<DIV dir=ltr align=left><SPAN class=958002708-16022010><FONT face=Arial 
color=#0000ff size=2>Steve,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=958002708-16022010><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=958002708-16022010><FONT face=Arial 
color=#0000ff size=2>My understanding is that deadband is not the same as 
throttle range. Deadband is the temperature&nbsp;range&nbsp;between the system 
being cooling to heating. See attached to clarify. </FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=958002708-16022010><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=958002708-16022010><FONT face=Arial 
color=#0000ff size=2>Regards</FONT></SPAN></DIV><!-- Converted from text/rtf format -->
<P><SPAN lang=es><SPAN class=958002708-16022010><FONT face=Arial color=#0000ff 
size=2>Francisco</FONT></SPAN></SPAN></P>
<DIV>&nbsp;</DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> equest-users-bounces@lists.onebuilding.org 
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>STEVE 
SAMENSKI<BR><B>Sent:</B> martes, 16 de febrero de 2010 1:05<BR><B>To:</B> Demba 
Ndiaye; equest-users@lists.onebuilding.org; John Aulbach<BR><B>Subject:</B> Re: 
[Equest-users] Reproducing Unmet Hours<BR></FONT><BR></DIV>
<DIV></DIV><FONT face=Arial><SPAN style="FONT-SIZE: 12pt">John &#8212; thanks for the 
tip on the throttling range. &nbsp;I was able to reduce the unmet hours by 
increasing the range from 2 degrees to 4 degrees in the perimeter 
zones.<BR><BR>Demba &#8212; As I read the help file, the throttling range is the same 
as the dead band described in in 6.4.3.1.2 of Standard 90.1.<BR><BR>&#8220;The number 
of degrees that room temperature must change in order to go from full heating to 
zero heating or from full cooling to zero cooling. The zone temperature heating 
or cooling set point is assumed to be at the midpoint of the throttling range. 
This keyword is appropriate to THERMOSTAT-TYPE = PROPORTIONAL or REVERSE-ACTION 
only. &#8220;<BR><BR>Since the heating or cooling setpoint is assumed to be at the 
midpoint of the throttling range, then a throttling range of 10 degrees would 
correspond to a dead band of &nbsp;5 degrees. &nbsp;Maybe tomorrow I&#8217;ll see what 
that does to my results.<BR><BR>Steve Samenski, PE, LEED AP<BR><A 
href="http://equest-diary.livejournal.com/">http://equest-diary.livejournal.com/</A><BR><BR>On 
2/15/10 3:42 PM, "Demba Ndiaye" &lt;<A 
href="Demba.Ndiaye@setty.com">Demba.Ndiaye@setty.com</A>&gt; 
wrote:<BR><BR></SPAN></FONT>
<BLOCKQUOTE><FONT color=#1f497d><FONT 
  face="Calibri, Verdana, Helvetica, Arial"><SPAN style="FONT-SIZE: 11pt">By 
  dead band, do you mean the throttling range that eQuest defines? If so, there 
  is a limit on how much you can increase it, due to the 5F minimum dead band 
  requirements of the 
  90.1.<BR>&nbsp;<BR>Demba.<BR>&nbsp;<BR></SPAN></FONT></FONT><FONT 
  face=Arial><SPAN style="FONT-SIZE: 12pt"><BR></SPAN></FONT><FONT size=2><FONT 
  face="Tahoma, Verdana, Helvetica, Arial"><SPAN 
  style="FONT-SIZE: 10pt"><B>From:</B> <A 
  href="equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</A> 
  [<A 
  href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</A>] 
  <B>On Behalf Of </B>John Aulbach<BR><B>Sent:</B> Sunday, February 14, 2010 
  12:57 AM<BR><B>To:</B> STEVE SAMENSKI; <A 
  href="equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</A><BR><B>Subject:</B> 
  Re: [Equest-users] Reproducing Unmet Hours<BR></SPAN></FONT></FONT><FONT 
  face="Times New Roman"><SPAN style="FONT-SIZE: 12pt"><BR></SPAN></FONT><SPAN 
  style="FONT-SIZE: 12pt"><FONT face=Arial><BR></FONT><FONT 
  face="Times New Roman">Steve:<BR></FONT><FONT face=Arial><BR></FONT><FONT 
  face="Times New Roman"><BR></FONT><FONT face=Arial><BR></FONT><FONT 
