class=310090919-03032010>Pasha,</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN class=310090919-03032010>I tried 
running your model as-is, and came up with a bunch of warnings re low 
preheat/heating capacities.&nbsp;</SPAN></FONT><FONT face=Calibri 
color=#0000ff><SPAN class=310090919-03032010>I added preheat</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN class=310090919-03032010>along with 
some humidity control for all the zones, and got the attached 
output.</SPAN></FONT><FONT face=Calibri color=#0000ff><SPAN 
class=310090919-03032010>&nbsp;</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN class=310090919-03032010>Maybe the 
program was just not doing the heating voluntarily, and had to be forced 
to.</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN class=310090919-03032010>Hope this 
helps,</SPAN></FONT></DIV>
<DIV><FONT face=Calibri color=#0000ff><SPAN 
class=310090919-03032010>Umesh</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT>&nbsp;</DIV>
<DIV><FONT face=Arial color=#0000ff size=2></FONT>&nbsp;</DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> equest-users-bounces@lists.onebuilding.org 
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Pasha 
Korber-Gonzalez<BR><B>Sent:</B> Wednesday, March 03, 2010 1:05 PM<BR><B>To:</B> 
James Hansen<BR><B>Cc:</B> eQUEST Users List<BR><B>Subject:</B> Re: 
[Equest-users] No heating load to systems<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV>Thanks James.&nbsp;&nbsp; I do have an additional HW loop pump...but I will 
take a look at the thermostat schedule stuff.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Pasha<BR><BR></DIV>
<DIV class=gmail_quote>On Wed, Mar 3, 2010 at 11:01 AM, James Hansen <SPAN 
dir=ltr>&lt;<A 
href="mailto:JHANSEN@ghtltd.com">JHANSEN@ghtltd.com</A>&gt;</SPAN> wrote:<BR>
<BLOCKQUOTE class=gmail_quote 
style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">
  <DIV lang=EN-US link="blue" vlink="purple">
  <DIV>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d">You might 
  need to add a hot water loop pump instead of just relying on a boiler 
  pump.&nbsp; See if that affects your heating energy consumption.</SPAN></P>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d"></SPAN>&nbsp;</P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: #1f497d">Also, your 
  zones don&#8217;t appear to have any thermostat schedules configured.</SPAN></P>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d"></SPAN>&nbsp;</P>
  <P class=MsoNormal><B><SPAN style="FONT-SIZE: 11pt; COLOR: teal">GHT 
  Limited<BR></SPAN></B><B><SPAN style="FONT-SIZE: 11pt"><SPAN 
  style="COLOR: black">James Hansen</SPAN></SPAN></B><B><SPAN 
  style="FONT-SIZE: 11pt; COLOR: black">, PE, LEED AP</SPAN></B></P>
  <P class=MsoNormal><B><SPAN style="FONT-SIZE: 10pt; COLOR: black">Senior 
  Associate</SPAN></B><B><SPAN 
  style="FONT-SIZE: 11pt; COLOR: black"></SPAN></B></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt"><SPAN 
  style="COLOR: black">1010 N. Glebe Rd, Suite 200</SPAN></SPAN><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d"></SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt"><SPAN 
  style="COLOR: black">Arlington</SPAN><SPAN style="COLOR: black">, </SPAN><SPAN 
  style="COLOR: black">VA</SPAN><SPAN style="COLOR: black">&nbsp; </SPAN><SPAN 
  style="COLOR: black">22201-4749</SPAN></SPAN><SPAN 
  style="FONT-SIZE: 11pt; COLOR: black"></SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt; COLOR: black">703-338-5754 
  (Cell)</SPAN><SPAN style="FONT-SIZE: 11pt; COLOR: black"></SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt; COLOR: black">703-243-1200 
