This is not a bug - just a matter of understanding the results being
presented.<br>
In the eQUEST results module Demand report, what you are looking at is
the breakdown of enduse energy use for the hour of highest overall <u>coincident</u>
electric (and gas) demand for each month. For any given month, the
highest coincident demand may or may not occur at a time when the
lighting load is at its peak. Hence the variation in monthly lighting
demand results.<br>
If this report indicated the peak non-coincident load for each enduse,
then you would see consistent lighting demand results, but their sum
would not (necessarily) add up to the building peak, since not all
enduses are likely to all peak at the same time from month to month.<br>
If you review the PS-E report in the detailed simulation results you
will see both the peak coincident and non-coincident demand results
listed for each month.<br>
<br>
- Scott<br>
<br>
<br>
Heinrich.ib-bauklima.de wrote:
<blockquote cite="mid:0Lxu9U-1NOwDB2MmC-015uzw@mrelayeu.kundenserver.de"
type="cite">
<meta http-equiv="Content-Type" content="text/html; ">
<meta content="MSHTML 6.00.6000.16890" name="GENERATOR">
<!--[if !mso]>
<STYLE>v\:* {
        BEHAVIOR: url(#default#VML)
}
o\:* {
        BEHAVIOR: url(#default#VML)
}
w\:* {
        BEHAVIOR: url(#default#VML)
}
.shape {
        BEHAVIOR: url(#default#VML)
}
</STYLE>
<![endif]-->
<style>@font-face {
        font-family: MS Mincho;
}
@font-face {
        font-family: Cambria Math;
}
@font-face {
        font-family: Calibri;
}
@font-face {
        font-family: Tahoma;
}
@font-face {
        font-family: Stylus BT;
}
@font-face {
        font-family: @MS Mincho;
}
@font-face {
        font-family: t;
}
@font-face {
        font-family: Verdana;
}
@page Section1 {size: 8.5in 11.0in; margin: 1.0in 1.0in 1.0in 1.0in; }
P.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman","serif"
}
LI.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman","serif"
}
DIV.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman","serif"
}
A:link {
        COLOR: blue; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.MsoHyperlink {
        COLOR: blue; TEXT-DECORATION: underline; mso-style-priority: 99
}
A:visited {
        COLOR: purple; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.MsoHyperlinkFollowed {
        COLOR: purple; TEXT-DECORATION: underline; mso-style-priority: 99
}
P {
        FONT-SIZE: 12pt; MARGIN-LEFT: 0in; MARGIN-RIGHT: 0in; FONT-FAMILY: "Times New Roman","serif"; mso-style-priority: 99; mso-margin-top-alt: auto; mso-margin-bottom-alt: auto
}
P.MsoAcetate {
        FONT-SIZE: 8pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Tahoma","sans-serif"; mso-style-priority: 99; mso-style-link: "Balloon Text Char"
}
LI.MsoAcetate {
        FONT-SIZE: 8pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Tahoma","sans-serif"; mso-style-priority: 99; mso-style-link: "Balloon Text Char"
}
DIV.MsoAcetate {
        FONT-SIZE: 8pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Tahoma","sans-serif"; mso-style-priority: 99; mso-style-link: "Balloon Text Char"
}
SPAN.spelle {
        mso-style-name: spelle
}
SPAN.EmailStyle21 {
        COLOR: #1f497d; FONT-FAMILY: "Calibri","sans-serif"; mso-style-type: personal-reply
}
SPAN.BalloonTextChar {
        FONT-FAMILY: "Tahoma","sans-serif"; mso-style-priority: 99; mso-style-link: "Balloon Text"; mso-style-name: "Balloon Text Char"
}
.MsoChpDefault {
        FONT-SIZE: 10pt; mso-style-type: export-only
}
DIV.Section1 {
        page: Section1
}
</style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="2050" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div dir="ltr" align="left">
<div dir="ltr" align="left"><span class="750532717-12042010"><font
face="Arial" size="2">Nick,</font></span></div>
