<div>I can&#39;t confirm for you your question about allowable zones, but I did want to offer a couple of cents from my perspective...I hope that you are not planning to zone each space for each floor.  This is what I call a simulation nightmare--primarily for you as the simulator, but also for anyone who is or will be reviewing your model.</div>

<div> </div>
<div>The zones are specifically thermal zones, so where you have alike thermal characteristics you can zone these spaces together as one zone.  Be mindful of zoning like spaces, but different perimeter exposures--for example you should not create a thermal zone that has both an east &amp; south perimeter exposure because of the envelope loads that are experienced by these differing exposures.</div>

<div> </div>
<div>Always try to simplify your models to work with as few zones as possible--from an input &amp; file management standpoint.  Remember the more inputs you have, the more you open the door for variable errors in your file.  Sometimes the fewest possible zones might be in the 100&#39;s, or in the 10&#39;s range, but I personally would question any model that used more than 1000 zones for anything unless there were extenuating circumstances.</div>

<div> </div>
<div>If you&#39;d like some extra assistance or suggestions for your thermal zoning approach &amp; input into eQuest, please contact me and send me some pdf&#39;s of your floor plans and I would be happy to help you.</div>

<div> </div>
<div>Pasha<br><br></div>
<div class="gmail_quote">On Tue, Mar 23, 2010 at 11:44 AM, James Hansen <span dir="ltr">&lt;<a href="mailto:JHANSEN@ghtltd.com">JHANSEN@ghtltd.com</a>&gt;</span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal">For those also subscribed to the bldg-sim list, you may have just seem Eric Sturm’s email with an updated spreadsheet comparing DOE2, eQuest, Trace and HAP.</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">I don’t think it’s up-to-date for eQuest, but something on the list scared me.  eQuest isn’t still limited to 1024 zones is it?</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">I’m working on a 19 story building with 100+ spaces per floor, and I’m hoping this isn’t still the case.  I thought I remember seeing that since version 3.37, you’re allowed to have something like 4000 spaces.</p>

<p class="MsoNormal"> </p>
<p class="MsoNormal">Can anyone confirm?  Would really suck to get ¾ of the way thru my model and realize I have to cut back on zoning.</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Thanks!</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><b><span style="COLOR: teal">GHT Limited<br></span></b><b><span><span style="COLOR: black">James Hansen</span></span></b><b><span style="COLOR: black">, PE, LEED AP</span></b></p>
<p class="MsoNormal"><b><span style="COLOR: black; FONT-SIZE: 10pt">Senior Associate</span></b><b><span style="COLOR: black"></span></b></p>
<p class="MsoNormal"><span style="FONT-SIZE: 7.5pt"><span style="COLOR: black">1010 N. Glebe Rd, Suite 200</span></span></p>
<p class="MsoNormal"><span style="FONT-SIZE: 7.5pt"><span style="COLOR: black">Arlington</span><span style="COLOR: black">, </span><span style="COLOR: black">VA</span><span style="COLOR: black">  </span><span style="COLOR: black">22201-4749</span></span><span style="COLOR: black"></span></p>

<p class="MsoNormal"><span style="COLOR: black; FONT-SIZE: 7.5pt">703-338-5754 (Cell)</span><span style="COLOR: black"></span></p>
<p class="MsoNormal"><span style="COLOR: black; FONT-SIZE: 7.5pt">703-243-1200 (Office)</span><span style="COLOR: black"></span></p>
<p class="MsoNormal"><span style="COLOR: black; FONT-SIZE: 7.5pt">703-276-1376 (Fax)</span><span style="COLOR: black"></span></p>
<p class="MsoNormal"><span style="COLOR: teal"><a href="http://www.ghtltd.com/" target="_blank"><span style="COLOR: blue; FONT-SIZE: 10pt">www.ghtltd.com</span></a></span></p>
<p class="MsoNormal"><b><span style="COLOR: #31849b"> </span></b></p>
<p class="MsoNormal"> </p></div></div>
<p align="left"><font size="2"><font face="Tahoma"><font color="#0000ff">
<hr>
</font></font><font color="#0000ff"><font color="#000000"><font face="Arial">The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to </font><a href="mailto:ght@ghtltd.com" target="_blank"><font face="Arial">ght@ghtltd.com</font></a><font face="Arial">, and destroy this communication and all copies thereof, including all attachments.  Thank you.</font></font><font color="#000000" face="Tahoma"></font></font></font> 
<p></p><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></p></blockquote></div><br>