<div>Hi Vik--Yes, per James suggestion I have added both these schedules and am now seeing better results without errors--so I am backing up with both my model files to make these adjustments.</div>
<div> </div>
<div>I guess I took for granted that all "default" input boxes even when they are left blank still defaulted to a baseline input...</div>
<div> </div>
<div>Thank you to all of you for taking time out of your busy project schedules to give me some support---it's not soo lonely in this simulation world.</div>
<div> </div>
<div>Cheers,</div>
<div>Pasha<br><br></div>
<div class="gmail_quote">On Wed, Mar 3, 2010 at 11:31 AM, Vikram Sami <span dir="ltr"><<a href="mailto:VSami@lasarchitect.com">VSami@lasarchitect.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-US" vlink="purple" link="blue">
<div>
<p class="MsoNormal"><span style="COLOR: #0000b4; FONT-SIZE: 11pt">Pasha,</span></p>
<p class="MsoNormal"><span style="COLOR: #0000b4; FONT-SIZE: 11pt">I suspect this might be because there is no space heating schedule. </span></p>
<p class="MsoNormal"><span style="COLOR: #0000b4; FONT-SIZE: 11pt"> </span></p>
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">HEAT-TEMP-SCH</span></b></p>
<p class="MsoNormal">Takes the U-name of a schedule of TYPE = TEMPERATURE that gives the heating setpoint of the zone thermostat. <b><u>If not specified, the program will assume that the zone has no zone-activated heating control. </u></b>If omitted, no heating in zone. For constant volume DDS, MZS, and PMZS systems this schedule provides the value of the lower end of the heating/cooling throttling range; the COOL-TEMP-SCH provides the value of the upper limit of the range</p>

<p class="MsoNormal"><span style="COLOR: #0000b4; FONT-SIZE: 11pt"> </span></p>
<p class="MsoNormal"><span style="COLOR: #0000b4; FONT-SIZE: 11pt"> </span></p>
<p class="MsoNormal"><span style="COLOR: #0000b4; FONT-SIZE: 11pt">If you assign a heating schedule to the spaces you will get your space heating loads.</span></p>
<p class="MsoNormal"><span style="COLOR: #0000b4; FONT-SIZE: 11pt"> </span></p>
<p class="MsoNormal"><span style="COLOR: #0000b4; FONT-SIZE: 11pt">I would have thought that you wouldn’t have much of a cooling load either because you don’t have that defined either. </span></p>
<p class="MsoNormal"><span style="COLOR: #0000b4; FONT-SIZE: 11pt"> </span></p>
<p class="MsoNormal"><b><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: black">Vikram Sami,</span></b><span style="COLOR: #0000b4"> </span><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: black">LEED AP</span><span style="COLOR: #0000b4"> <br>
</span><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: black">Direct Phone 404-253-1466 | Direct Fax 404-253-1366</span><span style="COLOR: #0000b4"> </span></p>
<p class="MsoNormal"><b><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: maroon">L</span></b><b><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: maroon; FONT-SIZE: 10pt">ORD</span></b><b><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: maroon">, A</span></b><b><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: maroon; FONT-SIZE: 10pt">ECK</span></b><b><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: maroon"> & S</span></b><b><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: maroon; FONT-SIZE: 10pt">ARGENT</span></b><b><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: maroon"> A</span></b><b><span style="FONT-FAMILY: 'Garamond','serif'; COLOR: maroon; FONT-SIZE: 10pt">RCHITECTURE</span></b><b><span style="COLOR: #0000b4"><br>
<br></span></b><span style="COLOR: #0000b4"></span></p>
<p class="MsoNormal"><span style="COLOR: #0000b4; FONT-SIZE: 11pt"> </span></p>
<div style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">From:</span></b><span style="FONT-SIZE: 10pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Pasha Korber-Gonzalez 
<div class="im"><br><b>Sent:</b> Wednesday, March 03, 2010 12:45 PM<br><b>To:</b> John Aulbach<br><b>Cc:</b> eQUEST Users List<br></div><b>Subject:</b> Re: [Equest-users] No heating load to systems</span> 
<p></p></p></div>
<div>
<div></div>
<div class="h5">
<p class="MsoNormal"> </p>
<div>
<p class="MsoNormal">Thanks John--I hadn't input the reheat delta t, thinking that it was one of those "blank" default auto-calc things....  so by inputting a 30 deg delta, that took away the error in the bdl file, but the results are still not showing any space heating consumption and yet somehow I have 0.0 hours out of throttling range---I thought this had to be too good to be true.</p>
</div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal">I've attached the current .pd2 & .inp files I am running.  If you do have time to take a quick peak at my inputs...this baseline file is  based on Appendix G compliance.  please note my system names do not match the system selection I have for baseline case.</p>
</div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal">Thanks for your time and attention to give me a hand.</p></div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p style="MARGIN-BOTTOM: 12pt" class="MsoNormal">Pasha</p></div>
<div>
<p class="MsoNormal">On Wed, Mar 3, 2010 at 10:32 AM, John Aulbach <<a href="mailto:jra_sac@yahoo.com" target="_blank">jra_sac@yahoo.com</a>> wrote:</p>
<div>
<div>
<div>
<p class="MsoNormal">Pasha:</p></div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal">Have you specified your Reheat-Delta-T for your zone VAV boxes? Send the .INP and .PD2 if you require further help.</p></div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><a name="127254cc679bd9c5_12725166779e50b7__MailAutoSig"><span style="COLOR: #1f497d">John R. Aulbach, PE, CEM</span></a></p>
<p class="MsoNormal"><span style="COLOR: #1f497d">Senior Energy Engineer</span></p>
<div>
<div class="MsoNormal"><span style="COLOR: #17365d">
<hr style="COLOR: #17365d" align="left" size="2" width="30%" noshade>
</span></div></div>
<p class="MsoNormal"><b><span style="FONT-VARIANT: small-caps; COLOR: navy">Partner</span></b><b><span style="FONT-VARIANT: small-caps; COLOR: green"> </span></b><b><span style="FONT-VARIANT: small-caps; COLOR: #006600">Energy</span></b></p>

