Hi, <div>thank you all...again the alternating solar gain factor is thorn in my flesh...i was actually looking for  hourly data for New Delhi for eight orientations (N,S,E,W,NW,NE,SW,SE)...</div><div>just in case anybody is familiar with the Admittance Procedure here is the formula</div>
<div><br></div><div>Qs(swing)-Swing in Fluctuating gains for Transparent surfaces.</div><div>A-Area of the glazing</div><div>I-Intensity</div><div>S-Solar Gain Factor</div><div> </div><div>Formula</div><div><b>Qs(swing)=A X I(swing) X S(swing)</b></div>
<div>where, I(swing)=Intensity(at time t) - Average Intensity</div><div>& S(swing)=S(at time t)-Average S</div><div><br></div><div><div>here is what Nick had suggested...but having tried that i didnt quite get the right results...maybe i am doing some thing wrong.....I would get S=.86 for all sunshine hours(mult factor=1) & S=0 for the night(& early morning) hours when there is no sunshine (mult factor=0) but here is a gist of the previous brainstorming session..</div>
<div><br></div><div><br></div></div><span class="Apple-style-span" style="font-family: arial, sans-serif; font-size: 13px; border-collapse: collapse; "><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; ">
<span style="font-size: 11pt; color: rgb(31, 73, 125); ">Hi Piyush,</span></p><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><span style="font-size: 11pt; color: rgb(31, 73, 125); "> </span></p>
<p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><span style="font-size: 11pt; color: rgb(31, 73, 125); ">Apologies, I wasn’t sure whether you meant SHGF. </span></p>
<p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><span style="font-size: 11pt; color: rgb(31, 73, 125); "> </span></p><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; ">
<span style="font-size: 11pt; color: rgb(31, 73, 125); ">I did some googling to check my vocabulary and found this reference:  <a href="http://www.levolux.com/L_PDF_Files/Lev.%20Comp%20Analysis%20Table.pdf" target="_blank" style="color: rgb(42, 93, 176); "><span style="font-size: 12pt; font-family: 'Times New Roman', serif; ">http://www.levolux.com/L_PDF_Files/Lev. Comp Analysis Table.pdf</span></a></span></p>
<p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><span style="font-size: 11pt; color: rgb(31, 73, 125); "> </span></p><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; ">
<span style="font-size: 11pt; color: rgb(31, 73, 125); ">It looks like:  Solar Gain Factor (S Factor) = Shading Coefficient (SC) * 0.87</span></p><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; ">
<span style="font-size: 11pt; color: rgb(31, 73, 125); ">I can add that:  Shading Coefficient (SC) = (Center of Glass SHGF) / 0.87</span></p><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; ">
<span style="font-size: 11pt; color: rgb(31, 73, 125); "> </span></p><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><span style="font-size: 11pt; color: rgb(31, 73, 125); ">So to answer your first question, while this is the first time I’ve personally run into S Factors, it would appear they’re analogous to a center-of-glass SHGF, but can vary based on external shading devices (including trees, curtains and shades) per the above.  I’m copying eQuest-users to share the following procedure and to allow others to correct any misunderstandings we may have regarding what S Factor really means – I hope you don’t mind!</span></p>
<p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><span style="font-size: 11pt; color: rgb(31, 73, 125); "> </span></p><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; ">
<span style="font-size: 11pt; color: rgb(31, 73, 125); ">So per your second inquiry to determine the hourly S Factors, and because I was curious, here’s a procedure:</span></p><p><span style="font-size: 11pt; color: rgb(31, 73, 125); "><span>-<span style="font: normal normal normal 7pt/normal 'Times New Roman'; ">          </span></span></span><span style="font-size: 11pt; color: rgb(31, 73, 125); ">Set up your windows and all variable shading items.</span></p>
<p><span style="font-size: 11pt; color: rgb(31, 73, 125); "><span>-<span style="font: normal normal normal 7pt/normal 'Times New Roman'; ">          </span></span></span><span style="font-size: 11pt; color: rgb(31, 73, 125); ">Create an hourly report/block for the window(s) in question selecting the items shown in the  screengrab below – SC and “Value by which…” SC multiplier for those of you in the archives.</span></p>
<p><span style="font-size: 11pt; color: rgb(31, 73, 125); "><span>-<span style="font: normal normal normal 7pt/normal 'Times New Roman'; ">          </span></span></span><span style="font-size: 11pt; color: rgb(31, 73, 125); ">Run the simulation and open the hourly results up in excel (hit the ‘hourly results’ button in the sim viewer).</span></p>
<p><span style="font-size: 11pt; color: rgb(31, 73, 125); "><span>-<span style="font: normal normal normal 7pt/normal 'Times New Roman'; ">          </span></span></span><span style="font-size: 11pt; color: rgb(31, 73, 125); ">Multiply those values across to get your hourly effective SC, and again by 0.87 to get an hourly S Factor.</span></p>
<div class="im" style="color: rgb(80, 0, 80); "><p class="MsoNormal" style="margin-top: 0px; margin-right: 0px; margin-bottom: 0px; margin-left: 0px; "><span style="font-size: 11pt; color: rgb(31, 73, 125); "> </span></p>
</div></span><div><span class="Apple-style-span" style="font-family: arial, sans-serif; font-size: 15px; border-collapse: collapse; color: rgb(31, 73, 125); "><img border="0" width="800" height="470" src="cid:image002.png@01CAE207.CD713F80"></span>  <br>
<br><div class="gmail_quote">On Tue, May 4, 2010 at 8:02 PM, Nick Caton <span dir="ltr"><<a href="mailto:ncaton@smithboucher.com">ncaton@smithboucher.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">










