I think I can point Susan in the right direction at least. First read this:<br><br><span style="font-size: 11pt; color: rgb(31, 73, 125);">For example, if 
the heating/cooling setpoints are 70/75, the
throttling range is 0.5F (throttling range is centered about the 
setpoint),
then the heating/cooling trigger temperatures for these reports are 
68.75F and
76.25F (half the throttling range plus 1F).</span><br>
<br>So you have 72 for heating and 74 for cooling. That means for heating your trigger temperature is 72 +/- 2F +/- 1F for 69F and 75F , for cooling you have 71F and 77F. So your heating/cooling trigger temperatures are crossing. That seems like it could cause a problem like you are experiencing.<br>
<br>WRT to the other temp, 70 F in the space, read the online help for setting this temp and follow it.<br><br>Cheers,<br>Carol<br><br><div class="gmail_quote">On Thu, Apr 22, 2010 at 10:19 AM, Howe, Timothy <span dir="ltr"><<a href="mailto:Timothy.Howe@stantec.com">Timothy.Howe@stantec.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">









<div link="blue" vlink="purple" lang="EN-US">

<div>

<p class="MsoNormal"><span style="font-size: 10pt; color: blue;">Just re-name the file “not-a-top-secret-nuclear-facility.pd2”. 
Should be all good.</span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: blue;"> </span></p>

<p class="MsoNormal"><span style="font-size: 10pt; color: blue;"> </span></p>

<div>

<div>

<p class="MsoNormal"><b><span style="font-size: 9pt; color: black;">Timothy Howe, MS, LEED® AP</span></b><span style="font-size: 9pt; color: black;"><br>
Mechanical Engineer<br>
Stantec</span></p>

</div>

<div>

<p class="MsoNormal"><span style="font-size: 9pt; color: gray;">2060 Brighton-Henrietta Town Line Road<br>
Rochester NY 14623-2792<br>
Ph:   (585) 413-5347<br>
Fx:   (585) 272-1814<br>
Cell: (585) 330-8681</span></p>

</div>

<div>

<p class="MsoNormal"><span style="font-size: 13pt; color: blue;"><a href="http://www.stantec.com" target="_blank"><b><span style="color: rgb(153, 51, 51); text-decoration: none;">stantec</span></b><span style="color: rgb(0, 63, 110); text-decoration: none;">.com</span></a> </span></p>


</div>

<div>

<p class="MsoNormal"><span style="font-size: 9pt; color: black;"> </span></p>

</div>

<div>

<p class="MsoNormal"><span style="font-size: 9pt; color: black;">The content of this email is the confidential property of Stantec
and should not be copied, modified, retransmitted, or used for any purpose
except with Stantec's written authorization. If you are not the intended
recipient, please delete all copies and notify us immediately.</span></p>

</div>

<div>

<p class="MsoNormal"><span style="font-size: 9pt; color: black;"> </span></p>

</div>

<p class="MsoNormal"><span style="font-size: 13.5pt; font-family: Webdings; color: rgb(0, 128, 64);">ü</span><span style="color: blue;"> </span><span style="font-size: 10pt; color: rgb(0, 128, 64);">Please
consider the environment before printing this email.</span><span style="color: blue;"> </span></p>

</div>

<p class="MsoNormal"><span style="font-size: 9pt; color: black;"> </span><span style="font-size: 10pt; color: blue;"></span></p>

<div>

<div style="border-width: 1pt medium medium; border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; padding: 3pt 0in 0in;">

<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Eric O'Neill<br>
<b>Sent:</b> Thursday, April 22, 2010 1:18 PM<br>
<b>To:</b> Susan F<div class="im"><br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Thermostat Setting</div></span></p>

</div>

</div><div class="im">

<p class="MsoNormal"> </p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">Can’t you just remove the sensitive project information
from the files? A text editor should allow you to find any “incriminating
evidence” and you can switch the weather file location so we won’t
even know where in the world it’s located :-) Unless you’re
modeling the pentagon, in which case I’ll quiet down.</span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);">And I doubt this is it, but you might want to double check your
header in the hourly report to make sure you’re not looking at just the
heating setpoint (see attached pg.2 and below). The space isn’t being
cooled at all, correct?</span></p>

<p class="MsoNormal"><img src="" width="502" border="0" height="283"><span style="font-size: 11pt; color: rgb(31, 73, 125);"></span></p>

<p class="MsoNormal"><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Susan F<br>
<b>Sent:</b> Thursday, April 22, 2010 11:47 AM<br>
<b>To:</b> Carol Gardner<br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Thermostat Setting</span></p>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

<p class="MsoNormal" style="margin-right: 0in; margin-bottom: 12pt; margin-left: 0.5in;">Unfortunately due to the sensitive nature of the
project I cannot send the files.  I have checked and my heating/cooling
schedules are assigned to the right locations.  <br>
<br>
Could it be related to the design temperatures I have indicated for each
zone?  The tstat schedules are as I have stated below but I have the
design temperatures at 74 cooling and 72 heating.  The load temperature
(in the space definition) is 70.  My throttling range is 2.  Would
any of this cause problems?</p>

<div>

<p class="MsoNormal" style="margin-left: 0.5in;">On Thu, Apr 22, 2010 at 11:50 AM,
Carol Gardner <<a href="mailto:cmg750@gmail.com" target="_blank">cmg750@gmail.com</a>>
wrote:</p>

<p class="MsoNormal" style="margin-right: 0in; margin-bottom: 12pt; margin-left: 0.5in;">Susan,<br>
<br>
While in detailed data edit go onto one of your thermal zone spreadsheets to
look at your schedules. You will be able to see them easily from there. Make
sure you haven't accidentally put your heating schedule in where your cooling
schedule should be. If this doesn't work zip up your .inp and .pd2 files and
send them to us.<br>
<br>
Good luck,<br>
<span style="color: rgb(136, 136, 136);">Carol</span></p>

<div>

<div>

<p class="MsoNormal" style="margin-left: 0.5in;">On Thu, Apr 22, 2010 at 6:11 AM,
Susan F <<a href="mailto:modelsenergy@gmail.com" target="_blank">modelsenergy@gmail.com</a>>
wrote:</p>

</div>

<blockquote style="border-width: medium medium medium 1pt; border-style: none none none solid; border-color: -moz-use-text-color -moz-use-text-color -moz-use-text-color rgb(204, 204, 204); padding: 0in 0in 0in 6pt; margin: 5pt 0in 5pt 4.8pt;">


<div>

<p class="MsoNormal" style="margin-right: 0in; margin-bottom: 12pt; margin-left: 0.5in;">I have a model that does not seem to be switching the
thermostat between heating and cooling.  When I output the hourly data for
the Zone Thermostat Setting it seems to always be the heating setpoints (70
occupied and 64 unoccupied).  Any idea why this wouldn't be changing over
to cooling setpoints (75 occupied and 82 unoccupied) during the warmer months?<br>
<br>
Thanks in advance.  </p>

</div>

<div>

<p class="MsoNormal" style="margin-right: 0in; margin-bottom: 12pt; margin-left: 0.5in;">_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>

</div>

</blockquote>

</div>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

</div>

<p class="MsoNormal" style="margin-left: 0.5in;"> </p>

</div></div>

</div>


<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><div style="visibility: hidden; display: inline;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup {  position:absolute;  z-index:9999;  padding: 0px 0px;  margin-left: 0px;  margin-top: 0px;  width: 240px;  overflow: hidden;  word-wrap: break-word;  color: black;  font-size: 10px;  text-align: left;  line-height: 13px;}</style>