<P><FONT size=2>All,<BR><BR>I believe it is the RA temperature of the Dummy Zone
that is passed to the units with OA-From specified, so you are right John that
the RA would be too cold to return to an ERV, assuming your dummy space is
something around 55F.<BR><BR>I have spent many a late night trying to work
around this problem and can recommend the following approaches:<BR></FONT><FONT
size=2>1. Model any Energy Recovery as an exceptional calculation (in a separate
model) for LEED<BR>2. Incorporate the Energy Recovery into the FCUs or AHUs
(although you have to be really careful to properly account for your fan energy
and flow rates).<BR><BR>Regards,</FONT></P>
<P><FONT size=2><B><SPAN style="FONT-FAMILY: 'GillSans Light'"><SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt">Jonathan
M. Curtin, EIT, LEED</SPAN></B><SUP><SPAN
style="FONT-FAMILY: 'GillSans Light'">®</SPAN></SUP><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt">
AP</SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'"><BR></SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt"><SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'">Mechanical
Engineer</SPAN></B><STRONG><SPAN
style="FONT-FAMILY: 'GillSans Light'"><?xml:namespace prefix = o ns =
"urn:schemas-microsoft-com:office:office" /><o:p></o:p></SPAN></STRONG></P>
<DIV class=Section1>
<P class=MsoNormal><STRONG><SPAN style="FONT-FAMILY: 'GillSans Light'"><SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></STRONG><B><SPAN
style="FONT-FAMILY: 'GillSans Light'"><IMG height=159
src="cid:655395221@01032010-160A" width=240
v:shapes="_x0000_i1025"><STRONG><o:p></o:p></STRONG></SPAN></B></P></DIV>
<P>-----Original Message-----<BR>From:
equest-users-bounces@lists.onebuilding.org [<A
href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</A>]
On Behalf Of Grando, John<BR>Sent: Monday, March 01, 2010 03:08 PM<BR>To: James
Hansen; Marcus Eliason; equest-users@lists.onebuilding.org<BR>Subject: Re:
[Equest-users] eQuest - FCU with DOAS<BR><BR><BR>One further question that has
been bothering me. How would you set up ERV with the DOAS? I've seen
some posts from the archives but none are too clear. The return air
temperature of the DOAS appears to be too low to use an ERV on. Any
suggestions?<BR><BR><BR>John Grando LEED AP<BR><BR><BR>-----Original
Message-----<BR>From: James Hansen [<A
href="mailto:JHANSEN@ghtltd.com">mailto:JHANSEN@ghtltd.com</A>]<BR>Sent: Monday,
March 01, 2010 11:16 AM<BR>To: Marcus Eliason;
equest-users@lists.onebuilding.org<BR>Subject: Re: [Equest-users] eQuest - FCU
with DOAS<BR><BR>I haven't had a chance to look at your .inp file, but when you
are creating a DOAS system, make sure that you at least do the
following:<BR><BR>1) Make sure the fan schedule is forced off at night and
setback times.<BR>2) Make sure the throttling range for the dummy zone
thermostat is at least 4 degrees (I usually use 6).<BR>3) Make sure that the
heating/cooling schedules that the dummy zone follows are set to something like
120 degrees cooling and 20 degrees heating after hours, just to make sure that a
call for heating/cooling doesn't show up in your report, and mess up the unmet
load hours.<BR><BR><BR>Just looked at your file: you need to specify some
sort of minimum OA control or minimum air schedule for the FCUs (I think).
