Instead of using the 'HP' system TYPE, try using the 'PSZ' or 'PVVT'
system TYPE. With HEAT-SOURCE = HEAT-PUMP and CONDENSER-TYPE =
WATER-COOLED (and connected to a LOOP of TYPE=WLHP) you will be
simulating a water source heat pump. These two system types support the
full DOE-2 ERV functionality.<br>
<pre class="moz-signature" cols="72">Kevin Madison PE
Madison Engineering PS
444 NE Ravenna Blvd Suite 406
Seattle WA 98115
<a class="moz-txt-link-abbreviated" href="http://www.madisonengineeringps.com">www.madisonengineeringps.com</a></pre>
<br>
On 2/16/2010 1:42 PM, O'Connor, Dennis CAR wrote:
<blockquote
 cite="mid:A4AFF2BE4B0F484DA867C19125B23F4303AC8FAC@UUSMNEG1.na.utcmail.com"
 type="cite">
  <meta http-equiv="Context-Type"
 content="text/html; charset=iso-8859-1">
  <div>
  <p><span>Fellow
Equest-Users, </span></p>
  <p><span>   </span></p>
  <p><span>I
would greatly appreciate it, if someone would take a moment to explain
the
following: </span></p>
  <p><span>   </span></p>
  <p><span>Why
doesn’t eQUEST allow airside heat recovery with water loop heat pumps?
 HAP
does allow this type of application. </span></p>
  <p><span>   </span></p>
  <p><span>I
went through the archives and was unable to find an answer to my
question. </span></p>
  <p><span>   </span></p>
  <p><span>Does
anyone know of a work around using a WLHP?   </span></p>
  <p><span>   </span></p>
  <p><span>Thanks
in advance for taking the time to review my question, </span></p>
  <p><span>   </span></p>
  <p><span>Dennis
O’Connor </span></p>
  <p><span>Graduate
Student at the University of Hartford </span></p>
  <p><span>   </span></p>
  <p><span><img src="cid:part1.07080905.09020102@yahoo.com"></span><span>
  </span></p>
  <p><span>   </span></p>
  <p><span>   </span></p>
  </div>
  <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
  </pre>
</blockquote>
</body>
</html>