I also found some formulas when tooling around in the archives the other day and could love to get comments, if any about their utlity:<br><br>EIR=(1/EER-0.012167)/((1/3.413)+0.012167)<br>and<br>EIR=((1/SEER*0.778+1.4)-0.012167)/((1/3.413)+0.012167)<br>
<br>Anyone remember these that knows the source and utility? Is there one for HSPF?<br><br>Carol<br><br><div class="gmail_quote">On Wed, Mar 24, 2010 at 7:50 AM, Bassam Yammine <span dir="ltr"><<a href="mailto:byammine@flowgroup.ca">byammine@flowgroup.ca</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">








<div link="blue" vlink="purple" lang="EN-US">

<div>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Hi Michael, to modify the EIR
(which is in Btu/Btu) in the detailed mode, click on the Air-Side HVAC icon at
the top of your screen, then double click on the heat pump. Under the cooling
and heating tabs you will find a Unitary Power tab where you can change your
EIR.</span></p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Regards,</span></p>

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);">Bassam</span></p><div class="im">

<p class="MsoNormal"><span style="color: rgb(31, 73, 125);"> </span></p>

<div>

<div style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">

<p class="MsoNormal"><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>M.
Shields<br>
<b>Sent:</b> Wednesday, March 24, 2010 6:59 AM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Heat Pump Efficiencies</span></p>

</div>

</div>

<p class="MsoNormal"> </p>

</div><p class="MsoNormal">Hi All,</p><div><div></div><div class="h5">

<p class="MsoNormal"> </p>

<p class="MsoNormal">I am still fairly new to equest and I am having a bit of
trouble with setting up my HVAC.  I created a building model using the
equest wizard and now I have made a number of changes within the detailed DOE2
interface.  The building uses air source heat pumps for the HVAC and I
would like to change the EER/COP values without going back to the wizard, but I
cannot figure where these values are stored.  Is there an easy way to make
changes like that within DOE2?</p>

<p class="MsoNormal"> </p>

<p class="MsoNormal">Thanks,</p>

<p class="MsoNormal">Michael Shields</p>

<p class="MsoNormal"> </p>

<p class="MsoNormal"><span style="font-size: 10pt; font-family: "Book Antiqua","serif";">____________________________<br>
Michael Shields<br>
Facility Strategies Group<br>
2222 Gold Hill Road, Suite 5<br>
Fort Mill, SC 29708<br>
Phone: 803-493-4507<br>
Fax: 803-548-2511<br>
Email: <a href="mailto:mshields@fstrategies.com" target="_blank">mshields@fstrategies.com</a></span></p>

<p class="MsoNormal"> </p>

</div></div></div>

</div>


<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>