Right now nothing shows up.<BR><BR>Also, why is the DOAS system serving so many
"dummy" zones? I *think* your DOAS system is EL1 Sys1 (SZRH), yet it is
serving 20+ zones. I'm confused...<BR><BR>GHT Limited<BR>James Hansen, PE,
LEED AP<BR>Senior Associate<BR>1010 N. Glebe Rd, Suite 200<BR>Arlington,
VA 22201-4749<BR>703-338-5754 (Cell)<BR>703-243-1200
(Office)<BR>703-276-1376 (Fax)<BR>www.ghtltd.com<BR><BR><BR><BR>-----Original
Message-----<BR>From: equest-users-bounces@lists.onebuilding.org [<A
href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</A>]
On Behalf Of Marcus Eliason<BR>Sent: Monday, March 01, 2010 11:04 AM<BR>To:
equest-users@lists.onebuilding.org<BR>Subject: [Equest-users] eQuest - FCU with
DOAS<BR><BR><BR>Hello,<BR><BR>I am trying to model a building with FCUs and a
DOAS to deliver outdoor air to the individual zones. I have put in the
dummy zones for the DOAS system, modeled as a single air handler with chilled
and hot water coils. I have changed the walls of the dummy zone to air walls,
specified the DOAS to get OA flow as sum of all zones and for the FCUs to get OA
from the DOAS. When I run the model, I get a lot of unmet hours
corresponding to the dummy zones and the DOAS system. I have tried but
cannot seem to turn off the return air path for the DOAS (since it is 100% OA)
and have specified the minimum OA fraction for the DOAS as 1. I am not
sure if the unmet hours means that my DOAS is not adequately cooling the OA load
or if it something else.<BR>Also, my "pump & aux" energy in the model seems
very high for a building that only has 3 pumps. Can someone familiar with
modeling DOAS shed any light on what might be causing some of these
problems. I have attached the .inp and .pd2 files for
reference.<BR><BR>Thanks,<BR><BR>Marcus Eliason<BR><BR><BR><BR>The information
contained in this communication is confidential, may be privileged, and is
intended only for the use of the addressee. It is the property of GHT
Limited. Unauthorized use, disclosure or copying of this communication or
any part thereof is strictly prohibited and may be unlawful. If you have
received this communication in error, please notify me immediately by return
e-mail or by e-mail to ght@ghtltd.com, and destroy this communication and all
copies thereof, including all attachments. Thank
you.<BR><BR><BR><BR><BR><BR>NOTICE OF CONFIDENTIALITY<BR><BR>This E-mail message
and its attachments (if any) are intended solely for the use of the addressees
hereof. In addition, this message and the attachments (if any) may contain
information that is confidential, privileged and exempt from disclosure under
applicable law. If you are not the intended recipient of this message, you
are prohibited from reading, disclosing, reproducing, distributing,
disseminating or otherwise using this transmission. Delivery of this
message to any person other than the intended recipient is not intended to waive
any right or privilege. If you have received this message in error, please
promptly notify the sender by reply E-mail and immediately delete this message
from your
system.<BR><BR><BR>_______________________________________________<BR>Equest-users
mailing list<BR><A
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuildingorg</A><BR>To
unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR></FONT></P>
<!--qsdbegin-->
<DIV><SPAN class=469015015-07012009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=469015015-07012009>
<DIV class=MsoNormal style="MARGIN: 0in 0in 0pt; TEXT-ALIGN: center"
align=center>
<HR align=center width="100%" SIZE=2>
</DIV><FONT color=#000000><U><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">Legal
Disclaimer:</SPAN></U><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">
</SPAN><STRONG><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">The
information contained in this communication is confidential and is
</SPAN></STRONG><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">covered
by the Electronic Communications Privacy Act, 18 U.S.C. §§ 2510-2521; it
</SPAN><STRONG><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">may
be privileged and is intended for the exclusive use of the above named
addressee(s). If you are not the intended recipient(s), you are expressly
prohibited from copying, distributing, disseminating, or in any other way using
any of the information contained within this communication. If you have received
this communication in error, please contact the sender by telephone at
(713) 781-2526 or by response via email and permanently delete the original
email (including attachments) and any copies. </SPAN></STRONG><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">
<BR><BR><SPAN
style="FONT-SIZE: 6.5pt; COLOR: #007213; FONT-FAMILY: Arial">Please consider the
environment before printing this email.</SPAN></I></SPAN></FONT></SPAN><B><SPAN
style="FONT-SIZE: 11pt; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 12.0pt"> <SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></B><B><SPAN
<!--qsdend-->
<br></BODY></HTML>