<div lang="EN-US" link="blue" vlink="purple">

<div>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Piyush,</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Off the list here, please do not (on my account) hesitate to
copy any of our previous off-list discussion regarding alternating solar gain
factors – not everyone maintains an archive to look up your previous query
easily.  </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">I’m do not think I have understood exactly what you’re looking
for, but weren’t you essentially trying to extract an hourly output for solar
admittance to a space to check against a separate simulation’s?   As a humble
suggestion, framing your question to the list with some additional context
regarding your purpose might help others to guide you to what you’re looking for
;).</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Best wishes as always,</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">~Nick </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<div>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"><img width="119" height="37" src="cid:image001.jpg@01CAEB6C.B13B4F90" alt="cid:489575314@22072009-0ABB"></span><b><span style="font-size:11.0pt;color:#2D4D5E"></span></b></p>


<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E"> </span></b></p>

<p class="MsoNormal"><b><span style="font-size:11.0pt;color:#2D4D5E">NICK CATON, E.I.T.</span></b><b><span style="color:#2D4D5E"></span></b></p>

<p class="MsoNormal"><span style="font-size:7.5pt;color:#CC9900">PROJECT ENGINEER</span><span style="font-size:7.5pt;color:#CC9900"></span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">25501 west valley parkway</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">olathe ks 66061</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">direct 913 344.0036</span></p>

<p class="MsoNormal"><span style="font-size:10.0pt;color:#2D4D5E">fax 913 345.0617</span></p>

<p class="MsoNormal"><i><span style="font-size:10.0pt;color:#2D4D5E">Check out our new web-site @ </span></i><span style="font-size:11.0pt;color:#1F497D"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><span style="font-size:10.0pt">www.smithboucher.com</span></a></span><u><span style="font-size:10.0pt;color:blue"> </span></u><span style="font-size:11.0pt;color:#1F497D"></span></p>


</div>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<div>

<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">

<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Demba
Ndiaye<br>
<b>Sent:</b> Tuesday, May 04, 2010 9:02 AM<br>
<b>To:</b> Pasha Korber-Gonzalez; Piyush Varma</span></p><div><div></div><div class="h5"><br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Queries</div></div><p></p>

</div>

</div><div><div></div><div class="h5">

<p class="MsoNormal"> </p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">It make think of the sign convention used in Thermodynamics. You
have the System and its Surroundings. Let’s say that the System is the
building. </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">In Thermo, heat received by the system from its surroundings
(cooling load) is “positive”. The heat lost by the system to its surroundings
(heating load) is “negative”.</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">It is the inverse for work.</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">_____________</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D">Demba NDIAYE</span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;color:#1F497D"> </span></p>

<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">

<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Pasha
Korber-Gonzalez<br>
<b>Sent:</b> Tuesday, May 04, 2010 5:25 AM<br>
<b>To:</b> Piyush Varma<br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Queries</span></p>

</div>

<p class="MsoNormal"> </p>

<div>

<p class="MsoNormal">Piyush,</p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">I can help with 01., but I do not understand the concept of alternating
solar gain factor that you are referring too, or maybe I just don't understand
the question exactly.</p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">For 01. I have always known the symbols of heating energy to
be referenced as (+) for cooling and (-) for heating although I can't give you
the exact reference this nomenclature comes from.  In terms of the
positive for cooling energy it is a description for heat energy being present
in the conditioned space(s)/building in terms of heat energy being gained (or
generated.)  Where the negative symbol is used to represent heating energy
this is describing that heat energy from the space/zone is being
lost via....whatever the mechanism (i.e. ext. wall or window conduction
losses, to exhaust air heat energy loss from the building, to infiltration
effects, etc.)  </p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">As long as you can keep your symbols managed with in your
own simulation work don't let this little quirk stop you from reporting your
numbers in your preferred format.  It is good that you are asking
these types of detail questions so that you can ensure your own foundation of
understanding for the tools you use.  This is what makes a good energy
simulator.   Keep asking questions, this list is a HUGE benefit from
my experience.</p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal" style="margin-bottom:12.0pt">pasha</p>

</div>

<div>

<p class="MsoNormal">On Tue, May 4, 2010 at 2:55 AM, Piyush Varma <<a href="mailto:varpiyush@gmail.com" target="_blank">varpiyush@gmail.com</a>> wrote:</p>

<p class="MsoNormal">Hi all, </p>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">I am an eQuest newbie and had 2 small queries which
hopefully would be answered.</p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">01. What's the logic behind eQuest giving positive (+ve)
Cooling Loads & (-ve) negative Heating Loads. (I made an Admittance Method
Algorithm & it gives me the opposite values, eQuest i.e. negative cooling
loads & +ve heating loads, have checked all sign convention...can't figure
out why? My algorithm simulates for Delhi's (India) climate predominantly,
cooling loads.</p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">02. I have asked this before...is there any library for data
of alternating solar gain factors, especially for Delhi, India. (As far as i
believe it does'nt take into account the alternating solar gain
factor...) </p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">hope these get resolved soon, thanks in advance.</p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">Regards,</p>

</div>

<div>

<p class="MsoNormal">Piyush</p>

</div>

<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>

</div>

<p class="MsoNormal"> </p>

</div></div></div>

</div>


</blockquote></div><br></div>