<DIV>Thanks for your replies.</DIV>
<DIV>It helps us a lot.</DIV>
<DIV> </DIV>
<DIV>On the model that we're working on,</DIV>
<DIV>We already did what everyone suggested.</DIV>
<DIV>We modeled the canopy as fixed shading.</DIV>
<DIV> </DIV>
<DIV>To double check if the model is running as what we're expecting based on cooling load fundamentals,</DIV>
<DIV>We modeled full opaque canopy (0 transmittance) and 1.0 transmittance for comparison purposes only.</DIV>
<DIV> </DIV>
<DIV>After running the model, we had weird results:</DIV>
<DIV> </DIV>
<DIV>0 transmittance</DIV>
<DIV>Chilled Water - 104.05 MBTU</DIV>
<DIV>Space Heating - 74.8 kwh (X000)</DIV>
<DIV> </DIV>
<DIV>1.0 transmittance</DIV>
<DIV>Chilled Water - 109.9 MBTU</DIV>
<DIV>Space Heating - 96.2 kwh (X000)</DIV>
<DIV> </DIV>
<DIV>Am I modeling it wrong?</DIV>
<DIV>Am I missing something?</DIV>
<DIV>Are we having the same results especially with the heating consumption?</DIV>
<DIV>What are the areas that I should check first before concluding?</DIV>
<DIV>Note that we modeled the systems for both as AUTOSIZING.</DIV>
<DIV> </DIV>
<DIV>Thanks for your assistance.</DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV>Reniel</DIV>
<DIV><BR> </DIV>
<DIV style="FONT-FAMILY: arial, helvetica, sans-serif; FONT-SIZE: 10pt"><BR>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><FONT size=2 face=Tahoma>
<HR SIZE=1>
<B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B> "Shinn, Kim" <kim.shinn@tlc-eng.com><BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> Nick Caton <ncaton@smithboucher.com>; Dakota Kelley <dakotak@teliospc.com>; reniel barroso <renielbarroso@yahoo.com>; "equest-users@lists.onebuilding.org" <equest-users@lists.onebuilding.org><BR><B><SPAN style="FONT-WEIGHT: bold">Sent:</SPAN></B> Wednesday, February 17, 2010 21:44:23<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> RE: [Equest-users] Above Roof Canopy Modeling<BR></FONT><BR>
<STYLE>
<!--
 
 _filtered {font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
 _filtered {font-family:Tahoma;
panose-1:2 11 6 4 3 5 4 4 2 4;}
 _filtered {font-family:"Stylus BT";
panose-1:2 14 4 2 2 2 6 2 3 4;}
 _filtered {font-family:"Franklin Gothic Book";}
 
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
margin-bottom:.0001pt;
font-size:12.0pt;
font-family:"Times New Roman", "serif";}
a:link, span.MsoHyperlink
        {
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {
color:purple;
text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {

margin:0in;
margin-bottom:.0001pt;
font-size:8.0pt;
font-family:"Tahoma", "sans-serif";}
span.BalloonTextChar
        {


font-family:"Tahoma", "sans-serif";}
span.EmailStyle19
        {
font-family:"Arial", "sans-serif";
color:#1F497D;}
span.EmailStyle20
        {
font-family:"Calibri", "sans-serif";
color:#1F497D;}
span.EmailStyle21
        {
font-family:"Calibri", "sans-serif";
color:#1F497D;}
span.EmailStyle22
        {
font-family:"Calibri", "sans-serif";
color:#1F497D;}
span.EmailStyle23
        {
font-family:"Arial", "sans-serif";
color:#1F497D;}
.MsoChpDefault
        {
font-size:10.0pt;}
 _filtered {
margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {}
-->
</STYLE>

<DIV class=Section1>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">At the risk of piling on more information than you really wanted:</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">App G allows you to take advantage of shading – so, remove shading from your 90.1 baseline.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">You can assign schedules, transparency and reflectance to shades.  If you want to model the effect of deciduous trees planted near the building, for instance, you can use a schedule to have greater transparency in the winter (for passive solar heating) and less transparency in the summer for shading.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<DIV>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Kim E Shinn, PE, LEED AP BD+C, CxA</SPAN></B><SPAN style="COLOR: #1f497d"></SPAN></P>
<P class=MsoNormal><I><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #333333; FONT-SIZE: 10pt">Senior Sustainability Consultant</SPAN></I><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"></SPAN></P></DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<DIV>
<DIV style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Tahoma', 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-FAMILY: 'Tahoma', 'sans-serif'; FONT-SIZE: 10pt"> Nick Caton [mailto:ncaton@smithboucher.com] <BR><B>Sent:</B> Wednesday, February 17, 2010 11:29 AM<BR><B>To:</B> Dakota Kelley; Shinn, Kim; reniel barroso; equest-users@lists.onebuilding.org<BR><B>Subject:</B> Re: [Equest-users] Above Roof Canopy Modeling</SPAN></P></DIV></DIV>
