color=#0000ff size=2>I run into this problem often when modeling mechanical
spaces as their own shell. It seems that some of the zoning patterns in
the wizard ("one per zone" especially) can not handle some of the custom shapes
you may make and will not let you select them in the zone group screen. My
solution has been just to select the zone pattern you want, then select
"custom", then on the pop up screen select "keep previous zoning pattern", and
then hit done when the drawing screen pops up. You can then go to the zone
groups screen and be able to select it. This has always worked for me so I
think it should solve your error.</FONT></SPAN></DIV>
<DIV> </DIV><!-- Converted from text/rtf format -->
<P><SPAN lang=en-us><FONT face=Arial></FONT></SPAN> <BR><SPAN
lang=en-us><B><FONT face=Arial color=#0000ff size=2>John Grando</FONT><FONT
face=Arial size=2> </FONT><FONT face=Arial color=#0000ff size=2>LEED
AP</FONT><FONT face=Arial size=2>| </FONT><FONT face=Arial color=#808080
size=2>Mechanical Engineer</FONT><BR></B></SPAN><BR><SPAN lang=en-us><FONT
face=Arial> </FONT></SPAN> </P>
<DIV> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> John Aulbach [mailto:jra_sac@yahoo.com]
<BR><B>Sent:</B> Tuesday, April 13, 2010 4:36 PM<BR><B>To:</B>
Gary.Schrader@buildings.schneider-electric.com<BR><B>Cc:</B>
equest-users@lists.onebuilding.org<BR><B>Subject:</B> Re: [Equest-users] error
message: "ShellWiz has no validZnGrpWizchildren." --- too many
shells?<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV
style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif">
<DIV>Let's try this..as I don't have much time today..</DIV>
<DIV> </DIV>
<DIV>Never try to name your files in the Wizard, as they will all be erased and
substitued with the THX1138 version of language (famous SF movie). And if you
try to change the .INP file while still in Wizard mode, they will also be
erased.</DIV>
<DIV> </DIV>
<DIV>When you get into the Detailed Edit mode, THEN you can make a space
"OFFICE-1" or CLASS-2, versus EL1 Ground Floor Core, as Gary intimated.</DIV>
<DIV> </DIV>
<DIV>Gary, I would need an example of what space you could not rename and
reassign. I have always been able to name and reassign spaces, zones, and HVAC
systems once in the Detailed Edit mode.</DIV>
<DIV> </DIV>
<DIV>I BELIEVE this naming nomenclature difficulty may be eliminated in the near
future...</DIV>
<DIV> </DIV>
<DIV><BR>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><A name=_MailAutoSig><SPAN
style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT
face=Calibri>John R. Aulbach, PE, CEM<o:p></o:p></FONT></SPAN></A></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="mso-bookmark: _MailAutoSig"><SPAN
style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT
face=Calibri>Senior Energy Engineer<o:p></o:p></FONT></SPAN></SPAN></P>
<DIV class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="mso-bookmark: _MailAutoSig"><SPAN
style="COLOR: #17365d; mso-fareast-font-family: 'Times New Roman'; mso-no-proof: yes"><FONT
face=Calibri>
<HR style="COLOR: #17365d" align=left width="30%" noShade SIZE=2>
</FONT></SPAN></SPAN></DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Calibri><SPAN
style="mso-bookmark: _MailAutoSig"><B><SPAN
style="COLOR: navy; FONT-VARIANT: small-caps; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Partner</SPAN></B></SPAN><SPAN
style="mso-bookmark: _MailAutoSig"><B><SPAN
style="COLOR: green; FONT-VARIANT: small-caps; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">
</SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN
style="COLOR: #006600; FONT-VARIANT: small-caps; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Energy</SPAN><SPAN
style="COLOR: navy; FONT-VARIANT: small-caps; mso-no-proof: yes"><o:p></o:p></SPAN></B></SPAN></FONT></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="mso-bookmark: _MailAutoSig"><SPAN
style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT
face=Calibri>1990 E. Grand Avenue, El Segundo, CA 90245<BR>W: 888-826-1216,
X254| D: 310-765-7295 | F: 310-817-2745<o:p></o:p></FONT></SPAN></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="mso-bookmark: _MailAutoSig"></SPAN><A
href="http://www.ptrenergy.com/"><FONT face=Calibri><SPAN
style="mso-bookmark: _MailAutoSig"><SPAN
style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">www.ptrenergy.com</SPAN></SPAN><SPAN
style="mso-bookmark: _MailAutoSig"></SPAN></FONT></A><SPAN