<p class="MsoNormal"><span style="COLOR: #1f497d">1990 E. Grand Avenue, El Segundo, CA 90245<br>W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745</span></p>
<p class="MsoNormal"><a href="http://www.ptrenergy.com/" target="_blank"><span>www.ptrenergy.com</span></a><span style="COLOR: #1f497d"> </span><a href="mailto:%7C%20jaulbach@ptrenergy.com" target="_blank"><span>| jaulbach@ptrenergy.com</span></a></p>

<p class="MsoNormal"><span> </span></p></div>
<div>
<p class="MsoNormal"> </p>
<div>
<div style="TEXT-ALIGN: center" class="MsoNormal" align="center"><span style="FONT-SIZE: 10pt">
<hr align="center" size="1" width="100%">
</span></div>
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">From:</span></b><span style="FONT-SIZE: 10pt"> Pasha Korber-Gonzalez <<a href="mailto:pasha.pkconsulting@gmail.com" target="_blank">pasha.pkconsulting@gmail.com</a>><br>
<b>To:</b> eQUEST Users List <<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>><br><b>Sent:</b> Wed, March 3, 2010 9:28:30 AM<br><b>Subject:</b> [Equest-users] No heating load to systems</span></p>

<div>
<div>
<p class="MsoNormal"> </p>
<div>
<p class="MsoNormal">Hi all,</p></div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p class="MsoNormal">I thought I was wrapping up my baseline model and then for some reason I discovered that the only heating energy being used is going through the zone baseboards.  When I take out the baseboards, the results show a big fat ZERO for any space heating energy the DOE2 error shows below.  How can the design loads not get passed to the system.  The baseline systems are VAV with reheat, but for some reason there is no heat or reheat unless I specify pre-heat (which there is none) or baseboards...  any ideas are appreciated--because I thought I was closer to finished with this model until this issue popped up.</p>
</div>
<div>
<p class="MsoNormal"> </p></div>
<div>
<p><span style="FONT-FAMILY: 'Courier New'; FONT-SIZE: 7.5pt">***ERROR***********************************************************************</span></p>
<p><span style="FONT-FAMILY: 'Courier New'; FONT-SIZE: 7.5pt">Loop: Hot Water Loop has zero design flow.</span></p>
<p><span style="FONT-FAMILY: 'Courier New'; FONT-SIZE: 7.5pt">Check input for consistency, or specify design loads.</span></p></div></div></div></div></div></div>
<p class="MsoNormal"> </p></div></div>
<p class="MsoNormal"> </p></div></div></div></div></blockquote></div><br>