<P class=MsoNormal> </P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Thanks Dakota!</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">This is good to know as I have a situation where it would probably be less work to explore some specific overhang/fin options within my complex eQuest model vs. trying to build a separate model through my more usual daylight analysis workflows.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Bonus points for your response being 10x more clear than my question =)!</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">~Nick</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><IMG id=_x0000_i1025 alt=cid:489575314@22072009-0ABB src="cid:1.3197703093@web63407.mail.re1.yahoo.com" width=119 height=37></SPAN><B><SPAN style="FONT-FAMILY: 'Stylus BT', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 11pt"></SPAN></B></P>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Stylus BT', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 11pt"> </SPAN></B></P>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Stylus BT', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 11pt">NICK CATON, E.I.T.</SPAN></B><B><SPAN style="FONT-FAMILY: 'Stylus BT', 'sans-serif'; COLOR: #2d4d5e"></SPAN></B></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #cc9900; FONT-SIZE: 7.5pt">PROJECT ENGINEER</SPAN><SPAN style="COLOR: #cc9900; FONT-SIZE: 7.5pt"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">25501 west valley parkway</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">olathe ks 66061</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">direct 913 344.0036</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">fax 913 345.0617</SPAN></P>
<P class=MsoNormal><I><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">Check out our new web-site @ </SPAN></I><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><A title=blocked::www.smithboucher.com rel=nofollow><SPAN style="FONT-SIZE: 10pt">www.smithboucher.com</SPAN></A></SPAN><U><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: blue; FONT-SIZE: 10pt"> </SPAN></U><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"></SPAN></P></DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<DIV>
<DIV style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Tahoma', 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-FAMILY: 'Tahoma', 'sans-serif'; FONT-SIZE: 10pt"> Dakota Kelley [mailto:dakotak@teliospc.com] <BR><B>Sent:</B> Wednesday, February 17, 2010 11:16 AM<BR><B>To:</B> Nick Caton; Shinn, Kim; reniel barroso; equest-users@lists.onebuilding.org<BR><B>Subject:</B> RE: [Equest-users] Above Roof Canopy Modeling</SPAN></P></DIV></DIV>
<P class=MsoNormal> </P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Window shades only shade their parent window, not the walls.  Building shades will shade everything in their shadow, and they rotate with the building if the azimuth is changed.  Fixed shades also shade everything in their shadow, but they do not rotate with the building.</SPAN></P>
<P class=MsoNormal><SPAN style="TEXT-TRANSFORM: uppercase; FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 10pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 10pt">                                </SPAN></P>
<P class=MsoNormal><SPAN style="MARGIN-TOP: 2px; WIDTH: 71px; HEIGHT: 90px; MARGIN-LEFT: 0px"><IMG src="cid:2.3197703093@web63407.mail.re1.yahoo.com" width=71 height=90></SPAN><B><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 10pt">                        DAKOTA KELLEY</SPAN></B><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 10pt">              </SPAN><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 8pt">                                                </SPAN><B><SPAN
 style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 10pt"></SPAN></B></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 8pt">                                </SPAN><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 10pt">Project Designer</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 8pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 8pt">                                Office:      214-744-6199</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 8pt">                                Cell:         214-280-3825</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 8pt">                                Fax:         214-744-0770 </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 8pt">                </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 8pt"><A href="http://www.teliospc.com/" rel=nofollow target=_blank><SPAN style="FONT-FAMILY: 'Times New Roman', 