<font face="Times New Roman, Times, serif">In your air side HVAC
section go into the zone level and check that your sizing option is set
to "adjust loads".&nbsp; If it is from loads go to the summary tab and
change all your zones.&nbsp; Also beside that is throttling range, you can
try adjusting that upwards say to 4 deg.&nbsp; You can also change your
control zone to see it this helps.&nbsp; If your AHU is off at night you can
also adjust it to come on before the occupancy.&nbsp; You SS-O report will
show this if the hours are lumped near the start up time.&nbsp; Then add
more heat as Pasha said.<br>
Bruce Easterbrook P.Eng.<br>
Abode Engineering<br>
</font><br>
On 10/06/2010 10:55 PM, Pasha Korber-Gonzalez wrote:
<blockquote
 cite="mid:AANLkTil3S_JgwdLM6LJJMcWGGvXCac0HxrNmphoSdQU_@mail.gmail.com"
 type="cite">
  <div>I have found with my own projects that even sometimes when the
HVAC designer has specified a specific capacity for htg water equipment
that sometime in my model file I still have unmet loads for htg.&nbsp; I
suggest at this point specify additional htg capacity by either
increasing the reheat delta-T from say 30F to 50F and/or adding zone
level baseboards.&nbsp; By adding the baseboards you are adding a component
of the system that will supplement the skin losses being experienced by
the simulation model.</div>
  <div>&nbsp;</div>
  <div>by adding baseboards for the additional requrired heat then you
should be able to meet your heating loads.</div>
  <div>&nbsp;</div>
  <div>hope this helps,</div>
  <div>pasha<br>
  <br>
  </div>
  <div class="gmail_quote">On Thu, Jun 10, 2010 at 7:38 PM, Robert Des
Rosiers <span dir="ltr">&lt;<a moz-do-not-send="true"
 href="mailto:desrosiers@studioma.com">desrosiers@studioma.com</a>&gt;</span>
wrote:<br>
  <blockquote
 style="border-left: 1px solid rgb(204, 204, 204); margin: 0px 0px 0px 0.8ex; padding-left: 1ex;"
 class="gmail_quote">
    <div vlink="purple" link="blue" lang="EN-US">
    <div>
    <p class="MsoNormal">All:</p>
    <p class="MsoNormal">I have completed an energy model for a
baseline scenario from which to compare my proposed design.&nbsp; The
baseline HVAC system is a constant volume single zone AHU w/ no reheat;
the AHU is served by HW and CHW loop from a central plant.&nbsp; I have set
this up in eQuest as a "Variable Air Volume" system type with the AHU
fan control set to "Constant Volume"; my thought here is that each zone
fed by the AHU will control temperature using a VAV box w/ no local
reheat or cooling.&nbsp; Flow and temperature from the AHU will be delivered
based on the coolest or warmest zone it serves.</p>
    <p class="MsoNormal">&nbsp;</p>
    <p class="MsoNormal">All seems fine with the design flows,
ventilation flows and cooling capacities.&nbsp; My problem is with the
heating capacity as I have excessive unmet heating hours (50,000).&nbsp; I
have allowed eQuest to size the heating capacity of the preheat and
heating coil as well as the minimum flow ratios.&nbsp; <u>Does anyone have
any thoughts as to what is causing these unmet heating load hours?&nbsp; Is
the way I have set-up the desired baseline HVAC system incorrect?</u></p>
    <p class="MsoNormal">&nbsp;</p>
    <p class="MsoNormal">Any guidance is greatly appreciated.&nbsp; Thanks -</p>
    <p class="MsoNormal">&nbsp;</p>
    <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Robert
Des Rosiers, LEED-AP</span></p>
    <p class="MsoNormal"><b><span style="color: rgb(31, 73, 125);">STUDIO
MA</span></b></p>
    <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">130 N
Central Avenue, No.300 Phoenix, Arizona 85004</span></p>
    <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Telephone
602 251 3800</span></p>
    <p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Fax 602
251 3100</span></p>
    <p class="MsoNormal">&nbsp;</p>
    </div>
    </div>
    <br>
_______________________________________________<br>
Equest-users mailing list<br>
    <a moz-do-not-send="true"
 href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
 target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send &nbsp;a blank message to <a
 moz-do-not-send="true"
 href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
    <br>
  </blockquote>
  </div>
  <br>
  <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
  </pre>
</blockquote>
</body>
</html>