style="mso-bookmark: _MailAutoSig"><SPAN
style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><FONT
face=Calibri> </FONT></SPAN></SPAN><A
href="mailto:%7C%20jaulbach@ptrenergy.com"><FONT face=Calibri><SPAN
style="mso-bookmark: _MailAutoSig"><SPAN
style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">|
jaulbach@ptrenergy.com</SPAN></SPAN><SPAN
style="mso-bookmark: _MailAutoSig"></SPAN></FONT></A><SPAN
style="mso-bookmark: _MailAutoSig"><SPAN
style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><o:p></o:p></SPAN></SPAN></P><SPAN
style="mso-bookmark: _MailAutoSig"></SPAN>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><SPAN
style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><o:p><FONT
face=Calibri> </FONT></o:p></SPAN></P></DIV>
<DIV
style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif"><BR>
<DIV
style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif"><FONT
face=Tahoma size=2>
<HR SIZE=1>
<B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B>
"Gary.Schrader@buildings.schneider-electric.com"
<Gary.Schrader@buildings.schneider-electric.com><BR><B><SPAN
style="FONT-WEIGHT: bold">Cc:</SPAN></B>
equest-users@lists.onebuilding.org<BR><B><SPAN
style="FONT-WEIGHT: bold">Sent:</SPAN></B> Tue, April 13, 2010 1:14:10
PM<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> Re: [Equest-users]
error message: "ShellWiz has no validZnGrpWizchildren." --- too many
shells?<BR></FONT><BR>
<STYLE>UNKNOWN {
FONT-FAMILY: Cambria Math
}
UNKNOWN {
FONT-FAMILY: Calibri
}
UNKNOWN {
FONT-FAMILY: Tahoma
}
UNKNOWN {
FONT-FAMILY: Consolas
}
UNKNOWN {
MARGIN: 1in
}
P.MsoNormal {
FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "serif"
}
LI.MsoNormal {
FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "serif"
}
DIV.MsoNormal {
FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "serif"
}
A:link {
COLOR: blue; TEXT-DECORATION: underline
}
SPAN.MsoHyperlink {
COLOR: blue; TEXT-DECORATION: underline
}
A:visited {
COLOR: purple; TEXT-DECORATION: underline
}
SPAN.MsoHyperlinkFollowed {
COLOR: purple; TEXT-DECORATION: underline
}
PRE {
FONT-SIZE: 10pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Courier New"
}
SPAN.HTMLPreformattedChar {
FONT-FAMILY: Consolas
}
SPAN.EmailStyle19 {
COLOR: #1f497d; FONT-FAMILY: "sans-serif"
}
.MsoChpDefault {
}
DIV.Section1 {
}
</STYLE>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN
class=558085119-13042010>I have received this error on several occasions by
screwing up the Zone Group Definitions Screen in the DD Wizard. (Screen
14)</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN
class=558085119-13042010></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN
class=558085119-13042010>I have never liked eQuest's naming nomenclature, so I
have always renamed zone groups myself so that I can better keep track of what
is what. (e.g.. "Gym" as opposed to "EL1 Ground Floor Core")</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN
class=558085119-13042010></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN
class=558085119-13042010>If you delete all of the zone groups and then recreate
them with your own name, sometimes I experience being unable to assign the new
groups to spaces. When I click the mouse on a space, a context menu does NOT
appear as it normally does. In this case, I am "stuck" and cannot assign a zone
group to a space.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT> </DIV>
<DIV><SPAN class=558085119-13042010><FONT face=Arial color=#0000ff size=2>My
experience has been that this error occurs much more commonly if you have
only one or two zone groups to assign to spaces.</FONT></SPAN></DIV>
<DIV><SPAN class=558085119-13042010><FONT face=Arial color=#0000ff
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=558085119-13042010><FONT face=Arial color=#0000ff
size=2>Previous uses have already chimed in as to the solution... a manual edit
of the .pd2 file. Just thought I would give some background as to what I have
done in the past to cause the error.</FONT></SPAN></DIV>
<DIV><SPAN class=558085119-13042010><FONT face=Arial color=#0000ff
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=558085119-13042010><FONT face=Arial color=#0000ff
size=2>Thanks,</FONT></SPAN></DIV>
<DIV><SPAN class=558085119-13042010><FONT face=Arial color=#0000ff
size=2>Gary</FONT></SPAN></DIV><SPAN style="FONT: 8.5pt Arial"><BR><FONT
