<div>I have found with my own projects that even sometimes when the HVAC designer has specified a specific capacity for htg water equipment that sometime in my model file I still have unmet loads for htg.  I suggest at this point specify additional htg capacity by either increasing the reheat delta-T from say 30F to 50F and/or adding zone level baseboards.  By adding the baseboards you are adding a component of the system that will supplement the skin losses being experienced by the simulation model.</div>

<div> </div>
<div>by adding baseboards for the additional requrired heat then you should be able to meet your heating loads.</div>
<div> </div>
<div>hope this helps,</div>
<div>pasha<br><br></div>
<div class="gmail_quote">On Thu, Jun 10, 2010 at 7:38 PM, Robert Des Rosiers <span dir="ltr">&lt;<a href="mailto:desrosiers@studioma.com">desrosiers@studioma.com</a>&gt;</span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-US" vlink="purple" link="blue">
<div>
<p class="MsoNormal">All:</p>
<p class="MsoNormal">I have completed an energy model for a baseline scenario from which to compare my proposed design.  The baseline HVAC system is a constant volume single zone AHU w/ no reheat; the AHU is served by HW and CHW loop from a central plant.  I have set this up in eQuest as a &quot;Variable Air Volume&quot; system type with the AHU fan control set to &quot;Constant Volume&quot;; my thought here is that each zone fed by the AHU will control temperature using a VAV box w/ no local reheat or cooling.  Flow and temperature from the AHU will be delivered based on the coolest or warmest zone it serves.</p>

<p class="MsoNormal"> </p>
<p class="MsoNormal">All seems fine with the design flows, ventilation flows and cooling capacities.  My problem is with the heating capacity as I have excessive unmet heating hours (50,000).  I have allowed eQuest to size the heating capacity of the preheat and heating coil as well as the minimum flow ratios.  <u>Does anyone have any thoughts as to what is causing these unmet heating load hours?  Is the way I have set-up the desired baseline HVAC system incorrect?</u></p>

<p class="MsoNormal"> </p>
<p class="MsoNormal">Any guidance is greatly appreciated.  Thanks -</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="COLOR: #1f497d">Robert Des Rosiers, LEED-AP</span></p>
<p class="MsoNormal"><b><span style="COLOR: #1f497d">STUDIO MA</span></b></p>
<p class="MsoNormal"><span style="COLOR: #1f497d">130 N Central Avenue, No.300 Phoenix, Arizona 85004</span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d">Telephone 602 251 3800</span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d">Fax 602 251 3100</span></p>
<p class="MsoNormal"> </p></div></div><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>