<br>Hello<div><br></div><div>I&#39;ve attached the document. Though it is nothing more than a sheet out of our assignment for the eQuest class.</div><div>I do not have the original document from where this would have been taken. Hopefully this helps :)</div>
<div><br></div><div>Regards</div><div>Supriya</div><div><br><div class="gmail_quote">On Wed, Jan 13, 2010 at 4:28 PM, Katie Tuttle <span dir="ltr">&lt;<a href="mailto:Katie.Tuttle@hei-eng.com">Katie.Tuttle@hei-eng.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">








<div lang="EN-US" link="blue" vlink="purple">

<div>

<p class="MsoNormal"><span style="font-size:11.0pt">I
would be curious to see that document.  Would you mind posting it?  Thanks!</span><b><span style="font-size:8.0pt;color:#566C11"></span></b></p>

<p class="MsoNormal"><span style="font-size:11.0pt"> </span></p>

<div style="border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in">

<p class="MsoNormal"><b><span style="font-size:10.0pt">From:</span></b><span style="font-size:10.0pt">
<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Supriya
Goel<br>
<b>Sent:</b> Wednesday, January 13, 2010 5:22 PM<br>
<b>To:</b> Jacob Goodman<br>
<b>Cc:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] Cooling EIR and unit EER</span></p>

</div><div><div></div><div class="h5">

<p class="MsoNormal"> </p>

<p class="MsoNormal">Jacob</p>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">You&#39;re right, EIR is not equal to 1/(EER/3.14)</p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">The equation used by eQuest for calculating EIR from EER is-</p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">COOLING-EIR = (1/EER - 0.012167) / ((1 / 3.413) + 0.012167)</p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">If you want more information, I could send you the document
from where I got this.</p>

</div>

<div>

<p class="MsoNormal"> </p>

</div>

<div>

<p class="MsoNormal">Regards</p>

</div>

<div>

<p class="MsoNormal">Supriya</p>

</div>

<div>

<p class="MsoNormal" style="margin-bottom:12.0pt"> </p>

<div>

<p class="MsoNormal">On Wed, Jan 13, 2010 at 4:11 PM, Jacob Goodman &lt;<a href="mailto:jacobg@lseng.com" target="_blank">jacobg@lseng.com</a>&gt; wrote:</p>

<div>

<p class="MsoNormal">How does eQuest calculate &quot;cooling electrical input
ratio&quot; shown in detailed edit mode when you input an EER in the wizard?
>From a few checks I&#39;ve done cooling EIR doesn&#39;t equal 1/(EER/3.413) as I would
expect.</p>

<div>

<p class="MsoNormal"><br>
<b><span style="font-size:11.0pt;color:black">Jacob
</span></b></p>

</div>

<p class="MsoNormal"> </p>

</div>

<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></p>

</div>

<p class="MsoNormal" style="margin-bottom:12.0pt"><br>
<br clear="all">
<br>
-- <br>
Graduate Student, MSBE<br>
School of Architecture and Landscape Architecture<br>
Arizona State University, Tempe<br>
<br>
<br>
</p>

</div>

</div></div></div>

<pre>This email and any files transmitted with it are confidential and
are intended solely for the use of the individual or entity to whom
they are addressed.  This communication represents the originator&#39;s
personal views and opinions, which do not necessarily reflect those of
Henderson Engineers, Inc.  If you are not the original recipient or the
person responsible for delivering the email to the intended recipient,
be advised that you have received this email in error, and that any use,
dissemination, forwarding, printing, or copying of this email is strictly
prohibited.  If you received this email in error, please immediately
notify <a href="mailto:administrator@hei-eng.com" target="_blank">administrator@hei-eng.com</a>.





</pre></div>


</blockquote></div><br><br clear="all"><br>-- <br>Graduate Student, MSBE<br>School of Architecture and Landscape Architecture<br>Arizona State University, Tempe<br><br><br><br>
</div>