Jacob,<br><br>I wouldn't even try to get this detailed in the Wizards, I would wait until you are in DD edit where you can see all the variables you need to evaluate. When you are inputting data for your proposed building, be sure you have set your altitude to zero under the Site Tab under Project and Properties or it will adjust everything using an altitude factor. You will see it on your SV-A report.<br>
<br>Good Luck.<br>Carol<br><br><div class="gmail_quote">On Mon, Apr 5, 2010 at 8:32 AM, Jacob Goodman <span dir="ltr"><<a href="mailto:jacobg@lseng.com">jacobg@lseng.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div bgcolor="#ffffff" text="#000000">
Dear all,<br>
<br>
I am attempting to set the fan supply volume for my model to match the
design fan supply volume. To set the supply volume, I input the value
(4,400 cfm) in wizard screen 4 of 7 in the air side system wizard by
using specify instead of auto-size. The input for OA % is set to the
design min OA cfm divided by the designed system supply volume. <br>
<br>
When I checked the "Supply Flow (CFM)" in the SV-A report, by adding
the supply flows for all the zones assigned to this system, the number
I got was somewhat higher than the input...should they be equal? Any
thoughts on setting supply volume and demonstrating that it was what
the model used?<br>
<br>
<br>
<div><br>
<span style="font-size: 11pt; font-family: Arial; color: black; font-weight: bold;">
Jacob Goodman
</span><span style="font-size: 8pt; font-family: Arial; color: rgb(102, 102, 102); font-weight: normal;">,
LEED AP</span></div>
<br>
<br>
</div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><div style="visibility: hidden; display: inline;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup { position:absolute; z-index:9999; padding: 0px 0px; margin-left: 0px; margin-top: 0px; width: 240px; overflow: hidden; word-wrap: break-word; color: black; font-size: 10px; text-align: left; line-height: 13px;}</style>