Hi Nick,<br><br>I don't know why but this came across as Wide. I find my tiny brain cannot focus on it when it is WIDE.<br><br>Help me!<br>Carol<br><br><div class="gmail_quote">On Fri, May 7, 2010 at 3:34 PM, Nick Caton <span dir="ltr"><<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">









<div link="blue" vlink="purple" lang="EN-US">

<div>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Eric,</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">I’m following your line of thinking… but I’m
still stumped as to the root cause…  If the design CFM was too low and
that’s why Z>1.0, wouldn’t there be a warning for that?  I
have a bunch of items referencing the library VSD curve in question so it’s
not easy for me to check all the potentially awry hourly results – but I
may need to go down that path…</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Carol,</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">ATTN is the report we can look at in the SIM file after running
a simulation – a screenshot follows.  It displays any cautions/warnings/errors
encountered when a simulation is attempted/completed.  Sorry for the minor
censoring but this is one of those “top-secret nuclear facilities”
we keep referencing for which I might get in actual trouble otherwise =).  It’s
a different project but similar caution popping up on the last day of the year.</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">As a related aside and general DOE2 inquiry – I’ve
been trying to enter the following line into my .inp file in various locations prior
to running a simulation, but I cannot get it to stick (eQuest seems to ignore
or erase it wherever I put it as soon as I try to run a simulation):  DIAGNOSTIC
WARNINGS ..</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">The idea is to have this ATTN report, which I’m
occasionally asked to present along with explanations, not show cautions (after
determining they are indeed erroneous, of course!).  Am I chasing my own
tail trying to put this into the .inp file?  Is there somewhere in the
eQuest interface we’re permitted to specify a DIAGNOSTIC option other
than the default CAUTIONS?</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"><img src="cid:image002.png@01CAEE08.83F6F770" alt="untitled.PNG" width="1260" height="747"></span><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>
<div class="im">

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"><img src="cid:image003.jpg@01CAEE08.83F6F770" alt="cid:489575314@22072009-0ABB" width="119" height="37"></span><b><span style="font-size: 11pt; color: rgb(45, 77, 94);"></span></b></p>


<p class="MsoNormal"><b><span style="font-size: 11pt; color: rgb(45, 77, 94);"> </span></b></p>

<p class="MsoNormal"><b><span style="font-size: 11pt; color: rgb(45, 77, 94);">NICK CATON, E.I.T.</span></b><b><span style="color: rgb(45, 77, 94);"></span></b></p>

<p class="MsoNormal"><span style="font-size: 7.5pt; color: rgb(204, 153, 0);">PROJECT ENGINEER</span><span style="font-size: 7.5pt; color: rgb(204, 153, 0);"></span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">25501 west valley parkway</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">olathe ks 66061</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">direct 913 344.0036</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: rgb(45, 77, 94);">fax 913 345.0617</span></p>

<p class="MsoNormal"><i><span style="font-size: 10pt; color: rgb(45, 77, 94);">Check out our new web-site @ </span></i><span style="font-size: 11pt; color: rgb(31, 73, 125);"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size: 10pt;">www.smithboucher.com</span></a></span><u><span style="font-size: 10pt; color: blue;"> </span></u><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>


<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

</div><div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">

<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;"> Carol Gardner
[mailto:<a href="mailto:cmg750@gmail.com" target="_blank">cmg750@gmail.com</a>] <br>
<b>Sent:</b> Friday, May 07, 2010 12:23 AM<br>
<b>To:</b> Eric O'Neill<br>
<b>Cc:</b> Nick Caton; eQUEST Users List<div><div></div><div class="h5"><br>
<b>Subject:</b> Re: [Equest-users] CAUTION: Variable Speed Drive FPLR???</div></div></span></p>

</div><div><div></div><div class="h5">

<p class="MsoNormal"> </p>

<p class="MsoNormal" style="margin-bottom: 12pt;">What the heck is an ATTN
screen?? Is it a LEED thingy??<br>
<br>
Confused in Portland,<br>
Carol</p>

<div>

<p class="MsoNormal">On Thu, May 6, 2010 at 12:39 PM, Eric O'Neill <<a href="mailto:elo@michaelsengineering.com" target="_blank">elo@michaelsengineering.com</a>>
wrote:</p>

