<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META http-equiv=Content-Type content="text/html; charset=us-ascii">
<META content="MSHTML 6.00.6000.17023" name=GENERATOR></HEAD>
<BODY>
<DIV dir=ltr align=left><FONT face="Trebuchet MS" color=#0000ff size=2><SPAN 
class=618572020-01042010>Brett, attached are some example kw/ton curves for 
existing chillers on a recent project.&nbsp; Chiller #1 is a 250 ton unit, and 
chillers 2 thru 4 are 550 ton units.&nbsp; Chillers 1 and 2 are ~ 15 years old, 
and chillers 3 and 4 are newer with better efficiencies.&nbsp; All 4 chillers 
are water cooled.&nbsp; The curves show efficiencies with and without Adjustable 
Frequency Drives.&nbsp; It's hard to tell the difference between the "w/AFD" and 
"w/o AFD" curves, but the "w/AFD" curves have a lower kw/ton except at full 
load.</SPAN></FONT></DIV>
<DIV>&nbsp;</DIV>
<DIV align=left><FONT face="Trebuchet MS" size=2>Jim Marsh, PE, LEED 
AP</FONT></DIV>
<DIV align=left><FONT face="Trebuchet MS" size=2>SEG, Inc.</FONT></DIV>
<DIV align=left><FONT face="Trebuchet MS" size=2>2550 Walsh Avenue</FONT></DIV>
<DIV align=left><FONT face="Trebuchet MS" size=2>Suite 120</FONT></DIV>
<DIV align=left><FONT face="Trebuchet MS" size=2>Santa Clara, CA 
95051</FONT></DIV>
<DIV align=left><FONT face="Trebuchet MS" size=2>Desk: 408 260 8008 Ext 
210</FONT></DIV>
<DIV align=left><FONT face="Trebuchet MS" size=2>Cell: 408 656 3096</FONT></DIV>
<DIV align=left><FONT face="Trebuchet MS" size=2>Fax: 408 260 8018</FONT></DIV>
<DIV align=left><A href="http://seg-corp.com/"><FONT face="Trebuchet MS" 
size=2>http://seg-corp.com/</FONT></A></DIV>
<DIV align=left><FONT face=Arial size=2></FONT>&nbsp;</DIV>
<DIV align=left><SPAN style="FONT-SIZE: 10pt; COLOR: #1f497d"></SPAN><FONT 
face=Arial size=2></FONT>&nbsp;</DIV>
<DIV align=left><FONT size=2><SPAN style="FONT-WEIGHT: bold">This communication 
constitutes an electronic communication within the meaning of the Electronic 
Communications Privacy Act, 18 USC 2510, and its disclosure is strictly limited 
to the recipient intended by the sender of this message. &nbsp;This 
communication may contain confidential and privileged material for the sole use 
of the intended recipient and receipt by anyone other than the intended 
recipient does not constitute a loss of the confidential or privileged nature of 
the communication. &nbsp;Any review or distribution by others is strictly 
prohibited. &nbsp;If you are not the intended recipient please contact the 
sender by return electronic mail and delete all copies of this 
communication.</SPAN><FONT face=Arial><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><?xml:namespace prefix = o ns = 
"urn:schemas-microsoft-com:office:office" /><o:p></o:p></SPAN></FONT></FONT> 
<P style="TEXT-ALIGN: center" align=center><I><FONT color=#007f00 size=2><SPAN 
style="FONT-SIZE: 10.5pt; COLOR: #007f00; FONT-STYLE: italic">Please consider 
the environment before printing this email</SPAN></FONT></I><FONT face=Arial 
size=2><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><o:p></o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN 
style="FONT-SIZE: 12pt"><o:p>&nbsp;</o:p></SPAN></FONT></P></DIV>
<DIV>&nbsp;</DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> equest-users-bounces@lists.onebuilding.org 
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Pasha 
Korber-Gonzalez<BR><B>Sent:</B> Thursday, April 01, 2010 1:11 PM<BR><B>To:</B> 
James Hansen<BR><B>Cc:</B> equest-users@lists.onebuilding.org<BR><B>Subject:</B> 
Re: [Equest-users] Chiller ROI - HELP!<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV>Brett,</DIV>
<DIV>&nbsp;</DIV>
<DIV>to get better part load data and efficiency of your proposed chiller 
replacement, call your chill sales engineer and ask them to generate a part load 
performance report for you in 10% unloading increments, then you can see the 
decrease in performance efficiency for each part-load step of the chiller.&nbsp; 
