Luka-<br>
<br>
The errors that you have attached below are not necessarily related to
the reason your simulation is failing.  The QC reporting mechanism
relies on results generated during the course of a successful
simulation, and the fact that you are unable to a simulation is the
reason
for some of the nonsensical numbers in the QC reporting results.  Check
the .sim file for information on why the simulation won't run.<br>
<br>
-Luke<br>
<pre class="moz-signature" cols="72">Lukas Hovee
Madison Engineering, PS
444 NE Ravenna Blvd, Suite 406
Seattle, WA 98115</pre>
On 3/9/2010 11:19 AM, Matutinovic, Luka wrote:
<blockquote
 cite="mid:A344C2884FB3234390270653C20B3D6D83ADF5@to1exc02wp.halsall.com"
 type="cite">
  <meta http-equiv="Content-Type"
 content="text/html; charset=ISO-8859-1">
  <meta name="Generator" content="Microsoft Word 12 (filtered medium)">
  <style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Univers;
        panose-1:2 11 6 3 2 2 2 3 2 4;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.5pt;
        font-family:"Univers","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal;
        font-family:"Univers","sans-serif";
        color:windowtext;
        font-weight:normal;
        font-style:normal;
        text-decoration:none none;}
span.EmailStyle18
        {mso-style-type:personal-reply;
        font-family:"Univers","sans-serif";
        color:blue;
        font-weight:normal;
        font-style:normal;
        text-decoration:none none;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {page:Section1;}
-->
  </style>
<!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
  <div class="Section1">
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">Hello
All,<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">My
simulation
won’t run because of unusual errors that I’ve never seen before, but
that I
picked up when looking at the details of the QC report:<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">Here
is a summary
of the errors.  If anyone has seen this before and may have ideas about
what’s causing it, I’d really appreciate the help.  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">I
haven’t attached
the .pd2 and .inp file due to file size, but I can forward them to
anyone who’s
interested in taking a peek.<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">Many
thanks,<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">Luka<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA"><o:p> </o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">====================================================================<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">4)
Hours of
Operation                                       
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">           
Hours
of
Operation                               
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
Fan
vs. Occupancy
Hours                     
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
The
average occupancy / fan operation ratio for the building is
-72480000.00
and appears high (error above 1.75, see PS-E & SS-C reports).<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
Fan
vs. Lighting Operating
Hours                       
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
The
average hours of light operation / fan operation ratio for the building
is
0 and appears low (error below 0.25, see PS-E & SS-C reports).<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
Fan
vs. Equipment Operating
Hours                   
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
The
average hours of plug load operation / fan operation ratio for the
building
is 0 and appears low (error below 0.25, see PS-E & SS-C reports).<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">5)
HVAC Equipment
Descriptions                                  
            <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">           
Air-Side
Checks                                   
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
CFM/ton
of
cooling                   
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
The
supply air flow for system 'E1 Sys1 (PIU) (B)' is 120000.0 cfm/ton and
appears high (see SV-A report).<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">           
User
Input Equipment Performance
Curves                                
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
Curve
coefficients sum to
1                  
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
The
sum of the coefficients for the 'ForCurve w Inlet Vanes FPLR' curve is
0.99
and does not equal 1 (check Curve Inputs for errors).<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">6)
Zone Control
and Equipment
Sizing                                        
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">           
Primary
Equipment Unable to Meet
Loads                                  
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
Chillers            
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
Chillers
on Loop: 'Chilled Water Loop' have a total Capacity to Load Ratio of
-1.00 and may be undersized (Error: Ratio <   0.90) <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">Total
Chiller Capacity
on Loop = -2 (Btu/hr)<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">Peak
CHW Loop Load
= -1 (Btu/hr)<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">Chiller:
'Chiller1a
(ElCentHerm)' capacity = -1 (Btu/hr)<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
Chiller:
'Chiller1b (ElCentHerm)' capacity = -1 (Btu/hr)<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
Boilers             
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
Boilers
on Loop: 'Hot Water Loop' have a total Capacity to Load Ratio of -0.00
and may be undersized (Error: Ratio < 0.90) <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">Total
Boiler
Capacity on Loop = -2 (Btu/hr)<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">Peak
HW Loop Load
= -1 (Btu/hr)<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">Boiler:
'Boiler1a
(HWNatDrft)' capacity = -1 (Btu/hr)<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
Boiler:
'Boiler1b (HWNatDrft)' capacity = -1 (Btu/hr)<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">           
Circulation
Loop
Overload                                 
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
Circulation
Loop
Overload                     
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">7)
HVAC Load &
Performance
Results                                      
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">           
Monthly
Pattern of HVAC
Loads           
                       
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
Heating
Coil Loads                    
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
System
'E1 Sys1 (PIU) (B)' has a high Summer/Winter heating coil load ratio of
1.0 (error over 0.2, see SS-D report).<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">           
Primary
HVAC Equipment
Performance                         
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
Average
Chiller
COP                 
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
'Chiller1a
(ElCentHerm)' Average Yearly COP (Total Annual Output/Total Annual
Input) = -1.0 and may be low (Error: Ratio <= 1).<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
'Chiller1b
(ElCentHerm)' Average Yearly COP (Total Annual Output/Total Annual
Input) = -1.0 and may be low (Error: Ratio <= 1).<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
Average
Cooling Tower COP                 
  <o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                                               
'Open
Tower' Average Yearly COP (Total Annual Output/Total Annual Input) =
-1.0
may be low (Error: Ratio <= 1).<o:p></o:p></span></p>
  <p class="MsoNormal"><span style="font-size: 10pt;" lang="EN-CA">                       
  <o:p></o:p></span></p>
  </div>
  <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>