Setting Maximum Heating Rate to 1 Btu/h gets rid of heating. On air-side hvac zone parameter screen, under heating tab. Change 1 time using your screen then find it under the spreadsheet option where you can copy and paste.<br>
<br>Note: you may still see a heating load on SV-A but you should have no heating energy use.<br><br>Another issue comes to mind: how to do this using a schedule so you can have heat when you want it.<br><br>Peace,<br>Carol<br>
<br><div class="gmail_quote">On Fri, May 7, 2010 at 1:13 PM, Paul Brooks <span dir="ltr"><<a href="mailto:equestpaul@yahoo.com">equestpaul@yahoo.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div><div style="font-family: times new roman,new york,times,serif; font-size: 12pt;"><div>I am getting a heat load in the middle of the cooling season. I don't believe it. the system is VAV, chilled water with reheat coils at the boxes only. Office Building in a semi-tropical zone (3). </div>
<div> </div>
<div>I understand that I should be able to turn the heat off/make unavailable, but the instructions on how seem cryptic.....that or my brain is overloaded. Can someone provide a quick answer ton how to do it?</div>
<div> </div>
<div>Thanks!</div>
<div> </div>
<div> </div></div><br>
</div><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><div style="visibility: hidden; display: inline;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup { position:absolute; z-index:9999; padding: 0px 0px; margin-left: 0px; margin-top: 0px; width: 240px; overflow: hidden; word-wrap: break-word; color: black; font-size: 10px; text-align: left; line-height: 13px;}</style>