<div dir="ltr" align="left"><span class="750532717-12042010"><span
class="203384519-12042010"><font face="Arial" size="2">and to all
eQUESTERs who are still wondering about my model-output.</font></span></span></div>
<div dir="ltr" align="left"><span class="750532717-12042010"></span> </div>
<div dir="ltr" align="left"><span class="750532717-12042010"><span
class="203384519-12042010"><font face="Arial" size="2">It seems to be
a bug in the generated demand-output of the eQUEST-run.</font></span></span></div>
<div dir="ltr" align="left"><span class="750532717-12042010"><span
class="203384519-12042010"><font face="Arial" size="2">When I write
out the hourly reports of the lighting loads there is no monthly
fluctuation in the peak lighting loads.</font></span></span></div>
<div dir="ltr" align="left"><span class="750532717-12042010"><span
class="203384519-12042010"><font face="Arial" size="2">Please correct
me if I'm wrong.</font></span></span></div>
<div dir="ltr" align="left"><span class="750532717-12042010"><span
class="203384519-12042010"></span></span> </div>
<div dir="ltr" align="left"><span class="750532717-12042010"></span><span
class="750532717-12042010"><span class="218293217-12042010"><font
face="Arial" size="2"><span class="203384519-12042010"></span></font></span></span> </div>
<div dir="ltr" align="left"><span class="750532717-12042010"><span
class="218293217-12042010"><font face="Arial" size="2">Heinrich</font></span></span></div>
<div dir="ltr" align="left"><span class="750532717-12042010"><span
class="218293217-12042010"></span></span> </div>
<div> </div>
<div class="Section1">
<p align="left"><em><span style="font-size: 10pt; font-family: t;">--------------------------------------------------</span></em><i><span
style="font-size: 10pt; font-family: Arial;"><o:p></o:p></span></i></p>
<p style="margin-bottom: 12pt;"><strong><i><span
style="font-size: 16pt; color: blue; font-family: Tahoma;">b</span></i></strong><strong><i><span
style="font-size: 8pt; color: blue; font-family: Verdana;"> </span></i></strong><em><b><span
style="font-size: 10pt; font-family: Verdana;">+</span></b></em><strong><i><span
style="font-size: 16pt; color: red; font-family: Tahoma;">e</span></i></strong><span
style="font-size: 10pt; font-family: Verdana;"><br>
Ingenieurbüro<br>
für Bauklima und <br>
Energiekonzeption<br>
Dr. Heinrich Post</span></p>
<p style=""><span class="SpellE"><span
style="font-size: 10pt; font-family: Verdana;">Brienner</span></span><span
style="font-size: 10pt; font-family: Verdana;"> Str. 48<br>
D-80333 München<br>
<br>
Fon <span style=""> </span>+49 (0) 89/54320678<br>
Fax <span style=""> </span>+49 (0) 89/54320679</span><span
style="font-family: Verdana;"> </span><span
style="font-size: 10pt; font-family: Verdana;"><br>
Mobil<span style=""> </span>+49 (0) 160/7225740</span><span
style="font-size: 10pt; font-family: Arial;"><br>
</span><span style="font-size: 10pt; font-family: Verdana;"><a
moz-do-not-send="true" title="mailto:dr.post@ib-bauklima.de"
href="blocked::mailto:dr.post@ib-bauklima.de"><span
style="color: black;"><span title="mailto:dr.post@ib-bauklima.de">mailto:dr.post@ib-bauklima.de</span></span></a><o:p></o:p></span></p>
<p><span style="font-size: 10pt; font-family: Verdana;">Besuchen Sie
uns im Internet:<o:p></o:p></span></p>
<p><span style="font-size: 10pt; font-family: Verdana;"><a
moz-do-not-send="true" href="blocked::http://www.ib-bauklima.de/">www.ib-bauklima.de</a><o:p></o:p></span></p>
<p><em><span style="font-size: 10pt; font-family: t;">--------------------------------------------------</span></em><span
style="font-size: 10pt; font-family: Arial;"><o:p></o:p></span></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<div> </div>
</div>
<div> </div>
<div class="Section1">
<p align="left"><em><span style="font-size: 10pt; font-family: t;">--------------------------------------------------</span></em><i><span