'serif'">http://www.teliospc.com</SPAN></A>          3535 Travis St. Suite 115 </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: black; FONT-SIZE: 8pt"><A href="mailto:dakotak@teliospc.com" rel=nofollow target=_blank ymailto="mailto:dakotak@teliospc.com"><SPAN style="FONT-FAMILY: 'Times New Roman', 'serif'">dakotak@teliospc.com</SPAN></A>             Dallas, TX 75204 </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: #3333ff; FONT-SIZE: 8pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: #3333ff; FONT-SIZE: 8pt">| MEP ENGINEERING </SPAN><SPAN style="COLOR: #3333ff; FONT-SIZE: 8pt">·</SPAN><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: #3333ff; FONT-SIZE: 8pt"> ENERGY MODELING </SPAN><SPAN style="COLOR: #3333ff; FONT-SIZE: 8pt">· </SPAN><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: #3333ff; FONT-SIZE: 8pt">LEED CONSULTATION </SPAN><SPAN style="COLOR: #3333ff; FONT-SIZE: 8pt">·</SPAN><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: #3333ff; FONT-SIZE: 8pt"> COMMISSIONING |</SPAN><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: #1f497d; FONT-SIZE: 8pt">                         </SPAN></P>
<P style="TEXT-ALIGN: justify" class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: gray; FONT-SIZE: 8pt"> </SPAN></P>
<P style="TEXT-ALIGN: justify" class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: gray; FONT-SIZE: 8pt"> </SPAN></P>
<P style="TEXT-ALIGN: justify" class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: gray; FONT-SIZE: 8pt">CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed, </SPAN></P>
<P style="TEXT-ALIGN: justify" class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: gray; FONT-SIZE: 8pt">And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you </SPAN></P>
<P style="TEXT-ALIGN: justify" class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: gray; FONT-SIZE: 8pt">are not the intended recipient, please email the sender immediately, and delete this email from all computers.  Any </SPAN></P>
<P style="TEXT-ALIGN: justify" class=MsoNormal><SPAN style="FONT-FAMILY: 'Franklin Gothic Book'; COLOR: gray; FONT-SIZE: 8pt">distribution or other use is strictly prohibited.  Copyright © 2010 Telios Corporation.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<DIV>
<DIV style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Tahoma', 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-FAMILY: 'Tahoma', 'sans-serif'; FONT-SIZE: 10pt"> Nick Caton [mailto:ncaton@smithboucher.com] <BR><B>Sent:</B> Wednesday, February 17, 2010 11:10 AM<BR><B>To:</B> Shinn, Kim; reniel barroso; equest-users@lists.onebuilding.org<BR><B>Subject:</B> Re: [Equest-users] Above Roof Canopy Modeling</SPAN></P></DIV></DIV>
<P class=MsoNormal> </P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Here is another illustration shading a courtyard of sorts.  You’re looking at the dark grey rectangle in both examples.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">I have a followup actually for others familiar with creating building shades – are they any different in behavior from a window shade, or are they the same thing simply defined in different ways?  More specifically, do window shades shade buildings and can I define building shades as a means of modeling multiple vertical fins/horizontal light shades per window?  </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><IMG id=_x0000_i1026 border=0 alt=cid:image002.png@01CA6907.A781F540 src="cid:3.3197703093@web63407.mail.re1.yahoo.com" width=1245 height=712></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">~Nick</SPAN></P>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><IMG id=Picture_x0020_1 border=0 alt=cid:489575314@22072009-0ABB src="cid:1.3197703093@web63407.mail.re1.yahoo.com" width=119 height=37></SPAN><B><SPAN style="FONT-FAMILY: 'Stylus BT', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 11pt"></SPAN></B></P>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Stylus BT', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 11pt"> </SPAN></B></P>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Stylus BT', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 11pt">NICK CATON, E.I.T.</SPAN></B><B><SPAN style="FONT-FAMILY: 'Stylus BT', 'sans-serif'; COLOR: #2d4d5e"></SPAN></B></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #cc9900; FONT-SIZE: 7.5pt">PROJECT ENGINEER</SPAN><SPAN style="COLOR: #cc9900; FONT-SIZE: 7.5pt"></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">25501 west valley parkway</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">olathe ks 66061</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">direct 913 344.0036</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">fax 913 345.0617</SPAN></P>
