<div>A good rule-of-thumb assumption for any new construction is ACH=0.20.  I believe this is based on an ASHRAE reference.  For existing building construction it can be slightly higher than that up to significantly higher depending on the construction type and age of the building.</div>

<div> </div>
<div>Generally for new construction 0.20 is a good solid assumption.</div>
<div> </div>
<div>pk<br></div>
<div class="gmail_quote">On Mon, Mar 8, 2010 at 6:06 PM, steve clark <span dir="ltr">&lt;<a href="mailto:scstevemclark@gmail.com">scstevemclark@gmail.com</a>&gt;</span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">Hi Nick,<br><br>Do you have a reference for the ASHRAE ACH estiamtes you mentioned?<br><br>thanks!<br>Steve<br>
<br>
<div class="gmail_quote">
<div>
<div></div>
<div class="h5">On Mon, Mar 8, 2010 at 7:47 PM, Nick Caton <span dir="ltr">&lt;<a href="mailto:ncaton@smithboucher.com" target="_blank">ncaton@smithboucher.com</a>&gt;</span> wrote:<br></div></div>
<blockquote style="BORDER-LEFT: rgb(204,204,204) 1px solid; MARGIN: 0pt 0pt 0pt 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div>
<div></div>
<div class="h5">
<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)">I’ve done exactly that in the past for the exactly the same purpose!</span></p>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)"> </span></p>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)">The only difference is I believe I always punch in the differences in the metric of ACH.  ASHRAE fundamentals provides some guidance regarding air change rates to expect for various classes of construction as a function of outdoor design temperature, and that was the best I could base my existing construction off of from what info I had available.</span></p>

<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)"> </span></p>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)">Come up with a  “leakiness” for both you construction, old and new windows, and do the weighted average jig =).</span></p>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)"> </span></p>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)">Kudos on your fancy facade spelling also ;)! </span></p>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)"> </span></p>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)">~Nick</span></p>
<div>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)"><img alt="cid:489575314@22072009-0ABB" width="119" height="37"></span><b><span style="COLOR: rgb(45,77,94)"></span></b></p>
<p class="MsoNormal"><b><span style="COLOR: rgb(45,77,94)"> </span></b></p>
<p class="MsoNormal"><b><span style="COLOR: rgb(45,77,94)">NICK CATON, E.I.T.</span></b><b><span style="COLOR: rgb(45,77,94); FONT-SIZE: 12pt"></span></b></p>
<p class="MsoNormal"><span style="COLOR: rgb(204,153,0); FONT-SIZE: 7.5pt">PROJECT ENGINEER</span><span style="FONT-FAMILY: &#39;Times New Roman&#39;,&#39;serif&#39;; COLOR: rgb(204,153,0); FONT-SIZE: 7.5pt"></span></p>
<p class="MsoNormal"><span style="COLOR: rgb(45,77,94); FONT-SIZE: 10pt">25501 west valley parkway</span></p>
<p class="MsoNormal"><span style="COLOR: rgb(45,77,94); FONT-SIZE: 10pt">olathe ks 66061</span></p>
<p class="MsoNormal"><span style="COLOR: rgb(45,77,94); FONT-SIZE: 10pt">direct 913 344.0036</span></p>
<p class="MsoNormal"><span style="COLOR: rgb(45,77,94); FONT-SIZE: 10pt">fax 913 345.0617</span></p>
<p class="MsoNormal"><i><span style="COLOR: rgb(45,77,94); FONT-SIZE: 10pt">Check out our new web-site @ </span></i><span style="COLOR: rgb(31,73,125)"><a title="blocked::www.smithboucher.com" href="http://www.smithboucher.com/" target="_blank"><span style="FONT-SIZE: 10pt">www.smithboucher.com</span></a></span><u><span style="COLOR: blue; FONT-SIZE: 10pt"> </span></u><span style="COLOR: rgb(31,73,125)"></span></p>
</div>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125)"> </span></p>
<div>
<div style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">From:</span></b><span style="FONT-SIZE: 10pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Alex Krickx<br>
<b>Sent:</b> Monday, March 08, 2010 6:05 PM<br><b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] Modeling Infiltration and Windows</span></p>
</div></div>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Hello all,</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">I am interested in modeling the energy savings that occurs when windows are replaced with lower-infiltration alternatives. In the wizard mode, the only place that I see infiltration is under the “Building Envelope Constructions”  Screen. </p>

<p class="MsoNormal"> </p>
<p class="MsoNormal">I’m hoping someone can confirm my methodology:</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Can I input a weighted average of window and wall air infiltration here?  If I’m looking at a building with 20% Window to Wall Ratio, and the windows have 0.1 CFM/ft² while the walls have 0.04 CFM/ft²can I apply an area weighted average into this box? I would take (20%*0.1+80%*0.04) as the <i>façade </i>infiltration value.</p>

<p class="MsoNormal"> </p>
<p class="MsoNormal">That way I could use the same formula to determine the area weighted infiltration of the façade if better windows were installed.</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">How do other people model this?</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Thanks in advance!</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Alex Krickx</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><span style="COLOR: rgb(38,47,19); FONT-SIZE: 12pt">Alex Krickx</span></p>
<p class="MsoNormal"><span style="COLOR: gray; FONT-SIZE: 9pt">Building Energy Specialist</span></p>
<p class="MsoNormal"><span style="COLOR: rgb(31,73,125); FONT-SIZE: 8pt"><img border="0" alt="email_sig" width="121" height="42"></span></p>
<p class="MsoNormal"><span style="FONT-SIZE: 9pt">1250 Elko Dr, Sunnyvale, CA 94089</span></p>
<p class="MsoNormal"><span style="FONT-SIZE: 9pt">(t) 408.541.8124</span></p>
<p class="MsoNormal"><span style="COLOR: gray; FONT-SIZE: 9pt"> </span></p>
<p class="MsoNormal"><b><i><span style="FONT-SIZE: 7.5pt">Warning:</span></i></b><i><span style="FONT-SIZE: 7.5pt"> The information contained in this e-mail may be privileged attorney-client communications or attorney work product and/or proprietary and confidential.  If the reader of this message is not the intended recipient then you have received it in error and any review, distribution or copying of this message is prohibited and you are to notify us immediately by reply e-mail and delete the original message immediately.</span></i></p>

<p class="MsoNormal"> </p>
<p class="MsoNormal"> </p></div></div><br></div></div>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><font color="#888888"><br>
<br clear="all"><br>-- <br>Steve Clark, MS PhD RESNET BPI ITC<br>ClarkEnergyConsultants.com<br>484.477.7525<br><br><br></font><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>