style="font-size: 10pt; font-family: Arial;"><o:p></o:p></span></i></p>
<p style="margin-bottom: 12pt;"><strong><i><span
style="font-size: 16pt; color: blue; font-family: Tahoma;">b</span></i></strong><strong><i><span
style="font-size: 8pt; color: blue; font-family: Verdana;"> </span></i></strong><em><b><span
style="font-size: 10pt; font-family: Verdana;">+</span></b></em><strong><i><span
style="font-size: 16pt; color: red; font-family: Tahoma;">e</span></i></strong><span
style="font-size: 10pt; font-family: Verdana;"><br>
Ingenieurbüro<br>
für Bauklima und <br>
Energiekonzeption<br>
Dr. Heinrich Post</span></p>
<p style=""><span class="SpellE"><span
style="font-size: 10pt; font-family: Verdana;">Brienner</span></span><span
style="font-size: 10pt; font-family: Verdana;"> Str. 48<br>
D-80333 München<br>
<br>
Fon <span style=""> </span>+49 (0) 89/54320678<br>
Fax <span style=""> </span>+49 (0) 89/54320679</span><span
style="font-family: Verdana;"> </span><span
style="font-size: 10pt; font-family: Verdana;"><br>
Mobil<span style=""> </span>+49 (0) 160/7225740</span><span
style="font-size: 10pt; font-family: Arial;"><br>
</span><span style="font-size: 10pt; font-family: Verdana;"><a
moz-do-not-send="true" title="mailto:dr.post@ib-bauklima.de"
href="mailto:dr.post@ib-bauklima.de"><span style="color: black;"><span
title="mailto:dr.post@ib-bauklima.de">mailto:dr.post@ib-bauklima.de</span></span></a><o:p></o:p></span></p>
<p><span style="font-size: 10pt; font-family: Verdana;">Besuchen Sie
uns im Internet:<o:p></o:p></span></p>
<p><span style="font-size: 10pt; font-family: Verdana;"><a
moz-do-not-send="true" href="http://www.ib-bauklima.de/">www.ib-bauklima.de</a><o:p></o:p></span></p>
<p><em><span style="font-size: 10pt; font-family: t;">--------------------------------------------------</span></em><span
style="font-size: 10pt; font-family: Arial;"><o:p></o:p></span></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<div> </div>
<br>
<blockquote dir="ltr"
style="border-left: 2px solid rgb(0, 0, 255); padding-left: 5px; margin-left: 5px; margin-right: 0px;">
<div class="OutlookMessageHeader" dir="ltr" align="left" lang="de">
<hr tabindex="-1"> <font face="Tahoma" size="2"><b>Von:</b> Nick
Caton [<a class="moz-txt-link-freetext" href="mailto:ncaton@smithboucher.com">mailto:ncaton@smithboucher.com</a>] <br>
<b>Gesendet:</b> Montag, 12. April 2010 17:46<br>
<b>An:</b> <a class="moz-txt-link-abbreviated" href="mailto:heinrich@ib-bauklima.de">heinrich@ib-bauklima.de</a>;
<a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Betreff:</b> Re: [Equest-users]
lighting-schedule&lighting-demand<br>
</font><br>
</div>
<div class="Section1">
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';">Heinrich,
<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';">I’ve
found something that may help or be a red herring… <o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';">I
tried running the simulation so I could view a few things in the
spreadsheet views, but I didn’t have the Dusseldorf weather file
on-hand, so without changing anything else I substituted a local
weather file I had on my computer for Kansas City, Missouri.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';">The
results (see attached consumption/demand reports ) interestingly show
the area lighting fluctuating a good deal more than the demand report
you provided, suggesting whatever is off may be weather-dependant.<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';">I
do not see any daylighting specified for the interior lighting, which
was my initial guess, so there I am at a loss! I’m not sure how else
the modeled interior lighting loads may be affected by the weather
file/site properties used (i.e. latitude/longitude)… Does “Area