<div>

<div>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Nick,</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">I’m not sure I can answer your
question. Maybe someone can pick up on this line of thought though to answer
the question.</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">If you play with the numbers, a PLR of
1.1 is yielding that fan vsd signal of 1.257. I believe the PLR is calculated
as (the current hour’s CFM)/(design CFM). So whatever’s going on
here is causing the system to call for (or think it has) a CFM value 10%
greater than design. Also, the function is supposed to set any outputs above
the set maximum (in this case 1) to the maximum, so I’m not sure what
about the last day of the year is causing it to ignore the maximum output
value. </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">When I look at the hourly reports on a
system that’s using that curve and getting that error at 12/31/24, my PLR
(variable 60) looks fine, and the CFM is at its minimum. So I don’t think
it’s a real issue. I’m also not very BDL/DOE2 literate, so I might
be looking at this wrong.</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Also, if you really wanted a clean ATTN
screen, you could just set your max output from that function to 1.28 ;-)</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Cheers,</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Eric</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<div>

<div style="border-width: 1pt medium medium; border-style: solid none none; padding: 3pt 0in 0in; border-color: -moz-use-text-color;">

<p class="MsoNormal" style="margin-left: 0.5in;"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of
</b>Nick Caton<br>
<b>Sent:</b> Thursday, May 06, 2010 12:32 PM<br>
<b>To:</b> Carol Gardner</span></p>

<div>

<div>

<p class="MsoNormal"><span style="font-size: 10pt;"><br>
<b>Cc:</b> eQUEST Users List<br>
<b>Subject:</b> Re: [Equest-users] CAUTION: Variable Speed Drive FPLR???</span></p>

</div>

</div>

</div>

</div>

<div>

<div>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Thanks Carol!</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);">I’m glad
to see some supporting information to assure me this CAUTION is likely not a
big deal, but it still kinda irks me that this is message is often the only
thing between me and a perfectly blank ATTN report in my models…</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);">If anyone can
offer some insight regarding this VSD curve message’s meaning and/or
root-causes, I’d be very grateful to either figure out a way to eliminate
these CAUTIONS, or to otherwise be able to sleep at night knowing I can provide
an in-depth response regarding its meaning and why it’s not a big deal
and ignore-able.</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);">~Nick</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);"><img src="cid:image003.jpg@01CAEE08.83F6F770" alt="cid:489575314@22072009-0ABB" width="119" border="0" height="37"></span></p>


<p class="MsoNormal" style="margin-left: 0.5in;"><b><span style="font-size: 11pt; color: rgb(45, 77, 94);"> </span></b></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><b><span style="font-size: 11pt; color: rgb(45, 77, 94);">NICK CATON,
E.I.T.</span></b></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 7.5pt; color: rgb(204, 153, 0);">PROJECT ENGINEER</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 10pt; color: rgb(45, 77, 94);">25501 west
valley parkway</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 10pt; color: rgb(45, 77, 94);">olathe ks 66061</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 10pt; color: rgb(45, 77, 94);">direct 913
344.0036</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 10pt; color: rgb(45, 77, 94);">fax 913 345.0617</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><i><span style="font-size: 10pt; color: rgb(45, 77, 94);">Check out our
new web-site @ </span></i><span style="font-size: 11pt; color: rgb(31, 73, 125);"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size: 10pt;">www.smithboucher.com</span></a></span><u><span style="font-size: 10pt; color: blue;"> </span></u></p>


<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<div style="border-width: 1pt medium medium; border-style: solid none none; padding: 3pt 0in 0in; border-color: -moz-use-text-color;">

<p class="MsoNormal" style="margin-left: 0.5in;"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;"> Carol Gardner [mailto:<a href="mailto:cmg750@gmail.com" target="_blank">cmg750@gmail.com</a>] <br>

<b>Sent:</b> Thursday, May 06, 2010 12:25 PM<br>
<b>To:</b> Nick Caton<br>
<b>Cc:</b> eQUEST Users List<br>
<b>Subject:</b> Re: [Equest-users] CAUTION: Variable Speed Drive FPLR???</span></p>

</div>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p style="margin-left: 0.5in;">Here you go Nick. This is in your 3-63 data area as
DOE-2.chm. There is tons of info there. Cautions are the least of your worries.</p>

<p style="margin-left: 0.5in;">ERRORS                     
Diagnostics deal with problems in the input that must be corrected before the
simulation will execute. </p>