  (Office)</SPAN><SPAN style="FONT-SIZE: 11pt; COLOR: black"></SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 7.5pt; COLOR: black">703-276-1376 
  (Fax)</SPAN><SPAN style="FONT-SIZE: 11pt; COLOR: black"></SPAN></P>
  <P class=MsoNormal><SPAN style="FONT-SIZE: 11pt; COLOR: teal"><A 
  href="http://www.ghtltd.com/" target=_blank><SPAN 
  style="FONT-SIZE: 10pt">www.ghtltd.com</SPAN></A></SPAN></P>
  <P class=MsoNormal><B><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #31849b"></SPAN></B>&nbsp;</P>
  <P class=MsoNormal><SPAN 
  style="FONT-SIZE: 11pt; COLOR: #1f497d"></SPAN>&nbsp;</P>
  <DIV 
  style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; PADDING-LEFT: 0in; PADDING-BOTTOM: 0in; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
  <P class=MsoNormal><B><SPAN style="FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
  style="FONT-SIZE: 10pt"> <A 
  href="mailto:equest-users-bounces@lists.onebuilding.org" 
  target=_blank>equest-users-bounces@lists.onebuilding.org</A> [mailto:<A 
  href="mailto:equest-users-bounces@lists.onebuilding.org" 
  target=_blank>equest-users-bounces@lists.onebuilding.org</A>] <B>On Behalf Of 
  </B>Pasha Korber-Gonzalez<BR><B>Sent:</B> Wednesday, March 03, 2010 12:45 
  PM<BR><B>To:</B> John Aulbach<BR><B>Cc:</B> eQUEST Users 
  List<BR><B>Subject:</B> Re: [Equest-users] No heating load to 
  systems</SPAN></P></DIV>
  <DIV>
  <DIV></DIV>
  <DIV class=h5>
  <P class=MsoNormal>&nbsp;</P>
  <DIV>
  <P class=MsoNormal>Thanks John--I hadn't input the reheat delta t, thinking 
  that it was one of those "blank" default auto-calc things....&nbsp; so by 
  inputting a 30 deg delta, that took away the error in the bdl file, but the 
  results are still not showing any space heating consumption and yet somehow I 
  have 0.0 hours out of throttling range---I thought this had to be too good to 
  be true.</P></DIV>
  <DIV>
  <P class=MsoNormal>&nbsp;</P></DIV>
  <DIV>
  <P class=MsoNormal>I've attached the current .pd2 &amp; .inp files I am 
  running.&nbsp; If you do have time to take a quick peak at my inputs...this 
  baseline file is&nbsp; based on Appendix G compliance.&nbsp; please note my 
  system names do not match the system selection&nbsp;I have for baseline 
  case.</P></DIV>
  <DIV>
  <P class=MsoNormal>&nbsp;</P></DIV>
  <DIV>
  <P class=MsoNormal>Thanks for your time and attention to give me a 
  hand.</P></DIV>
  <DIV>
  <P class=MsoNormal>&nbsp;</P></DIV>
  <DIV>
  <P class=MsoNormal style="MARGIN-BOTTOM: 12pt">Pasha</P></DIV>
  <DIV>
  <P class=MsoNormal>On Wed, Mar 3, 2010 at 10:32 AM, John Aulbach &lt;<A 
  href="mailto:jra_sac@yahoo.com" target=_blank>jra_sac@yahoo.com</A>&gt; 
  wrote:</P>
  <DIV>
  <DIV>
  <DIV>
  <P class=MsoNormal>Pasha:</P></DIV>
  <DIV>
  <P class=MsoNormal>&nbsp;</P></DIV>
  <DIV>
  <P class=MsoNormal>Have you specified your Reheat-Delta-T for your zone VAV 
  boxes? Send the .INP and .PD2 if you require further help.</P></DIV>
  <DIV>
  <P class=MsoNormal>&nbsp;</P></DIV>
  <DIV>
  <P class=MsoNormal>&nbsp;</P>
  <P class=MsoNormal><A 
  name=12725306a9705bfe_12725166779e50b7__MailAutoSig><SPAN 
  style="COLOR: #1f497d">John R. Aulbach, PE, CEM</SPAN></A></P>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d">Senior Energy 
  Engineer</SPAN></P>
  <DIV>
  <DIV class=MsoNormal><SPAN style="COLOR: #17365d">
  <HR style="COLOR: #17365d" align=left width="100%" noShade SIZE=2>
  </SPAN></DIV></DIV>
  <P class=MsoNormal><B><SPAN 
  style="COLOR: navy; FONT-VARIANT: small-caps">Partner</SPAN></B><B><SPAN 
  style="COLOR: green; FONT-VARIANT: small-caps"> </SPAN></B><B><SPAN 
  style="COLOR: #006600; FONT-VARIANT: small-caps">Energy</SPAN></B></P>
