<span class="Apple-style-span" style="border-collapse: separate; color: rgb(0, 0, 0); font-family: 'Times New Roman'; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; font-size: medium;"><span class="Apple-style-span" style="font-family: arial; font-size: small;">Hi All,<div>
<br></div><div>I am modeling a VAV system using water cooled DX air handlers on four of five floors.  24/7 load spaces use CHW fan coil units and the entire fourth floor uses chilled water VAV air handler.  Each DX VAV has an economizer coil so hours in the winter when the CW temp is low enough the internal zone receives free cooling.  The entire chilled water loop also has a water-side economizer so all the chilled water equipment can recieve free cooling.</div>
<div><br></div><div>As seen by the elec consumption graphs I'm having a problem with the CW loop control strategy.  Either the loop operates at the commanded setpoint of 85 deg.  Which means there is no free cooling.  Or when I try to use OA-Reset the cooling loads during the winter are met via free-cooling but during the summer the chiller barely runs and the cooling tower tries to meet the load of the CHW loop.<br>
<br>I was able to find the way to disable the error caused by condenser water below 65 deg thanks to post from board veterans like Mike TIllou, Steve Gates, John Albach, and others).  I do not know what else to try.<br><br>
Thanks,<br>MH<br></div></span></span>