color=green>_______________________________________________________________________________________________________________________</FONT><BR><BR>
<P style="FONT: 8.5pt Arial" align=left><B>Gary Schrader</B> | <B><FONT
color=green>Schneider Electric </FONT></B>| <B>Buildings Business</B> |
<B>Energy Solutions </B>| <B>Engineer I</B><BR><B>Phone:</B> +1 | <B>Mobile:
</B>+1 913 217 8068 | <B>Fax: </B>+1 913 469 0206<BR><B>Email: </B><A
href="mailto:gary.schrader@buildings.schneider-electric.com" target=_blank
rel=nofollow
ymailto="mailto:gary.schrader@buildings.schneider-electric.com">gary.schrader@buildings.schneider-electric.com</A>
| <B>Site: </B><A href="http://www.schneider-electric.com/buildings"
target=_blank rel=nofollow>www.schneider-electric.com/buildings</A> |
<B>Address: </B>16011 College Boulevard, Suite 212, Lenexa, KS 66219,
USA<BR><BR><FONT color=green>*** Please consider the environment before printing
this email.</P></FONT></SPAN>
<DIV> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> equest-users-bounces@lists.onebuilding.org
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>James
Hansen<BR><B>Sent:</B> Tuesday, April 13, 2010 2:44 PM<BR><B>To:</B> Carol
Gardner; Richard Williams<BR><B>Cc:</B>
equest-users@lists.onebuilding.org<BR><B>Subject:</B> Re: [Equest-users] error
message: "ShellWiz has no validZnGrpWizchildren." --- too many
shells?<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV class=Section1>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'">Open up your
PD2 file and take a look around – the ZnGrpWiz command usually follows the
Dayshapes/Shapewiz commands for each shell, and directly precedes definition of
the custom zones for the shell.</SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'">Look thru
each shell, and see if some have them and some don’t…I don’t know why eQuest
wouldn’t automatically define this, but I’ve successfully messed around with the
PD2 file before without damaging anything. Make you can copy one of the
ZnGrpWiz commands from one shell to another and make sure to rename
accordingly.</SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'">Shellwiz is a
lot more important: that’s the “beginning” of the definition for each
shell. Open up the PD2 file and see if there are ANY shellwiz definitions,
and report back…</SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><B><SPAN
style="FONT-SIZE: 11pt; COLOR: teal; FONT-FAMILY: 'sans-serif'">GHT
Limited<BR></SPAN></B><B><SPAN
style="FONT-SIZE: 11pt; FONT-FAMILY: 'sans-serif'"><SPAN
style="COLOR: black">James Hansen</SPAN></SPAN></B><B><SPAN
style="FONT-SIZE: 11pt; COLOR: black; FONT-FAMILY: 'sans-serif'">, PE, LEED
AP</SPAN></B></P>
<P class=MsoNormal><B><SPAN
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'sans-serif'">Senior
Associate</SPAN></B><B><SPAN
style="FONT-SIZE: 11pt; COLOR: black; FONT-FAMILY: 'sans-serif'"></SPAN></B></P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'sans-serif'"><SPAN
style="COLOR: black">1010 N. Glebe Rd, Suite 200</SPAN><SPAN
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"></SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'sans-serif'"><SPAN
style="COLOR: black">Arlington</SPAN><SPAN style="COLOR: black">, </SPAN><SPAN
style="COLOR: black">VA</SPAN><SPAN style="COLOR: black"> </SPAN><SPAN
style="COLOR: black">22201-4749</SPAN></SPAN></SPAN><SPAN
style="FONT-SIZE: 11pt; COLOR: black; FONT-FAMILY: 'sans-serif'"></SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 7.5pt; COLOR: black; FONT-FAMILY: 'sans-serif'">703-338-5754
(Cell)</SPAN><SPAN
style="FONT-SIZE: 11pt; COLOR: black; FONT-FAMILY: 'sans-serif'"></SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 7.5pt; COLOR: black; FONT-FAMILY: 'sans-serif'">703-243-1200
(Office)</SPAN><SPAN
style="FONT-SIZE: 11pt; COLOR: black; FONT-FAMILY: 'sans-serif'"></SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 7.5pt; COLOR: black; FONT-FAMILY: 'sans-serif'">703-276-1376
(Fax)</SPAN><SPAN
style="FONT-SIZE: 11pt; COLOR: black; FONT-FAMILY: 'sans-serif'"></SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 11pt; COLOR: teal; FONT-FAMILY: 'sans-serif'"><A
href="http://www.ghtltd.com/" target=_blank rel=nofollow><SPAN
style="FONT-SIZE: 10pt">www.ghtltd.com</SPAN></A></SPAN></P>
<P class=MsoNormal><B><SPAN
style="FONT-SIZE: 11pt; COLOR: #31849b; FONT-FAMILY: 'sans-serif'"></SPAN></B> </P>
<P class=MsoNormal><SPAN
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'sans-serif'"></SPAN> </P>
