class=935515714-03032010>Kevin,</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN 
class=935515714-03032010></SPAN></FONT>&nbsp;</DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN class=935515714-03032010>Assuming 
your two story space has the same footprint across floors, please see attached 
screenshots.</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN class=935515714-03032010>You can 
locate the screen under Building Footprint &gt; Zone 
Characteristics.</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN class=935515714-03032010>You could 
define it as a 'multi-level space' on the lower floor, and as a 'multi-level 
space' and 'open to below'</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN class=935515714-03032010>for the 
upper floor. The multi-level space can be defined as conditioned or 
unconditioned per your design.</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN class=935515714-03032010>Hope this 
helps,</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN 
class=935515714-03032010>Umesh</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT>&nbsp;</DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT>&nbsp;</DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT>&nbsp;</DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> equest-users-bounces@lists.onebuilding.org 
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Supriya 
Goel<BR><B>Sent:</B> Wednesday, March 03, 2010 1:26 AM<BR><B>To:</B> Edward 
Kucirek<BR><B>Cc:</B> equest-users@lists.onebuilding.org<BR><B>Subject:</B> Re: 
[Equest-users] Zoning Layouts<BR></FONT><BR></DIV>
<DIV></DIV>Hi Edward,
<DIV><BR></DIV>
<DIV>What I had done in a similar situation was- create 
2&nbsp;different&nbsp;zones in the wizard, and in the detail edit mode, assign 
that specific space to the zone of the other floor, and then I deleted the other 
zone (as it had no space&nbsp;assigned&nbsp;to it). I guess this would be right 
way to do it, but I am not completely sure.</DIV>
<DIV><BR></DIV>
<DIV>Hopefully this helps :)</DIV>
<DIV><BR></DIV>
<DIV>Regards</DIV>
<DIV>Supriya<BR><BR>
<DIV class=gmail_quote>On Tue, Mar 2, 2010 at 2:19 PM, Edward Kucirek <SPAN 
dir=ltr>&lt;<A 
href="mailto:kucirekengineering@hotmail.com">kucirekengineering@hotmail.com</A>&gt;</SPAN> 
wrote:<BR>
<BLOCKQUOTE class=gmail_quote 
style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">
  <DIV>I am modeling a building with different zoning on the first and second 
  floor. I know I can accomplish this with 2 different shells but I also have a 
  space that is two stories tall (similar to an atrium). Has anyone encountered 
  this? Any help would be much appreciated.<BR><BR>Kevin<BR><BR><FONT 
  style="FONT-SIZE: 10pt" face=Arial size=2>K</FONT>ucirek <FONT 
  style="FONT-SIZE: 10pt" face=Verdana size=2>E</FONT>ngineering, <FONT 
  style="FONT-SIZE: 10pt" face=Verdana size=2>I</FONT>nc.<BR>7587 Main 
  St.<BR>Omaha, NE 68127<BR>Ph: (402)951-0022<BR>Fax: (402)951-0023<BR><A 
  href="mailto:kucirekengineering@hotmail.com" 
  target=_blank>kucirekengineering@hotmail.com</A><BR>
  <DIV class=hm><BR><BR><BR>
  <HR>
  Hotmail: Free, trusted and rich email service. <A 
  href="http://clk.atdmt.com/GBL/go/201469228/direct/01/" target=_blank>Get it 
  now.</A></DIV></DIV><BR>_______________________________________________<BR>Equest-users 
  mailing list<BR><A 
  href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" 
  target=_blank>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</A><BR>To 
  unsubscribe from this mailing list send &nbsp;a blank message to <A 
  href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR><BR></BLOCKQUOTE></DIV><BR><BR 
clear=all><BR>-- <BR>Graduate Student, MSBE<BR>School of Architecture and 
Landscape Architecture<BR>Arizona State University, 
Tempe<BR><BR><BR><BR></DIV></BODY></HTML>