Bassam,<br><br>If you look at the polygon for each of the affected spaces you will notice that the vertices which connect them are off by a small amount. Once you make them match your exterior wall should go away. In detailed edit you might have to actively delete it and replace it with an interior wall. It is always good to catch this kind of thing when you are in the wizard by looking carefully at your zone characteristics rendering on screen 2. Exterior walls show up as darker than interior walls and when you see them in the wrong place you can go back into your footprint and change the vertices right then.<br>
<br>Hope this helps,<br>Carol<br><br><div class="gmail_quote">On Tue, Mar 9, 2010 at 11:32 PM, Bassam Yammine <span dir="ltr"><<a href="mailto:byammine@flowgroup.ca">byammine@flowgroup.ca</a>></span> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
<div>
<div><font color="#000000" face="Arial" size="2">Hi, I'm modeling a building by creating a number of shells that have different use and systems. The building consists mainly of an office space and a Garage area. Both are conditioned. My intent was to create the garage under a separate shell and have it positioned at 0 ft from the reference shell.</font></div>
<div><font face="Arial" size="2">The problem I noticed is that the wall between the two shells is showing to be an exterior wall, whereas it is supposed to be an interior wall.</font></div>
<div><font face="Arial" size="2">Is there a way to change the wall type in the detailed edit mode without going back to the wizzard so other data inputted in the detailed mode is not lost?</font></div>
<div><font face="Arial" size="2"></font> </div>
<div><font face="Arial" size="2">Thanks.</font></div>
<div><font face="Arial" size="2">Bassam</font></div></div><br>_______________________________________________<br>