Lauren,<br><br>What is the system type?<br><br>Carol<br><br><div class="gmail_quote">On Thu, May 6, 2010 at 3:39 PM, Pasha Korber-Gonzalez <span dir="ltr"><<a href="mailto:pasha.pkconsulting@gmail.com">pasha.pkconsulting@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;"><div>There are so many things that can contribute to this issue or it could be a lack of inputs that may be causing some issues. It depends, on underheating or undercooling, it depends if all of the hours are happening in one zone only or spread across all the zones?</div>
<div> </div>
<div>You'll need to start by reviewing the SS-F and SS-R reports to get more insight, then you might want to look at the SS-O reports for the specific zones that are troubled. Sometimes it can be affected by schedules, or by lack of inputs, or equipment sizing ratios, or by specifying CFM's or equipment capacities, or , or, or....there are so many things that could affect this.</div>
<div> </div>
<div>Suggestions are to do a little engineering analysis on what could be causing the types of under-conditioning you are getting, (i.e. is it because there is not enough CFM being supplied to handle the loads?), next you could do experiements by "turning off" some of the inputs that you have used and see if one of those is the culprit, or you can ask someone else to look at your file. You are welcome to send your .pd2 & .inp files to us and maybe someone will have some time to take a look at it and help find your issue.</div>
<div> </div>
<div>pasha<br><br></div>
<div class="gmail_quote"><div><div></div><div class="h5">On Thu, May 6, 2010 at 4:24 PM, Lauren Rosenthal <span dir="ltr"><<a href="mailto:Lauren.Rosenthal@arup.com" target="_blank">Lauren.Rosenthal@arup.com</a>></span> wrote:<br>
</div></div><blockquote style="border-left: 1px solid rgb(204, 204, 204); margin: 0px 0px 0px 0.8ex; padding-left: 1ex;" class="gmail_quote"><div><div></div><div class="h5">
<div vlink="purple" link="blue" lang="EN-US">
<div>
<p class="MsoNormal">All,</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">What are some common sources/inputs that could cause unmet load hours, especially for cooling hours?</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Almost all of my systems are creating unmet load hours and I’m not sure what inputs could be the cause.</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Any suggestions would be greatly appreciated.</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Thanks,</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="color: gray; font-size: 10pt;">____________________________________</span></p>
<p class="MsoNormal"><span style="color: gray; font-size: 10pt;">Lauren Rosenthal</span><span style="color: gray;"></span></p>
<p class="MsoNormal"><span style="color: gray; font-size: 10pt;">Mechanical Engineer</span><span style="color: gray;"></span></p>
<p class="MsoNormal"><span style="color: gray;"> </span></p>
<p class="MsoNormal"><span style="color: gray; font-size: 10pt;">Los Angeles CA</span><span style="color: gray;"></span></p>
<p class="MsoNormal"> </p></div><pre style="white-space: normal;">____________________________________________________________<br>Electronic mail messages entering and leaving Arup business<br>systems are scanned for acceptability of content and viruses<br>
</pre></div><br></div></div>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><div style="visibility: hidden; display: inline;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup { position:absolute; z-index:9999; padding: 0px 0px; margin-left: 0px; margin-top: 0px; width: 240px; overflow: hidden; word-wrap: break-word; color: black; font-size: 10px; text-align: left; line-height: 13px;}</style>