<DIV
style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; PADDING-LEFT: 0in; PADDING-BOTTOM: 0in; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
<P class=MsoNormal><B><SPAN
style="FONT-SIZE: 10pt; FONT-FAMILY: 'sans-serif'">From:</SPAN></B><SPAN
style="FONT-SIZE: 10pt; FONT-FAMILY: 'sans-serif'">
equest-users-bounces@lists.onebuilding.org
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Carol
Gardner<BR><B>Sent:</B> Tuesday, April 13, 2010 3:29 PM<BR><B>To:</B> Richard
Williams<BR><B>Cc:</B> equest-users@lists.onebuilding.org<BR><B>Subject:</B> Re:
[Equest-users] error message: "ShellWiz has no valid ZnGrpWizchildren." --- too
many shells?</SPAN></P></DIV>
<P class=MsoNormal> </P>
<P class=MsoNormal style="MARGIN-BOTTOM: 12pt">This sounds like an eQUEST
developer question. Hopefully one of them will be willing/able to take the time
to answer it.<BR><BR>Carol</P>
<DIV>
<P class=MsoNormal>On Tue, Apr 13, 2010 at 12:09 PM, Richard Williams <<A
href="mailto:Richard.Williams@arup.com" target=_blank rel=nofollow
ymailto="mailto:Richard.Williams@arup.com">Richard.Williams@arup.com</A>>
wrote:</P>
<DIV>
<DIV>
<P class=MsoNormal> </P>
<P class=MsoNormal>Dear all</P>
<P class=MsoNormal> </P>
<P class=MsoNormal>I have been building a model with a large number of shells. I
understand that this is not ideal but I have many overhangs and setbacks.</P>
<P class=MsoNormal> </P>
<P class=MsoNormal>Once I reach about 60-70 shells a get the following error
messages:</P>
<P class=MsoNormal> </P>
<P class=MsoNormal>“ShellWiz has no valid ZnGrpWiz children.”</P>
<P class=MsoNormal> </P>
<P class=MsoNormal>“Error: No ShellWiz components exist.”</P>
<P class=MsoNormal> </P>
<P class=MsoNormal>“Error creating BDL input file from wizard inputs!”</P>
<P class=MsoNormal> </P>
<P class=MsoNormal> </P>
<P class=MsoNormal>After these messages the model becomes unusable. Is this
likely to be a shell problem or perhaps something to do with the limitations of
running in wizard mode?</P>
<P class=MsoNormal> </P>
<P class=MsoNormal>Any suggestions much appreciated.</P>
<P class=MsoNormal> </P>
<P class=MsoNormal>Regards</P>
<P class=MsoNormal> </P>
<P class=MsoNormal>Richard</P></DIV><PRE>____________________________________________________________</PRE><PRE>Electronic mail messages entering and leaving Arup business</PRE><PRE>systems are scanned for acceptability of content and viruses</PRE></DIV>
<P class=MsoNormal
style="MARGIN-BOTTOM: 12pt"><BR>_______________________________________________<BR>Equest-users
mailing
list<BR>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<BR>To
unsubscribe from this mailing list send a blank message to <A
href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target=_blank
rel=nofollow
ymailto="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</A></P></DIV>
<P class=MsoNormal> </P></DIV>
<P align=left><FONT size=2><FONT face=Tahoma><FONT color=#0000ff>
<HR>
</FONT></FONT><FONT color=#0000ff><FONT color=#000000><FONT face=Arial>The
information contained in this communication is confidential, may be privileged,
and is intended only for the use of the addressee. It is the property of
GHT Limited. Unauthorized use, disclosure or copying of this communication
or any part thereof is strictly prohibited and may be unlawful. If you
have received this communication in error, please notify me immediately by
return e-mail or by e-mail to </FONT><A href="mailto:ght@ghtltd.com"
target=_blank rel=nofollow ymailto="mailto:ght@ghtltd.com"><FONT
face=Arial>ght@ghtltd.com</FONT></A><FONT face=Arial>, and destroy this
communication and all copies thereof, including all attachments. Thank
you.</FONT></FONT><FONT face=Tahoma color=#000000></FONT>
<P></P></FONT></FONT><BR>______________________________________________________________________<BR>This
email has been scanned by the MessageLabs Email Security System.<BR>For more
information please visit http://www.messagelabs.com/email
<BR>______________________________________________________________________<BR></DIV></DIV></DIV><BR><br clear=all> NOTICE OF CONFIDENTIALITY
This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof. In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law. If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission. Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege. If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.
</BODY></HTML>