<br><font size=2 face="sans-serif">If a building is going under LEED NC,
does it not have to be rotated even if it is existing? I think the argument
for this had something to do with the fact that the AE team could still
modify the building envelope to make it more efficient.</font>
<br>
<br><font size=2 face="sans-serif">My understanding was that if a building
was applied under LEED EB then it would not have to be rotated. </font>
<br>
<br><font size=2 face="sans-serif">I could be very wrong though.</font>
<br>
<br><font size=2 face="sans-serif">-----------------------------------------<br>
Jack Vithayapun<br>
Building Systems Engineer<br>
USDA Forest Service<br>
1720 Peachtree Street, NW<br>
Atlanta, GA 30309<br>
Tel: (404)-347-2522<br>
Fax: (404)-347-2399<br>
</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td width=40%><font size=1 face="sans-serif"><b>Gregg Liddick <gliddick@theepstengroup.com></b>
</font>
<br><font size=1 face="sans-serif">Sent by: equest-users-bounces@lists.onebuilding.org</font>
<p><font size=1 face="sans-serif">03/12/2010 11:42 AM</font>
<td width=59%>
<table width=100%>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">To</font></div>
<td><font size=1 face="sans-serif">James Hansen <JHANSEN@ghtltd.com>,
Erik Dyrr <erik.dyrr@gmail.com>, "omoltay@mimtarch.com"
<omoltay@mimtarch.com></font>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">cc</font></div>
<td><font size=1 face="sans-serif">"equest-users@lists.onebuilding.org"
<equest-users@lists.onebuilding.org>, "bldg-sim@lists.onebuilding.org"
<bldg-sim@lists.onebuilding.org></font>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">Subject</font></div>
<td><font size=1 face="sans-serif">Re: [Equest-users] [Bldg-sim] Existing
Building LEED Baseline</font></table>
<br>
<table>
<tr valign=top>
<td>
<td></table>
<br></table>
<br>
<br>
<br><font size=2 color=#004080 face="Calibri">James is correct regarding
the windows – they should be modeled using the pre-renovation U-value
and SHGC in the baseline case.</font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 color=#004080 face="Calibri">The baseline case should
not be rotated for existing buildings, nor should it be rotated if the
construction is an addition. The basis of the rotation requirement
for new construction is to reward the project team for choosing the most
efficient orientation for a building and this is not an option for existing
buildings and additions.</font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 color=#004080 face="Calibri">Best Regards,</font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 face="Times New Roman">Gregg Liddick, EIT, LEED<sup>®</sup>
AP</font>
<br><font size=2 face="Calibri"> </font>
<br><font size=2 face="Times New Roman">The Epsten Group, Inc.</font>
<br><font size=2 face="Times New Roman">429 Edgewood Avenue</font>
<br><font size=2 face="Times New Roman">Atlanta GA 30312</font>
<br><font size=2 face="Times New Roman">Phone: 404-577-0370 ext.
102</font>
<br><font size=2 face="Times New Roman">Fax: 404-577-1739</font>
<br><a href=http://www.theepstengroup.com/ target=_blank><font size=2 face="Times New Roman"><u>www.theepstengroup.com</u></font></a>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 color=#008250 face="Times New Roman">Please consider the
environment before printing this e-mail.</font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=1 face="Times New Roman">This transmission is intended exclusively
for the individual or entity to which it is addressed. This communication
may contain information that is confidential, proprietary, privileged or
otherwise exempt from disclosure. If you are not the named addressee, you
are NOT authorized to read, print, retain, copy or disseminate this communication,
its attachments or any part of them. If you have received this communication
in error, please notify the sender immediately and delete this communication
from all computers. This communication does not form any contractual obligation
on behalf of the sender, the sender's employer, or the employer's parent
company, affiliates or subsidiaries.</font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 face="Tahoma"><b>From:</b> bldg-sim-bounces@lists.onebuilding.org
[mailto:bldg-sim-bounces@lists.onebuilding.org] <b>On Behalf Of </b>James
Hansen<b><br>
Sent:</b> Thursday, March 11, 2010 9:50 PM<b><br>
To:</b> Erik Dyrr; omoltay@mimtarch.com<b><br>
Cc:</b> equest-users@lists.onebuilding.org; bldg-sim@lists.onebuilding.org<b><br>
Subject:</b> Re: [Bldg-sim] Existing Building LEED Baseline</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=2 color=#004080 face="Calibri">I may be misreading one of
your emails, but if you are doing a building renovation to an existing
building, even if you ARE changing out windows, the baseline model retains
the envelope characteristics of the existing building. You don’t
have to bring the baseline windows up to 90.1 standards unless it is a
