Thanks for your thoughts and here is your answers:<br><br>1) yes, but there is no night set back time.<br>2) everything is 100% oa and constant volume 24/7/365<br>3)no exhaust heat recovery, and steam preheat.  the thermostat is set for 70 - 73 heating and cooling and the set back is to 60 and 80 at night for my parametric run.<br>
4) the cooling comes from a central chilled water plant for the entire campus, and i just created a chilled water loop, added a meter and a pump and it seems to be running happily.<br>5) the fans run all the time, day and night<br>
6) I do have internal loads with latent heat, and it cycles down at night to almost nothing.  These loads are currently the same for the model and the parametric run.<br>7) i have set humidity levels to 20% and 53%, which also do not change with my parametric run.  <br>
<br>hope this give you enough information.<br><br>thanks again<br><br><div class="gmail_quote">On Wed, May 19, 2010 at 11:13 AM, David Bastow <span dir="ltr"><<a href="mailto:dbastow@mcclure-engineering.com">dbastow@mcclure-engineering.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">



<div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial" size="2">Rob,</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial" size="2"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" face="Arial" size="2">I have a number of questions:</font></span></div>
<ol dir="ltr">
  <li>
  <div align="left"><span><font color="#0000ff" face="Arial" size="2">Do you have many lab hoods?  And are exhaust and make-up air 
  revised for the lab hoods at the night set back time?</font></span></div></li>
  <li>
  <div align="left"><span><font color="#0000ff" face="Arial" size="2">What is the percent of outside air to the lab?  Does this 
  percentage change during the night set back time?</font></span></div></li>
  <li>
  <div align="left"><span><font color="#0000ff" face="Arial" size="2">Do you have a pre-heat or exhaust heat recovery and 
  pre-cooling on your make-up air?  What is the temperature setting of 
  this pre-heat or heat recovery and pre-cooling?  Does the temperature 
  settings on these change at the night set back 
  time?</font></span></div></li>
  <li>
  <div align="left"><span><font color="#0000ff" face="Arial" size="2">Do you utilize an air or water side economizer for 1st stage 
  cooling?  Does this use change any at night set back 
  time?</font></span></div></li>
  <li>
  <div align="left"><span><font color="#0000ff" face="Arial" size="2">Does the fan run continuously day and night?  Have you ran 
  models with the fan running continuously, and with fan cycling based on demand 
  at night and off completely at night, to see how the results 
  compare?</font></span></div></li>
  <li>
  <div align="left"><span><font color="#0000ff" face="Arial" size="2">Do you have a internal load watts per square foot and latent 
  load on the space from interior lighting and equipment?  Do these 
  loads change at the night set back time?</font></span></div></li>
  <li>
  <div align="left"><span><font color="#0000ff" face="Arial" size="2">Are you adding humidification or dehumidifying the space based on 
  some humidity settings?  Does the humidity settings change during the 
  night set back time?</font></span></div></li></ol>
<div><span></span><font face="Arial"><font color="#0000ff"><font size="2">One of these things is probably causing the increased chilled water cooling load.  Often if you have high internal loads, even at night, then changes to the fan cycling and the amount of outside air brought in<span> at 
night,</span> will increase the chilled water cooling load.  I would review all of these areas and run various test models to see how they each affect your energy usage when modified.</font></font></font></div>
<div><font face="Arial"><font color="#0000ff"><font size="2"></font></font></font> </div>
<div><font color="#0000ff" face="Arial" size="2"><span>Our 
firm just completed modeling some very large lab facilities with more than 55 
exhaust hoods in the building, with high internal loads 24/7 and 100% 
outside air.  As long as the models are set up correctly they are normally 
right.  It takes some real design and thermal dynamic thought and often may 
models to really get your mind right with what is truly going on with the 
facility.  Its important to keep an open mind to what is going on.  
Having been doing computer hourly modeling for over 17 years, it is often easy 
to think you have a handle on what is going on with the building, but it is 
important to keep an open mind and investigate all the different avenues that 
you can think of until figure out what is going on.  I have 99% of the time 
that I have blamed the screwy program having problems that I have found that I 
just didn't look at all the different angles enough.</span></font></div>
<div><font color="#0000ff" face="Arial" size="2"><span></span></font> </div>
<div><font color="#0000ff" face="Arial" size="2"><span>
<div align="left">
<div align="left"><b><i><font color="#0000ff" face="Bradley Hand ITC" size="6">David A. Bastow </font></i></b></div>
<div align="left"><b><i><font face="Rockwell Extra Bold">McClure 
Engineering, Inc.  </font></i></b></div>
<div align="left"><font face="Batang"><a title="http://www.mcclure-engineering.com/" href="http://www.mcclure-engineering.com/" target="_blank"><font title="http://www.mcclure-engineering.com/" color="#0000ff" face="Arial" size="2"></font></a></font> </div>
</div></span></font></div>
<div><br></div>
<div dir="ltr" align="left" lang="en-us">
<hr>
<font face="Tahoma" size="2"><b>From:</b> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> 
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Rob 
Hudson<br><b>Sent:</b> Wednesday, May 19, 2010 7:46 AM<br><b>To:</b> 
<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] T-Stat is 
acting Screwy<br></font><br></div><div class="im">
<div></div>I have a lab space that is kept between 73 and 70 degrees all year 
long.  One of my parametric runs has the cooling and heating T-stat 
schedules changing to have night time setbacks to 80 and 60, respectively.  
When i use these, i get more energy spent overall.  specifically, i have a 
chilled water meter, steam meter, electric meter and hot water meter to monitor 
everything.  The chilled water increases while the others slightly decrease 
when i use the set back schedules.  Any ideas?<br clear="all"><br>-- <br>Rob 
Hudson<br></div></div>
</blockquote></div><br><br clear="all"><br>-- <br>Rob Hudson<br>