That is the same logic i went through, and double checking my plenum zones have shown that they in fact are all unconditioned or plenum.  I can send out the .inp file or the output reports if people have time to check it out.  <br>
<br><div class="gmail_quote">On Tue, Mar 16, 2010 at 3:49 AM, Gaurav Mehta <span dir="ltr"><<a href="mailto:gmehta75@gmail.com">gmehta75@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin: 0pt 0pt 0pt 0.8ex; border-left: 1px solid rgb(204, 204, 204); padding-left: 1ex;">
<div style="padding-left: 10px; padding-right: 10px; padding-top: 15px;" name="Compose message area">
<div><font face="Arial" size="2">Rob/ Pasha,</font></div>
<div><font face="Arial" size="2"></font> </div>
<div><font face="Arial" size="2">The kBtu/SF on the BEPS Report and $/SF on ES-D 
report use the conditioned floor area. Please see the LS-C report that shows the 
conditioned floor area you are modeling. </font></div>
<div><font face="Arial" size="2"></font> </div>
<div><font face="Arial" size="2">LV-B report does show all the spaces including 
unconditioned spaces and plenums, but the total area is not used 
in the summary report.</font></div>
<div><font face="Arial" size="2"></font> </div>
<div><font face="Arial" size="2">Without looking at your model, I can 
only make a guess that you might be modeling the Plenum zones as 
'Conditioned'. By the numbers that you have provided:</font></div>
<div><font face="Arial" size="2"></font> </div>
<div><font face="Arial" size="2">9,500 SF x( 3 [floors] + 3 [plenums] ) = 
57,000 SF subtract any unconditioned spaces and the answer would be ~ 
50,000 SF</font></div>
<div><font face="Arial" size="2"></font> </div>
<div><font face="Arial" size="2">Please check your inputs for plenum zones under 
both 'Spaces' and 'Zones' and in both, the 'Zone Type' input should 
either be 'Unconditioned' or 'Plenum'.</font></div>
<div><font face="Arial" size="2"></font> </div>
<div><font face="Arial" size="2">Hope it helps.</font></div>
<div><font face="Arial" size="2"></font> </div>
<div><font face="Arial" size="2"></font> </div>
<div><font face="Arial" size="2">Best regards,</font></div>
<div><font face="Arial" size="2"></font> </div>
<div><font face="Arial" size="2">Gaurav Mehta</font></div>
<div><font face="Arial" size="2">Sustainable Building Analyst</font></div>
<div><font face="Arial" size="2">Stantec</font></div>
<div><br></div>
<div style="font: 10pt Tahoma;">
<div style="background: none repeat scroll 0% 0% rgb(245, 245, 245);">
<div><b>From:</b> <a title="mailto:pasha.pkconsulting@gmail.com
CTRL + Click to follow link" href="mailto:pasha.pkconsulting@gmail.com" target="_blank">Pasha Korber-Gonzalez</a> </div>
<div><b>Sent:</b> Monday, March 15, 2010 13:40</div>
<div><b>To:</b> <a title="mailto:rdh4176@gmail.com
CTRL + Click to follow link" href="mailto:rdh4176@gmail.com" target="_blank">Rob Hudson</a> </div>
<div><b>Cc:</b> <a title="mailto:equest-users@lists.onebuilding.org
CTRL + Click to follow link" href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a> 
</div>
<div><b>Subject:</b> Re: [Equest-users] Building Square 
Footage</div></div></div><div><div></div><div class="h5">
<div><br></div>
<div>Hi Rob,</div>
<div> </div>
<div>this is a good question and important to understand about how inputs are 
translated to DOE & reported in the output.</div>
<div> </div>
<div>Yes you are right that the summary is accounting for the floor area of the 
unconditioned spaces as well and the plenum spaces.  If you look at report 
LV-B, summary of spaces in your project you will find the info you are looking 
for.</div>
<div> </div>
<div>This report is a listing of all the spaces (or thermal zones) in the 
project.  Theis listing incudes both conditioned spaces as well as 
unconditioned spaces and plenums.  In reviewing this report, pay special 
attention to the column labeled "space floor multiplier".  The total area 
and volume for each space is this value times the area and volume listed in the 
last two columns.  The building totals row includes the effect of these 
multipliers, but the area includes plenums and unconditioned spaces as 
well. </div>
<div> </div>
<div>Pasha<br><br></div>
<div class="gmail_quote">On Mon, Mar 15, 2010 at 2:02 PM, Rob Hudson <span dir="ltr"><<a title="mailto:rdh4176@gmail.com
CTRL + Click to follow link" href="mailto:rdh4176@gmail.com" target="_blank">rdh4176@gmail.com</a>></span> wrote:<br>
<blockquote style="border-left: 1px solid rgb(204, 204, 204); margin: 0px 0px 0px 0.8ex; padding-left: 1ex;" class="gmail_quote">This seems like a silly question, but i would like some 
  input regardless.  My building has three floors, each about 9,500 square 
  feet.  However, the looking at the BEPU and other reports are showing a 
  total utility cost of 110632$ and a $/sqft of 2.25.  this shows a sqft of 
  about 50,000 for the building.  Is this something that i should disregard 
  or is it relevant?  I have also modeled the unconditioned space above 
  each room as a separate space.  Could the program be combining this 
  plenum space into the sqft of the entire building?  Is this plenum sqft 
  affecting the output of the reports?  any help is greatly appreciated.<br clear="all"><br>-- <br><font color="#888888">Rob 
  Hudson<br></font><br>_______________________________________________<br>Equest-users 
  mailing list<br><a title="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
CTRL + Click to follow link" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To 
  unsubscribe from this mailing list send  a blank message to <a title="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG
CTRL + Click to follow link" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>
</div></div><p>
</p><hr><div class="im">
<p></p>_______________________________________________<br>Equest-users mailing 
list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>To 
unsubscribe from this mailing list send  a blank message to 
<a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br></div></div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Rob Hudson<br>