Also be sure that you recognize if you are looking at RATED Conditions (which 
means chiller performance at ARI standard conditions), or at DESIGN conditions 
(which are your project's specified operating conditions--this would account for 
part load efficiencies if you were running a 12-or 14 Degree delta-T across your 
chiller.)</DIV>
<DIV>&nbsp;</DIV>
<DIV>Before you set up a new performance curve you will need to get this data 
supplied from the manufacturer.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Pasha<BR><BR></DIV>
<DIV class=gmail_quote>On Thu, Apr 1, 2010 at 2:01 PM, James Hansen <SPAN 
dir=ltr>&lt;<A 
href="mailto:JHANSEN@ghtltd.com">JHANSEN@ghtltd.com</A>&gt;</SPAN> wrote:<BR>
<BLOCKQUOTE class=gmail_quote 
style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">
  <DIV lang=EN-US link="blue" vlink="purple">
  <DIV>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d">KW/ton drops off with 
  decreasing part load, and since the chiller isn&#8217;t always operating at ARI full 
  load conditions, you can&#8217;t just divide total chiller energy consumption (in 
  KWH) by the total cooling load (in btu) and hope to get anywhere near the full 
  load rated KW/ton.</SPAN></P>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d"></SPAN>&nbsp;</P>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d">As you go about this ROI 
  study, make sure that when you are analyzing your proposed chiller 
  replacement, that you create a custom EIR vs PLR curve based on manufacturer&#8217;s 
  data, otherwise you&#8217;re using a default DOE-2 curve that isn&#8217;t necessarily 
  correct.</SPAN></P>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d"></SPAN>&nbsp;</P>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d">Furthermore, to make the study 
  worthwhile, the existing chiller model really needs to be normalized as best 
  as possible to actual building operating conditions.&nbsp; You can get away 
  without doing it for a simple comparison, but it would be more accurate if you 
  normalized to utility bills.</SPAN></P>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d"></SPAN>&nbsp;</P>
  <DIV>
  <P class=MsoNormal><B><SPAN style="COLOR: teal">GHT 
  Limited<BR></SPAN></B><B><SPAN><SPAN style="COLOR: black">James 
  Hansen</SPAN></SPAN></B><B><SPAN style="COLOR: black">, PE, LEED 
  AP</SPAN></B></P>
  <P class=MsoNormal><B><SPAN style="FONT-SIZE: 10pt; COLOR: black">Senior 
  Associate</SPAN></B><B><SPAN style="COLOR: black"></SPAN></B></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt"><SPAN 
  style="COLOR: black">1010 N. Glebe Rd, Suite 200</SPAN></SPAN><SPAN 
  style="COLOR: #1f497d"></SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt"><SPAN 
  style="COLOR: black">Arlington</SPAN><SPAN style="COLOR: black">, </SPAN><SPAN 
  style="COLOR: black">VA</SPAN><SPAN style="COLOR: black">&nbsp; </SPAN><SPAN 
  style="COLOR: black">22201-4749</SPAN></SPAN><SPAN 
  style="COLOR: black"></SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt; COLOR: black">703-338-5754 
  (Cell)</SPAN><SPAN style="COLOR: black"></SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt; COLOR: black">703-243-1200 
  (Office)</SPAN><SPAN style="COLOR: black"></SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt; COLOR: black">703-276-1376 
  (Fax)</SPAN><SPAN style="COLOR: black"></SPAN></P>
  <P class=MsoNormal><SPAN style="COLOR: teal"><A href="http://www.ghtltd.com/" 
  target=_blank><SPAN 
  style="FONT-SIZE: 10pt">www.ghtltd.com</SPAN></A></SPAN></P>
  <P class=MsoNormal><B><SPAN style="COLOR: #31849b"></SPAN></B>&nbsp;</P></DIV>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d"></SPAN>&nbsp;</P>
  <DIV>
  <DIV 
  style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; PADDING-LEFT: 0in; PADDING-BOTTOM: 0in; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
  <P class=MsoNormal><B><SPAN style="FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
  style="FONT-SIZE: 10pt"> <A 
  href="mailto:equest-users-bounces@lists.onebuilding.org" 
