>I am modeling a school using eQUEST. I have entered the values corresponding to the proposed building (like the specifications given). I would like to model the baseline building according to ASHRAE 90.1 standard. </SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt" lang=EN-GB>Do I have to change the U-values, HVAC strategy, Window/wall ratio, and the other stuff manually? That is, shall I open the ASHRAE standard and start changing all values one-by-one? The ASHRAE Standard 90.1 isn’t recognized by eQUEST such that it can create the baseline case alone? That would save a lot of time!</SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt" lang=EN-GB> </SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt" lang=EN-GB>Best regards,</SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; FONT-SIZE: 10pt" lang=EN-GB>Omar</SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: navy; FONT-SIZE: 10pt" lang=EN-GB>___________________________</SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: navy; FONT-SIZE: 10pt" lang=EN-GB>Omar Katanani<BR>Sustainable Design Engineer</SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: navy; FONT-SIZE: 10pt" lang=EN-GB>Email: <A href="mailto:omar@ecoconsulting.net" rel=nofollow target=_blank ymailto="mailto:omar@ecoconsulting.net">omar@ecoconsulting.net</A></SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: navy" lang=EN-GB> </SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: navy; FONT-SIZE: 7.5pt" lang=EN-GB>EcoConsulting (Lebanon)<BR>Chawkatly Building (Valli & Valli), 6<SUP>th</SUP> floor</SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: navy; FONT-SIZE: 7.5pt" lang=EN-GB>Charles Helou Street, Saifi District</SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: navy; FONT-SIZE: 7.5pt" lang=EN-GB>Beirut, Lebanon   <BR>Mobile:    +961 (0) 3 045 045</SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN lang=EN-GB> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: navy; FONT-SIZE: 7.5pt" lang=EN-GB>EcoConsulting (UK) Ltd<BR>28 Marshalsea Road<BR>London, SE1 1HF<BR>Tel:  +44 (0) 207 939 0989<BR>Fax:  +44 (0) 207 939 0981</SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: navy; FONT-SIZE: 7.5pt" lang=EN-GB>Website: <A href="http://www.ecoconsulting.net/" rel=nofollow target=_blank>www.ecoconsulting.net</A></SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN lang=EN-GB> </SPAN></P>
<P style="MARGIN: 0in 0in 0pt"><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: navy; FONT-SIZE: 10pt" lang=EN-GB> <IMG id=_x0000_i1027 border=0 src="cid:4.155196273@web52801.mail.re2.yahoo.com" width=870 height=102></SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'sans-serif'; COLOR: navy; FONT-SIZE: 10pt" lang=EN-GB> </SPAN><SPAN lang=EN-GB></SPAN></P>
<P class=MsoNormal><SPAN lang=EN-GB> </SPAN></P>
<P class=MsoNormal><SPAN lang=EN-GB> </SPAN></P>
<P class=MsoNormal><SPAN lang=EN-GB> </SPAN></P>
<P class=MsoNormal><SPAN lang=EN-GB> </SPAN></P>
<DIV style="TEXT-ALIGN: center" class=MsoNormal align=center>
<HR align=center SIZE=2 width="100%">
</DIV>
<P class=MsoNormal>_______________________________________________<BR>Equest-users mailing list<BR>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<BR>To unsubscribe from this mailing list send  a blank message to <A href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" rel=nofollow target=_blank ymailto="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</A></P></BLOCKQUOTE></DIV></DIV></DIV></div><br>
      </body></html>