<div>Hi Umesh,</div>
<div> </div>
<div>thanks for your attention to my issue.  Unfortunately because this is a baseline case I can only put in pre-heat if my proposed design has it, and my case does not.  What I thought was interesting in my case was that the preheat & baseboard inputs were showing heating energy consumption, but the AHU & HW coil was not showing any heating energy---I have know learned that because I didn't have the T-stat schedule input this was not offering the "call for heating" that the AHU was looking for.</div>

<div> </div>
<div>At some point when I switched my project from Wizard to DDedit mode (& changed my HVAC system type from chosen in the Wiz) so I went through the input spreadsheet and "reset" the inputs back to default since I had changed from an initial FC system selected in the wizard.  I didn't realize that by "re-setting" the t-stat schedules they didn't default to a common schedule, they just defaulted to nothing---so nothing was what I got.</div>

<div> </div>
<div>this is a great simulation community and resource where we can all support and help each other learn and learn from others' trials & troubles.  keep the communication flowing...</div>
<div> </div>
<div>Pasha<br><br></div>
<div class="gmail_quote">On Wed, Mar 3, 2010 at 12:22 PM, Umesh Atre <span dir="ltr"><<a href="mailto:umesh@innovativedesign.net">umesh@innovativedesign.net</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div>
<div><font color="#0000ff" size="2" face="Arial"></font> </div>
<div><font color="#0000ff" face="Calibri"><span>Pasha,</span></font></div>
<div><font color="#0000ff" face="Calibri"><span>I tried running your model as-is, and came up with a bunch of warnings re low preheat/heating capacities. </span></font><font color="#0000ff" face="Calibri"><span>I added preheat</span></font></div>

<div><font color="#0000ff" face="Calibri"><span>along with some humidity control for all the zones, and got the attached output.</span></font><font color="#0000ff" face="Calibri"><span> </span></font></div>
<div><font color="#0000ff" face="Calibri"><span>Maybe the program was just not doing the heating voluntarily, and had to be forced to.</span></font></div>
<div><font color="#0000ff" face="Calibri"><span>Hope this helps,</span></font></div>
<div><font color="#0000ff" face="Calibri"><span>Umesh</span></font></div>
<div><font color="#0000ff" size="2" face="Arial"></font> </div>
<div><font color="#0000ff" size="2" face="Arial"></font> </div><br>
<div dir="ltr" lang="en-us" align="left">
<hr>
<font size="2" face="Tahoma">
<div class="im"><b>From:</b> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Pasha Korber-Gonzalez<br>
</div>
<div class="im"><b>Sent:</b> Wednesday, March 03, 2010 1:05 PM<br><b>To:</b> James Hansen<br></div>
<div>
<div></div>
<div class="h5"><b>Cc:</b> eQUEST Users List<br><b>Subject:</b> Re: [Equest-users] No heating load to systems<br></div></div></font><br></div>
<div>
<div></div>
<div class="h5">
<div></div>
<div>Thanks James.   I do have an additional HW loop pump...but I will take a look at the thermostat schedule stuff.</div>
<div> </div>
<div>Pasha<br><br></div>
<div class="gmail_quote">On Wed, Mar 3, 2010 at 11:01 AM, James Hansen <span dir="ltr"><<a href="mailto:JHANSEN@ghtltd.com" target="_blank">JHANSEN@ghtltd.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-US" vlink="purple" link="blue">
<div>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt">You might need to add a hot water loop pump instead of just relying on a boiler pump.  See if that affects your heating energy consumption.</span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt"></span> </p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt">Also, your zones don’t appear to have any thermostat schedules configured.</span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt"></span> </p>
<p class="MsoNormal"><b><span style="COLOR: teal; FONT-SIZE: 11pt">GHT Limited<br></span></b><b><span style="FONT-SIZE: 11pt"><span style="COLOR: black">James Hansen</span></span></b><b><span style="COLOR: black; FONT-SIZE: 11pt">, PE, LEED AP</span></b></p>

<p class="MsoNormal"><b><span style="COLOR: black; FONT-SIZE: 10pt">Senior Associate</span></b><b><span style="COLOR: black; FONT-SIZE: 11pt"></span></b></p>
<p class="MsoNormal"><span style="FONT-SIZE: 7.5pt"><span style="COLOR: black">1010 N. Glebe Rd, Suite 200</span></span><span style="COLOR: #1f497d; FONT-SIZE: 11pt"></span></p>
<p class="MsoNormal"><span style="FONT-SIZE: 7.5pt"><span style="COLOR: black">Arlington</span><span style="COLOR: black">, </span><span style="COLOR: black">VA</span><span style="COLOR: black">  </span><span style="COLOR: black">22201-4749</span></span><span style="COLOR: black; FONT-SIZE: 11pt"></span></p>