  target=_blank>equest-users-bounces@lists.onebuilding.org</A> [mailto:<A 
  href="mailto:equest-users-bounces@lists.onebuilding.org" 
  target=_blank>equest-users-bounces@lists.onebuilding.org</A>] <B>On Behalf Of 
  </B>Brett Sanicola<BR><B>Sent:</B> Thursday, April 01, 2010 2:38 
  PM<BR><B>To:</B> <A href="mailto:equest-users@lists.onebuilding.org" 
  target=_blank>equest-users@lists.onebuilding.org</A><BR><B>Subject:</B> 
  [Equest-users] Chiller ROI - HELP!</SPAN></P></DIV></DIV>
  <DIV>
  <DIV></DIV>
  <DIV class=h5>
  <P class=MsoNormal>&nbsp;</P>
  <P class=MsoNormal>I've been attempting to calculate a simple ROI for a new 
  250 ton chiller our client wants to install to replace his older 
  chiller.&nbsp; I ran the simulation for the default "high rise hotel" 
  construction which, to my luck, is quite similar to the actual building.&nbsp; 
  The detailed results, however, are not making sense to me.&nbsp; Specifically, 
  when I look at Equipment Loads and Energy Use for the Chiller, the Elec Use 
  and Cool Load don't coincide given the default Chiller efficiency of 
  .67kw/ton.&nbsp; For example they give a Chiller Elec Use of 535453 KWH and a 
  Cool Load of 3294 MBTU.&nbsp; However, according to my calculations, at 
  .67KW/TON, 535453 KWH should give me closer to 9590 MBTU.&nbsp; I see most of 
  the hours are in part load range, but does the efficiency drop off that 
  dramatically at part load that it would explain the discrepancy?&nbsp; Which 
  numbers should I base my analysis on, the Cool Load number or the Elec Use 
  number.</P>
  <P class=MsoNormal>&nbsp;</P>
  <P class=MsoNormal>Also, on the same page (Equipment Loads and Energy Usage), 
  it gives me a peak load of 2436 KBTU/HR.&nbsp; However, when I go to the 
  section titled "Building Peak Load Components" the peak cooling load is 
  significantly less (1619 KBTU/HR)</P>
  <P class=MsoNormal>&nbsp;</P>
  <P class=MsoNormal>At this point, I have no idea what any number represents, 
  since I don&#8217;t know how it was calculated.</P>
  <P class=MsoNormal>&nbsp;</P>
  <P class=MsoNormal>I greatly appreciate any help!&nbsp; Thanks.</P>
  <P class=MsoNormal>&nbsp;</P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 10pt">Respectfully,</SPAN></P>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman','serif'"></SPAN>&nbsp;</P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 10pt">Brett Sanicola</SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 10pt">Engineer</SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 10pt">ASB Engineering</SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 10pt">(516) 
  785-4200</SPAN></P></DIV></DIV></DIV></DIV>
  <P align=left><FONT size=2><FONT face=Tahoma><FONT color=#0000ff>
  <HR>
  </FONT></FONT><FONT color=#0000ff><FONT color=#000000><FONT face=Arial>The 
  information contained in this communication is confidential, may be 
  privileged, and is intended only for the use of the addressee.&nbsp; It is the 
  property of GHT Limited.&nbsp; Unauthorized use, disclosure or copying of this 
  communication or any part thereof is strictly prohibited and may be 
  unlawful.&nbsp; If you have received this communication in error, please 
  notify me immediately by return e-mail or by e-mail to </FONT><A 
  href="mailto:ght@ghtltd.com" target=_blank><FONT 
  face=Arial>ght@ghtltd.com</FONT></A><FONT face=Arial>, and destroy this 
  communication and all copies thereof, including all attachments.&nbsp; Thank 
  you.</FONT></FONT><FONT face=Tahoma color=#000000></FONT></FONT></FONT> 
  <P></P><BR>_______________________________________________<BR>Equest-users 
  mailing list<BR><A 
  href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" 
  target=_blank>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</A><BR>To 
  unsubscribe from this mailing list send &nbsp;a blank message to <A 
  href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR><BR>
  <P></P></BLOCKQUOTE></DIV><BR></BODY></HTML>