Set your snap temperature lower.  It should do the trick.  See the definition of Snap in the help files below:<br><br><p class="CodeWord">SNAP                          A control mode where the loop 
operation snaps on or off according to a monitored temperature. SNAP has 
slightly different meanings depending on the type of loop:</p>
<p class="ListBulletCode" style=""><span style="font-family: 'Courier New';">o  </span>For a heating-type loop, this 
keyword will cause the loop to activate when a specified temperature sensor is 
below the SNAP-T value. An outside-air lockout is another way of thinking of 
this control mode; however, the temperature causing the lockout may be either 
the outdoor air temperature, or a zone temperature. You specify the location of 
the temperature sensor using the SNAP-LOCN and SNAP-ZONE keywords.</p>
<p class="ListBulletCode" style=""><span style="font-family: 'Courier New';">o  </span>Cooling-type loops are similar to 
heating-type loops, except that the loop will activate when the monitored 
temperature is above the SNAP-T value.</p>
<p class="ListBulletCode" style=""><span style="font-family: 'Courier New';">o  </span>2-pipe loops will be in the heating 
mode below SNAP-T, and in the cooling mode above SNAP-T. In other words, the 
SNAP-T is the changeover temperature. Note, however, that a changeover 
temperature deadband can be specified using the HEATING-SCH and COOLING-SCH 
described under the next code-word.</p>
<p class="ListBulletCode" style=""><span style="font-family: 'Courier New';">o  </span>WLHP loops will enable the heating 
equipment when below the SNAP-T, and the heat-rejection equipment above the 
SNAP-T. In practice, this is a dangerous control mode for WLHP's as the loop may 
go to an extreme temperature when either type of primary equipment is 
disabled.</p><br><br><div class="gmail_quote">On Tue, Jun 8, 2010 at 4:58 AM, tsea2005 <span dir="ltr"><<a href="mailto:tsea2005@163.com">tsea2005@163.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">




<div style="margin: 10px; font-family: verdana; font-size: 10pt;">
<div><font face="Verdana" size="2"></font> </div>
<div><font face="Verdana" size="2">HI :</font></div>
<div> </div>
<div><font face="Verdana" size="2">How to turn off the hot water loop in the RHFS 
? I have choose the loop operation at snap ,and set the snap temp at 120 ,but 
the hot water loop still work ,in the report ,there is still have space heating. 
How to turn off ?</font></div>
<div align="left"><font color="#c0c0c0" face="Verdana" size="2">2010-06-08 
</font></div><font face="Verdana" size="2">
<hr style="width: 122px; min-height: 2px;" align="left" size="2">

<div><font color="#c0c0c0" face="Verdana" size="2"><span>tsea2005</span> 
</font></div></font></div>