  <P class=MsoNormal><SPAN style="COLOR: #1f497d">1990 E. Grand Avenue, El 
  Segundo, CA 90245<BR>W: 888-826-1216, X254| D: 310-765-7295 | F: 
  310-817-2745</SPAN></P>
  <P class=MsoNormal><A href="http://www.ptrenergy.com/" 
  target=_blank><SPAN>www.ptrenergy.com</SPAN></A><SPAN style="COLOR: #1f497d"> 
  </SPAN><A href="mailto:%7C%20jaulbach@ptrenergy.com" target=_blank><SPAN>| 
  jaulbach@ptrenergy.com</SPAN></A></P>
  <P class=MsoNormal><SPAN></SPAN>&nbsp;</P></DIV>
  <DIV>
  <P class=MsoNormal>&nbsp;</P>
  <DIV>
  <DIV class=MsoNormal style="TEXT-ALIGN: center" align=center><SPAN 
  style="FONT-SIZE: 10pt">
  <HR align=center width="100%" SIZE=1>
  </SPAN></DIV>
  <P class=MsoNormal><B><SPAN style="FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
  style="FONT-SIZE: 10pt"> Pasha Korber-Gonzalez &lt;<A 
  href="mailto:pasha.pkconsulting@gmail.com" 
  target=_blank>pasha.pkconsulting@gmail.com</A>&gt;<BR><B>To:</B> eQUEST Users 
  List &lt;<A href="mailto:equest-users@lists.onebuilding.org" 
  target=_blank>equest-users@lists.onebuilding.org</A>&gt;<BR><B>Sent:</B> Wed, 
  March 3, 2010 9:28:30 AM<BR><B>Subject:</B> [Equest-users] No heating load to 
  systems</SPAN></P>
  <DIV>
  <DIV>
  <P class=MsoNormal>&nbsp;</P>
  <DIV>
  <P class=MsoNormal>Hi all,</P></DIV>
  <DIV>
  <P class=MsoNormal>&nbsp;</P></DIV>
  <DIV>
  <P class=MsoNormal>I thought I was wrapping up my baseline model and then for 
  some reason I discovered that the only heating energy being used is going 
  through the zone baseboards.&nbsp; When I take out the baseboards, the results 
  show a big fat ZERO for any space heating energy&nbsp;the DOE2 error shows 
  below.&nbsp; How can the design loads not get passed to the system.&nbsp; The 
  baseline systems are VAV with reheat, but for some reason there is no heat or 
  reheat unless I specify pre-heat (which there is none) or baseboards...&nbsp; 
  any ideas are appreciated--because I thought I was closer to finished with 
  this model until this issue popped up.</P></DIV>
  <DIV>
  <P class=MsoNormal>&nbsp;</P></DIV>
  <DIV>
  <P><SPAN 
  style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Courier New'">***ERROR***********************************************************************</SPAN></P>
  <P><SPAN style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Courier New'">Loop: Hot Water 
  Loop has zero design flow.</SPAN></P>
  <P><SPAN style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Courier New'">Check input for 
  consistency, or specify design 
  loads.</SPAN></P></DIV></DIV></DIV></DIV></DIV></DIV>
  <P class=MsoNormal>&nbsp;</P></DIV></DIV>
  <P class=MsoNormal>&nbsp;</P></DIV></DIV></DIV></DIV>
  <P align=left><FONT size=2><FONT face=Tahoma><FONT color=#0000ff>
  <HR>
  </FONT></FONT><FONT color=#0000ff><FONT color=#000000><FONT face=Arial>The 
  information contained in this communication is confidential, may be 
  privileged, and is intended only for the use of the addressee.&nbsp; It is the 
  property of GHT Limited.&nbsp; Unauthorized use, disclosure or copying of this 
  communication or any part thereof is strictly prohibited and may be 
  unlawful.&nbsp; If you have received this communication in error, please 
  notify me immediately by return e-mail or by e-mail to </FONT><A 
  href="mailto:ght@ghtltd.com" target=_blank><FONT 
  face=Arial>ght@ghtltd.com</FONT></A><FONT face=Arial>, and destroy this 
  communication and all copies thereof, including all attachments.&nbsp; Thank 
  you.</FONT></FONT><FONT face=Tahoma color=#000000></FONT></FONT></FONT> 
  <P></P>
  <P></P></BLOCKQUOTE></DIV><BR></BODY></HTML>