  face="Times New Roman">The NO. 1 thing I have found effective is to increase 
  the deanband in the thermostat. I don't thin USGBC has any problem with 
  that.<BR></FONT><FONT face=Arial><BR></FONT><FONT 
  face="Times New Roman"><BR></FONT><FONT face=Arial><BR></FONT><FONT 
  face="Times New Roman">It also depends on wheather it is COOLING or HEATING 
  unmet housers. Sometimes, you haven't provided a reheat vaule.<BR></FONT><FONT 
  face=Arial><BR></FONT><FONT face="Times New Roman"><BR></FONT><FONT 
  face=Arial><BR></FONT><FONT face="Times New Roman">Try those 
  first.<BR></FONT><FONT face=Arial><BR></FONT><FONT 
  face="Times New Roman"><BR></FONT><FONT face=Arial></FONT></SPAN>
  <P align=center><FONT size=2><FONT 
  face="Tahoma, Verdana, Helvetica, Arial"><SPAN style="FONT-SIZE: 10pt">
  <HR align=center width="100%" SIZE=1>
  </SPAN></FONT></FONT>
  <P><FONT size=2><FONT face="Tahoma, Verdana, Helvetica, Arial"><SPAN 
  style="FONT-SIZE: 10pt"><B>From:</B> STEVE SAMENSKI &lt;<A 
  href="steve@thespinnakergroupinc.com">steve@thespinnakergroupinc.com</A>&gt;<BR><B>To:</B> 
  <A 
  href="equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</A><BR><B>Sent:</B> 
  Sat, February 13, 2010 2:59:00 PM<BR><B>Subject:</B> [Equest-users] 
  Reproducing Unmet Hours<BR></SPAN></FONT></FONT><FONT 
  face="Times New Roman"><SPAN style="FONT-SIZE: 12pt"><BR></SPAN></FONT><SPAN 
  style="FONT-SIZE: 12pt"><FONT face=Arial>It seems I spend a great deal of time 
  with eQuest trying to reduce unmet hours in a model. &nbsp;One thing I&#8217;ve 
  tried is having eQuest produce an hourly report of a problem zone&#8217;s 
  temperature and T-stat setting, exporting the data to Excel and then searching 
  it for patterns. &nbsp;This approach has a few problems:<BR></FONT></SPAN>
  <OL>
    <LI><SPAN style="FONT-SIZE: 12pt"><FONT face=Arial>I can barely figure out 
    how to create the hourly report I&#8217;m looking for. &nbsp;The reporting 
    function (in the Detailed Data Edit mode, under Project &amp; Site, Hourly 
    Reports) isn&#8217;t very intuitive, and I can&#8217;t find any documentation on it. 
    &nbsp;Has anyone found the docs on this? &nbsp;(I&#8217;m currently working 
    through the relevant sections of the DOE 2-2 Dictionary, trying to cross 
    reference between the inputs to eQuest and the BDL file generated from those 
    inputs. &nbsp;I&#8217;m just wondering if there&#8217;s a short-cut somewhere.) 
    </FONT></SPAN>
    <LI><SPAN style="FONT-SIZE: 12pt"><FONT face=Arial>Once I get the data in 
    Excel and do some filtering, I can never get the exported data to match the 
    unmet hours found in report SS-R. &nbsp;The Excel analysis seems to always 
    overstate the unmet hours. &nbsp;Has anyone had any luck reproducing the 
    SS-R values? &nbsp;Any ideas? </FONT></SPAN>
    <LI><SPAN style="FONT-SIZE: 12pt"><FONT face=Arial>I&#8217;d like to hear other 
    user&#8217;s experience. &nbsp;Do you find that resolving unmet hours is a 
    significant part of your modeling time? <BR></FONT></SPAN></LI></OL><FONT 
  size=1><FONT face="Verdana, Helvetica, Arial"><SPAN 
  style="FONT-SIZE: 9pt"><BR></SPAN></FONT></FONT><FONT face=Arial><SPAN 
  style="FONT-SIZE: 12pt">Steve Samenski, PE, LEED AP</SPAN></FONT><SPAN 
  style="FONT-SIZE: 12pt"><FONT face="Times New Roman"> 
  <BR>&nbsp;<BR></FONT><FONT face=Arial><BR>
  <HR align=center width="95%" SIZE=3>
  </FONT><FONT 
  face="Courier New">_______________________________________________<BR>Equest-users 
  mailing list<BR><A 
  href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</A><BR>To 
  unsubscribe from this mailing list send &nbsp;a blank message to <A 
  href="EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</A></FONT></SPAN></BLOCKQUOTE></BODY></HTML>