<p class="MsoNormal"><span style="COLOR: black; FONT-SIZE: 7.5pt">703-338-5754 (Cell)</span><span style="COLOR: black; FONT-SIZE: 11pt"></span></p>
<p class="MsoNormal"><span style="COLOR: black; FONT-SIZE: 7.5pt">703-243-1200 (Office)</span><span style="COLOR: black; FONT-SIZE: 11pt"></span></p>
<p class="MsoNormal"><span style="COLOR: black; FONT-SIZE: 7.5pt">703-276-1376 (Fax)</span><span style="COLOR: black; FONT-SIZE: 11pt"></span></p>
<p class="MsoNormal"><span style="COLOR: teal; FONT-SIZE: 11pt"><a href="http://www.ghtltd.com/" target="_blank"><span style="FONT-SIZE: 10pt">www.ghtltd.com</span></a></span></p>
<p class="MsoNormal"><b><span style="COLOR: #31849b; FONT-SIZE: 11pt"></span></b> </p>
<p class="MsoNormal"><span style="COLOR: #1f497d; FONT-SIZE: 11pt"></span> </p>
<div style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">From:</span></b><span style="FONT-SIZE: 10pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Pasha Korber-Gonzalez<br>
<b>Sent:</b> Wednesday, March 03, 2010 12:45 PM<br><b>To:</b> John Aulbach<br><b>Cc:</b> eQUEST Users List<br><b>Subject:</b> Re: [Equest-users] No heating load to systems</span></p></div>
<div>
<div></div>
<div>
<p class="MsoNormal"> </p>
<div>
<p class="MsoNormal">Thanks John--I hadn't input the reheat delta t, thinking that it was one of those "blank" default auto-calc things....  so by inputting a 30 deg delta, that took away the error in the bdl file, but the results are still not showing any space heating consumption and yet somehow I have 0.0 hours out of throttling range---I thought this had to be too good to be true.</p>
</div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal">I've attached the current .pd2 & .inp files I am running.  If you do have time to take a quick peak at my inputs...this baseline file is  based on Appendix G compliance.  please note my system names do not match the system selection I have for baseline case.</p>
</div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal">Thanks for your time and attention to give me a hand.</p></div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p style="MARGIN-BOTTOM: 12pt" class="MsoNormal">Pasha</p></div>
<div>
<p class="MsoNormal">On Wed, Mar 3, 2010 at 10:32 AM, John Aulbach <<a href="mailto:jra_sac@yahoo.com" target="_blank">jra_sac@yahoo.com</a>> wrote:</p>
<div>
<div>
<div>
<p class="MsoNormal">Pasha:</p></div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal">Have you specified your Reheat-Delta-T for your zone VAV boxes? Send the .INP and .PD2 if you require further help.</p></div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><a name="1272571c49207aab_12725306a9705bfe_12725166779e50b7__MailAutoSig"><span style="COLOR: #1f497d">John R. Aulbach, PE, CEM</span></a></p>
<p class="MsoNormal"><span style="COLOR: #1f497d">Senior Energy Engineer</span></p>
<div>
<div class="MsoNormal"><span style="COLOR: #17365d">
<hr style="COLOR: #17365d" align="left" size="2" width="100%" noshade>
</span></div></div>
<p class="MsoNormal"><b><span style="FONT-VARIANT: small-caps; COLOR: navy">Partner</span></b><b><span style="FONT-VARIANT: small-caps; COLOR: green"> </span></b><b><span style="FONT-VARIANT: small-caps; COLOR: #006600">Energy</span></b></p>

<p class="MsoNormal"><span style="COLOR: #1f497d">1990 E. Grand Avenue, El Segundo, CA 90245<br>W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745</span></p>
<p class="MsoNormal"><a href="http://www.ptrenergy.com/" target="_blank"><span>www.ptrenergy.com</span></a><span style="COLOR: #1f497d"> </span><a href="mailto:%7C%20jaulbach@ptrenergy.com" target="_blank"><span>| jaulbach@ptrenergy.com</span></a></p>

<p class="MsoNormal"><span></span> </p></div>
<div>
<p class="MsoNormal"> </p>
<div>
<div style="TEXT-ALIGN: center" class="MsoNormal" align="center"><span style="FONT-SIZE: 10pt">
<hr align="center" size="1" width="100%">
</span></div>
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">From:</span></b><span style="FONT-SIZE: 10pt"> Pasha Korber-Gonzalez <<a href="mailto:pasha.pkconsulting@gmail.com" target="_blank">pasha.pkconsulting@gmail.com</a>><br>
<b>To:</b> eQUEST Users List <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>><br><b>Sent:</b> Wed, March 3, 2010 9:28:30 AM<br><b>Subject:</b> [Equest-users] No heating load to systems</span></p>

<div>
<div>
<p class="MsoNormal"> </p>
<div>
<p class="MsoNormal">Hi all,</p></div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal">I thought I was wrapping up my baseline model and then for some reason I discovered that the only heating energy being used is going through the zone baseboards.  When I take out the baseboards, the results show a big fat ZERO for any space heating energy the DOE2 error shows below.  How can the design loads not get passed to the system.  The baseline systems are VAV with reheat, but for some reason there is no heat or reheat unless I specify pre-heat (which there is none) or baseboards...  any ideas are appreciated--because I thought I was closer to finished with this model until this issue popped up.</p>
</div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p><span style="FONT-FAMILY: 'Courier New'; FONT-SIZE: 7.5pt">***ERROR***********************************************************************</span></p>
<p><span style="FONT-FAMILY: 'Courier New'; FONT-SIZE: 7.5pt">Loop: Hot Water Loop has zero design flow.</span></p>
<p><span style="FONT-FAMILY: 'Courier New'; FONT-SIZE: 7.5pt">Check input for consistency, or specify design loads.</span></p></div></div></div></div></div></div>
<p class="MsoNormal"> </p></div></div>
<p class="MsoNormal"> </p></div></div></div></div>
<p align="left"><font size="2"><font face="Tahoma"><font color="#0000ff">
<hr>
</font></font><font color="#0000ff"><font color="#000000"><font face="Arial">The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to </font><a href="mailto:ght@ghtltd.com" target="_blank"><font face="Arial">ght@ghtltd.com</font></a><font face="Arial">, and destroy this communication and all copies thereof, including all attachments.  Thank you.</font></font><font color="#000000" face="Tahoma"></font></font></font> 
<p></p>
<p></p>
<p></p></p></blockquote></div><br></div></div></div></blockquote></div><br>