portion of the building that is being added under the proposed work.</font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 color=#004080 face="Calibri">Also, check the archives
– I thought that some GBCI reviews of projects have required the four
orientations even for existing buildings.</font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 color=#008080 face="Arial"><b>GHT Limited</b></font><font size=2 face="Arial"><b><br>
James Hansen</b></font><font size=2 face="Calibri"><b>, PE, LEED AP</b></font>
<br><font size=2 face="Arial"><b>Senior Associate</b></font>
<br><font size=1 face="Arial">1010 N. Glebe Rd, Suite 200</font>
<br><font size=1 face="Arial">Arlington, VA 22201-4749</font>
<br><font size=1 face="Arial">703-338-5754 (Cell)</font>
<br><font size=1 face="Arial">703-243-1200 (Office)</font>
<br><font size=1 face="Arial">703-276-1376 (Fax)</font>
<br><a href=http://www.ghtltd.com/><font size=2 color=blue face="Arial"><u>www.ghtltd.com</u></font></a>
<br><font size=2 color=#3f8080 face="Calibri"><b> </b></font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 face="Tahoma"><b>From:</b> bldg-sim-bounces@lists.onebuilding.org
[mailto:bldg-sim-bounces@lists.onebuilding.org] <b>On Behalf Of </b>Erik
Dyrr<b><br>
Sent:</b> Thursday, March 11, 2010 8:25 PM<b><br>
To:</b> omoltay@mimtarch.com<b><br>
Cc:</b> equest-users@lists.onebuilding.org; bldg-sim@lists.onebuilding.org<b><br>
Subject:</b> Re: [Bldg-sim] Existing Building LEED Baseline</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman">If the windows are existing to
remain, then you are correct that they would be the same in the proposed
and baseline. If you change out windows then the baseline would be min
performance per ASHRAE.</font>
<br><font size=3 face="Times New Roman"> </font>
<br><font size=3 face="Times New Roman">I think your assumption about not
changing the windows by orientation is correct. I am not sure you
even need to do four orientations if the building is existing.</font>
<br><font size=3 face="Times New Roman">On Mon, Feb 22, 2010 at 12:14 PM,
<</font><a href=mailto:omoltay@mimtarch.com><font size=3 color=blue face="Times New Roman"><u>omoltay@mimtarch.com</u></font></a><font size=3 face="Times New Roman">>
wrote:</font>
<br><font size=3 face="Times New Roman">Dear All,<br>
<br>
Just want to have your opinions about this: Since the building we are<br>
applying for LEED certification is an existing building (and there are
no<br>
additions), the building envelope in our baseline model is identical to<br>
the existing conditions in real life. We have interpreted this to also<br>
include the SHGC on the windows and any fixed shading devices on the<br>
windows, so these we have also modeled as existing in real life.<br>
<br>
I assume this would further mean that when we are doing the baseline<br>
simulation in four rotations, we do not need to change anything with the<br>
SHGC's on the windows in each rotation.<br>
<br>
Although according to Appendix G I believe this should be the way (since<br>
the remark involving existing buildings is printed as the last entry in<br>
the table), I still have some doubts as in the LEED NC reference guide<br>
they have only printed that remark for the building envelope involving<br>
opaque surfaces, and the criteria involving windows seems to be<br>
independent of this (on p.270).<br>
<br>
Thanks for any replies,<br>
<br>
Omer Moltay, LEED AP<br>
Mimta Ltd.<br>
<br>
_______________________________________________<br>
Bldg-sim mailing list</font><font size=3 color=blue face="Times New Roman"><u><br>
</u></font><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"><font size=3 color=blue face="Times New Roman"><u>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</u></font></a><font size=3 face="Times New Roman"><br>
To unsubscribe from this mailing list send a blank message to </font><a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"><font size=3 color=blue face="Times New Roman"><u>BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</u></font></a>
<br><font size=3 face="Times New Roman"> </font>
<div align=center>
<br>
<hr></div>
<br><font size=2 face="Arial">The information contained in this communication
is confidential, may be privileged, and is intended only for the use of
the addressee. It is the property of GHT Limited. Unauthorized
use, disclosure or copying of this communication or any part thereof is
strictly prohibited and may be unlawful. If you have received this
communication in error, please notify me immediately by return e-mail or
by e-mail to </font><a href=mailto:ght@ghtltd.com><font size=2 color=blue face="Arial"><u>ght@ghtltd.com</u></font></a><font size=2 face="Arial">,
and destroy this communication and all copies thereof, including all attachments.
Thank you.</font><tt><font size=2>_______________________________________________<br>
Equest-users mailing list<br>
</font></tt><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"><tt><font size=2>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<br>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<br>
</font></tt></a>
<br>