<p style="margin-left: 0.5in;">WARNINGS                
Diagnostics are concerned with input data that can be used in the simulation
but are probably erroneous (such as a temperature input of 700 instead of
70.0). </p>

<p style="margin-left: 0.5in;">CAUTIONS                  
Diagnostics are much less severe than WARNINGS messages and deal with questionable
input value that do not significantly affect the results of the simulation.
This is the default level.</p>

<p style="margin-left: 0.5in;">Regards,</p>

<p style="margin-left: 0.5in;">Carol</p>

<p class="MsoNormal" style="margin-bottom: 12pt; margin-left: 0.5in;"> </p>

<div>

<p class="MsoNormal" style="margin-left: 0.5in;">On Thu, May 6, 2010 at 9:32 AM, Nick Caton <<a href="mailto:ncaton@smithboucher.com" target="_blank">ncaton@smithboucher.com</a>>
wrote:</p>

<div>

<div>

<p class="MsoNormal" style="margin-left: 0.5in;">On many projects, I’ve run into the following typical
CAUTION in my SIM ATTN report:</p>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p style="margin-left: 0.5in;"><span style="font-size: 8pt; font-family: "Courier New";"> </span></p>

<p style="margin-left: 0.5in;"><span style="font-size: 8pt; font-family: "Courier New";"> **CAUTION**********************************************************************</span></p>

<p style="margin-left: 0.5in;"><span style="font-size: 8pt; font-family: "Courier New";">            
In curve: Variable Speed Drive FPLR       
the dependent value</span></p>

<p style="margin-left: 0.5in;"><span style="font-size: 8pt; font-family: "Courier New";">            
is exceeding the limits.</span></p>

<p style="margin-left: 0.5in;"><span style="font-size: 8pt; font-family: "Courier New";">            
Value/Min/Max/First time:         
1.257         
0.100          1.000 
12/31/24</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p class="MsoNormal" style="margin-left: 0.5in;">It’s <u>always</u> referencing this specific library
VSD curve, and it <u>always</u> occurs in the last hours of the very last day
of the modeled year.  I’ve seen it so much I’m pretty certain
that particular value 1.257 is always present too.</p>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p class="MsoNormal" style="margin-left: 0.5in;">What are the implications here to the modeled behavior? 
Is this caution something of concern?  Is something off with the library
curve?</p>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p class="MsoNormal" style="margin-left: 0.5in;">I’ve always assumed that if something is only off in
the last hours of the modeled year, it shouldn’t be a big deal –
but it’s bugging me that I’m seeing this come up again and again
and I don’t know what it really means…</p>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p class="MsoNormal" style="margin-left: 0.5in;">~Nick</p>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p class="MsoNormal" style="margin-left: 0.5in;"><img src="cid:image003.jpg@01CAEE08.83F6F770" alt="cid:489575314@22072009-0ABB" width="119" border="0" height="37"></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><b><span style="color: rgb(45, 77, 94);"> </span></b></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><b><span style="color: rgb(45, 77, 94);">NICK CATON, E.I.T.</span></b></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 7.5pt; color: rgb(204, 153, 0);">PROJECT ENGINEER</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 10pt; color: rgb(45, 77, 94);">25501 west
valley parkway</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 10pt; color: rgb(45, 77, 94);">olathe ks 66061</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 10pt; color: rgb(45, 77, 94);">direct 913
344.0036</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><span style="font-size: 10pt; color: rgb(45, 77, 94);">fax 913 345.0617</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><i><span style="font-size: 10pt; color: rgb(45, 77, 94);">Check out our
new web-site @ </span></i><span style="color: rgb(31, 73, 125);"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size: 10pt;">www.smithboucher.com</span></a></span><u><span style="font-size: 10pt; color: blue;"> </span></u></p>


<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

</div>

</div>

<p class="MsoNormal" style="margin-bottom: 12pt; margin-left: 0.5in;"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>

</div>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

</div>

</div>

</div>

</div>

</div>

<p class="MsoNormal"> </p>

</div></div></div>

</div>


</blockquote></div><br><div style="visibility: hidden; display: inline;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup {  position:absolute;  z-index:9999;  padding: 0px 0px;  margin-left: 0px;  margin-top: 0px;  width: 240px;  overflow: hidden;  word-wrap: break-word;  color: black;  font-size: 10px;  text-align: left;  line-height: 13px;}</style>