Lighting” cover more than interior lighting loads? Perhaps someone
more experienced can comment…? <o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';">I’ll
be interested to hear your findings,<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';">~Nick<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';">PS:
I’m unsure of whether a space being unoccupied might override any
hourly values entered in a lighting schedule... I had a hunch this
might be the case since you appeared to have a clean block of months
with uniformly lowered demand. Even so, I think I’ve verified it
cannot be a holiday scheduling issue by changing your custom holiday
schedule to “No holidays,” and still observing fluctuating area
lighting loads. <o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><o:p> </o:p></span></p>
<div>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><img
id="Picture_x0020_1" alt="cid:489575314@22072009-0ABB"
src="cid:part1.03030205.04030802@gmail.com" height="37" width="119"></span><b><span
style="font-size: 11pt; color: rgb(45, 77, 94); font-family: 'Stylus BT','sans-serif';"><o:p></o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size: 11pt; color: rgb(45, 77, 94); font-family: 'Stylus BT','sans-serif';"><o:p> </o:p></span></b></p>
<p class="MsoNormal"><b><span
style="font-size: 11pt; color: rgb(45, 77, 94); font-family: 'Stylus BT','sans-serif';">NICK
CATON, E.I.T.</span></b><b><span
style="color: rgb(45, 77, 94); font-family: 'Stylus BT','sans-serif';"><o:p></o:p></span></b></p>
<p class="MsoNormal"><span
style="font-size: 7.5pt; color: rgb(204, 153, 0); font-family: 'Calibri','sans-serif';">PROJECT
ENGINEER</span><span style="font-size: 7.5pt; color: rgb(204, 153, 0);"><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 10pt; color: rgb(45, 77, 94); font-family: 'Calibri','sans-serif';">25501
west valley parkway<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 10pt; color: rgb(45, 77, 94); font-family: 'Calibri','sans-serif';">olathe
ks 66061<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 10pt; color: rgb(45, 77, 94); font-family: 'Calibri','sans-serif';">direct
913 344.0036<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size: 10pt; color: rgb(45, 77, 94); font-family: 'Calibri','sans-serif';">fax
913 345.0617<o:p></o:p></span></p>
<p class="MsoNormal"><i><span
style="font-size: 10pt; color: rgb(45, 77, 94); font-family: 'Calibri','sans-serif';">Check
out our new web-site @ </span></i><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><a
moz-do-not-send="true" title="blocked::www.smithboucher.com"
href="www.smithboucher.com"><span style="font-size: 10pt;">www.smithboucher.com</span></a></span><u><span
style="font-size: 10pt; color: blue; font-family: 'Calibri','sans-serif';">
</span></u><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><o:p></o:p></span></p>
</div>
<p class="MsoNormal"><span
style="font-size: 11pt; color: rgb(31, 73, 125); font-family: 'Calibri','sans-serif';"><o:p> </o:p></span></p>
<div>
<div
style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><span
style="font-size: 10pt; font-family: 'Tahoma','sans-serif';">From:</span></b><span
style="font-size: 10pt; font-family: 'Tahoma','sans-serif';">
<a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b><a class="moz-txt-link-abbreviated" href="mailto:heinrich@ib-bauklima.de">heinrich@ib-bauklima.de</a><br>
<b>Sent:</b> Monday, April 12, 2010 7:34 AM<br>
<b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] lighting-schedule&lighting-demand<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">Dear eQUEST-Users,</span><o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">this is a
great community for troubleshooting in eQUEST.</span><o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">So
hopefully you can help me solving my problem with an eQUEST-model.</span><o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">I have