<P class=MsoNormal><I><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">Check out our new web-site @ </SPAN></I><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><A title=blocked::www.smithboucher.com rel=nofollow><SPAN style="FONT-SIZE: 10pt">www.smithboucher.com</SPAN></A></SPAN><U><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: blue; FONT-SIZE: 10pt"> </SPAN></U><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"></SPAN></P></DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<DIV>
<DIV style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Tahoma', 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-FAMILY: 'Tahoma', 'sans-serif'; FONT-SIZE: 10pt"> equest-users-bounces@lists.onebuilding.org [mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Shinn, Kim<BR><B>Sent:</B> Wednesday, February 17, 2010 9:03 AM<BR><B>To:</B> reniel barroso; equest-users@lists.onebuilding.org<BR><B>Subject:</B> Re: [Equest-users] Above Roof Canopy Modeling</SPAN></P></DIV></DIV>
<P class=MsoNormal> </P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Reniel:</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">What you need is an exterior shade.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">In detailed edit mode, go to Building Shell and select Fixed Shades (or a Building Shade, depending on whether you want the shade to be attached to the building – as it rotates, for instance).  A fixed shade remains fixed in space.  This is a good way to model adjacent buildings.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><IMG id=Picture_x0020_2 border=0 src="cid:4.3197703093@web63407.mail.re1.yahoo.com" width=1280 height=1024></SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Right click on Fixed Shade and go through the dialog boxes.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<DIV>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Kim E Shinn, PE, LEED AP BD+C, CxA</SPAN></B><SPAN style="COLOR: #1f497d"></SPAN></P>
<P class=MsoNormal><I><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #333333; FONT-SIZE: 10pt">Senior Sustainability Consultant</SPAN></I><SPAN style="FONT-FAMILY: 'Calibri', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"></SPAN></P></DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"> </SPAN></P>
<DIV>
<DIV style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'Tahoma', 'sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-FAMILY: 'Tahoma', 'sans-serif'; FONT-SIZE: 10pt"> reniel barroso [mailto:renielbarroso@yahoo.com] <BR><B>Sent:</B> Wednesday, February 17, 2010 8:22 AM<BR><B>To:</B> equest-users@lists.onebuilding.org<BR><B>Subject:</B> [Equest-users] Above Roof Canopy Modeling</SPAN></P></DIV></DIV>
<P class=MsoNormal> </P>
<DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt">Hi to All,</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt"> </SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt">We are modeling 3 buildings interconnected with each other.</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt">A large canopy is covering the roof of the buildings and partially shading the courtyard within these buildings.</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt"> </SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt">Can we model this canopy in eQuest? How?</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt">Can we model its effect on the cooling load of spaces facing the courtyard?</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt">We are expecting that solar heat gain will be lower on fenestrations of the rooms/spaces facing courtyard due to shading compared to perimeter spaces facing outside the development.</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt"> </SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt">Thanks in advance.</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt"> </SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt"> </SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt">Reniel</SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt"> </SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt"> </SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt"> </SPAN></P></DIV></DIV>
<P class=MsoNormal> </P>
<DIV style="TEXT-ALIGN: center" class=MsoNormal align=center>
<HR align=center SIZE=1 width="100%">
</DIV>
<P class=MsoNormal><A href="http://sg.rd.yahoo.com/aa/mail/domainchoice/mail/signature/*http:/mail.promotions.yahoo.com/newdomains/aa/" rel=nofollow target=_blank>New Email addresses available on Yahoo! </A><BR>Get the Email name you've always wanted on the new @ymail and @rocketmail.<BR>Hurry before someone else d</P></DIV></DIV></DIV></div><br>