some serious trouble to model the lighting schedules of my baseline
building.</span><o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">I defined
the schedules as told from the client.</span><o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">When
I select some of the lighting
schedules (EXHIBIT,ARCHIVE,CONFER,KITCHEN,GARAGE) I get changes in
lighting demand over the year (Demand_Baseline_28f.pdf). </span><o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">But this
is not correct. They should not change, because each of the lighting
schedules are modeled the same each week and do not change over the
year.</span><o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">When I
deselect these schedules I get constant lighting demands over the year
(BASELINE_28e.pdf).</span><o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">I can't
find any mistake in the lighting schedules.</span><o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">Anybody
know how to solve this?</span><o:p></o:p></p>
</div>
<div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">Please
feel free to check my eQUEST-model.<o:p></o:p></span></p>
</div>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">Thanks,</span><o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<p class="MsoNormal"><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';">Heinrich</span><o:p></o:p></p>
</div>
</div>
<div>
<p class="MsoNormal"> <o:p></o:p></p>
</div>
<div>
<div>
<p><em><span style="font-size: 10pt; font-family: 't','serif';">--------------------------------------------------</span></em><i><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';"><o:p></o:p></span></i></p>
<p style="margin-bottom: 12pt;"><strong><i><span
style="font-size: 16pt; color: blue; font-family: 'Tahoma','sans-serif';">b</span></i></strong><strong><i><span
style="font-size: 8pt; color: blue; font-family: 'Verdana','sans-serif';">
</span></i></strong><em><b><span
style="font-size: 10pt; font-family: 'Verdana','sans-serif';">+</span></b></em><strong><i><span
style="font-size: 16pt; color: red; font-family: 'Tahoma','sans-serif';">e</span></i></strong><span
style="font-size: 10pt; font-family: 'Verdana','sans-serif';"><br>
Ingenieurbüro<br>
für Bauklima und <br>
Energiekonzeption<br>
Dr. Heinrich Post</span><o:p></o:p></p>
<p><span class="spelle"><span
style="font-size: 10pt; font-family: 'Verdana','sans-serif';">Brienner</span></span><span
style="font-size: 10pt; font-family: 'Verdana','sans-serif';"> Str. 48<br>
D-80333 München<br>
<br>
Fon +49 (0) 89/54320678<br>
Fax +49 (0) 89/54320679</span><span
style="font-family: 'Verdana','sans-serif';"> </span><span
style="font-size: 10pt; font-family: 'Verdana','sans-serif';"><br>
Mobil +49 (0) 160/7225740</span><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';"><br>
</span><span
style="font-size: 10pt; font-family: 'Verdana','sans-serif';"><a
moz-do-not-send="true" title="mailto:dr.post@ib-bauklima.de"
href="mailto:dr.post@ib-bauklima.de"><span style="color: black;">mailto:dr.post@ib-bauklima.de</span></a><o:p></o:p></span></p>
<p><span
style="font-size: 10pt; font-family: 'Verdana','sans-serif';">Besuchen
Sie uns im Internet:<o:p></o:p></span></p>
<p><span
style="font-size: 10pt; font-family: 'Verdana','sans-serif';"><a
moz-do-not-send="true" href="http://www.ib-bauklima.de/">www.ib-bauklima.de</a><o:p></o:p></span></p>
<p><em><span style="font-size: 10pt; font-family: 't','serif';">--------------------------------------------------</span></em><span
style="font-size: 10pt; font-family: 'Arial','sans-serif';"><o:p></o:p></span></p>
<p class="MsoNormal" style=""><o:p> </o:p></p>
</div>
</div>
</div>
</blockquote>
<pre wrap="">
<hr size="4" width="90%">
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>