<br><font size=2 face="sans-serif">Here's a better explanation:</font>
<br>
<br><font size=2 face="sans-serif">Anytime a shell is placed "<b>Immediately
Above</b>" another, eQUEST realizes that floor of the current shell
is adjacent to the roof of the shell in reference and models it as an interior
surface. But if the footprints of the two shells differ in shape resulting
in overhangs (or cantilevered floors) or extended roofs eQUEST will not
be able to create new polygons on its own in order to generate additional
roofs (exterior surfaces). This has to be done manually in detailed data
edit mode.</font>
<br>
<br><font size=2 face="sans-serif">In order <b>not </b>to create an exterior
roof for every shell, on screen 3 of the DD wizard "<b>No Exterior
Exposure (adiabatic)</b>" needs to be chosen for roof construction.</font>
<br>
<br><font size=2 face="sans-serif">Hope this doesn't cause further confusion!
:)<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Anand Varahala, LEED<sup>®</sup> AP</b> | </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b> | Energy
Solutions</b> | <b>Application Engineer</b> <b><br>
Phone:</b> +1 </font><font size=1 face="Arial">(919) 227-3920</font><font size=1 face="Arial">
| <b>Fax:</b> </font><font size=1 face="Arial">+1 (859) 962-4561</font><font size=1 face="Arial">
| </font><font size=1 face="Arial"> </font><font size=1 face="Arial"><b>Mobile:</b>
</font><font size=1 face="Arial">+1 (919) 720-0769</font><font size=1 face="Arial">
<b><br>
Email:</b> </font><a href="mailto:Anand.Varahala@us.schneider-electric.com"><font size=1 color=blue face="Arial"><u>Anand.Varahala@us.schneider-electric.com</u></font></a><font size=1 face="Arial">
| <b>Site:</b> </font><a href="http://www.schneider-electric.us/"><font size=1 color=blue face="Arial"><u>www.schneider-electric.us</u></font></a><font size=1 face="Arial">
| <b>Address:</b> </font><font size=1 face="Arial">4917 Waters
Edge Dr, Suite 270, Raleigh NC 27606</font><font size=1 face="Arial"> USA</font><font size=5 color=#008000 face="Webdings"><br>
P</font><font size=1 color=#00a000 face="Arial"> Please consider the environment
before printing this e-mail</font><font size=1 face="Arial"> </font>
<br>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td width=40%><font size=1 face="sans-serif"><b>Anand Varahala/US/Schneider</b></font>
<p><font size=1 face="sans-serif">01/05/2010 10:44</font>
<td width=59%>
<table width=100%>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">To</font></div>
<td><font size=1 face="sans-serif">equest-users@lists.onebuilding.org</font>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">cc</font></div>
<td><font size=1 face="sans-serif">jwendel@heatheng.com</font>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">Subject</font></div>
<td><font size=1 face="sans-serif">Re: Multiple Floors with Multiple Roofs?</font><a href=Notes://CVGNM02/852574DA0068B7B4/A4D87D90E1B19842852564FF006DED4E/13BB4C0AE0AFCA81852576A20053D710>Link</a></table>
<br>
<table>
<tr valign=top>
<td>
<td></table>
<br></table>
<br>
<br><font size=2 face="sans-serif">Jason,</font>
<br>
<br><font size=2 face="sans-serif">I will go ahead and assume you meant
to say you created 3 "shells" (instead of 'models') and stacked
them on top of each other.</font>
<br>
<br><font size=2 face="sans-serif">If you did this in the Design Development
Wizard, you must have chosen a roof type for every shell, which would be
incorrect according to eQUEST. One of the cons of eQUEST is unlike walls
it doesn't automatically detect floors adjacent to roofs and 'crop' them
accordingly.</font>
<br><font size=2 face="sans-serif">You will have to do this yourself in
detailed data edit mode. There are two ways to do this:</font>
<br>
<br><font size=2 face="sans-serif">1. Assign a roof for every shell and
then delete the portions that have a floor above.</font>
<br><font size=2 face="sans-serif">2. Do <b>not </b>create roofs for any
of the floors except the top most, and then in detailed mode add roofs
to the lower level floors as needed.</font>
<br>
<br><font size=2 face="sans-serif">I hope this will be fixed in the upcoming
version 3.64, but we will have to wait and see.</font>
<br>
<br><font size=2 face="sans-serif">Hope it helps, let me know if you have
more questions.<br>
</font><font size=3 color=#008000>_____________________________________________________________________________________</font><font size=3>
<br>
</font><font size=1 face="Arial"><b><br>
Anand Varahala, LEED<sup>®</sup> AP</b> | </font><font size=1 color=#008000 face="Arial"><b>
Schneider Electric </b></font><font size=1 face="Arial"><b> | Energy
Solutions</b> | <b>Application Engineer</b> <b><br>
Phone:</b> +1 </font><font size=1 face="Arial">(919) 227-3920</font><font size=1 face="Arial">
| <b>Fax:</b> </font><font size=1 face="Arial">+1 (859) 962-4561</font><font size=1 face="Arial">
| </font><font size=1 face="Arial"> </font><font size=1 face="Arial"><b>Mobile:</b>
</font><font size=1 face="Arial">+1 (919) 720-0769</font><font size=1 face="Arial">
<b><br>
Email:</b> </font><a href="mailto:Anand.Varahala@us.schneider-electric.com"><font size=1 color=blue face="Arial"><u>Anand.Varahala@us.schneider-electric.com</u></font></a><font size=1 face="Arial">
| <b>Site:</b> </font><a href="http://www.schneider-electric.us/"><font size=1 color=blue face="Arial"><u>www.schneider-electric.us</u></font></a><font size=1 face="Arial">
| <b>Address:</b> </font><font size=1 face="Arial">4917 Waters
Edge Dr, Suite 270, Raleigh NC 27606</font><font size=1 face="Arial"> USA</font><font size=5 color=#008000 face="Webdings"><br>
P</font><font size=1 color=#00a000 face="Arial"> Please consider the environment
before printing this e-mail</font><font size=1 face="Arial"> </font>
<br>
<br>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td width=40%><font size=1 face="sans-serif"><b>equest-users-request@lists.onebuilding.org</b>
</font>
<br><font size=1 face="sans-serif">Sent by: equest-users-bounces@lists.onebuilding.org</font>
<p><font size=1 face="sans-serif">01/05/2010 10:19</font>
<table border>
<tr valign=top>
<td bgcolor=white>
<div align=center><font size=1 face="sans-serif">Please respond to<br>
equest-users@lists.onebuilding.org</font></div></table>
<br>
<td width=59%>
<table width=100%>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">To</font></div>
<td><font size=1 face="sans-serif">equest-users@lists.onebuilding.org</font>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">cc</font></div>
<td>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">Subject</font></div>
<td><font size=1 face="sans-serif">Equest-users Digest, Vol 22, Issue 5</font></table>
<br>
<table>
<tr valign=top>
<td>
<td></table>
<br></table>
<br>
<br>
<br><font size=2 color=#800080 face="sans-serif">----- Message from Jason
Wendel <jwendel@heatheng.com> on Tue, 5 Jan 2010 15:09:47 +0000 -----</font>
<table>
<tr>
<td>
<div align=right><font size=3><b>To:</b></font></div>
<td><font size=3>"'equest-users@lists.onebuilding.org'" <equest-users@lists.onebuilding.org></font>
<tr>
<td>
<div align=right><font size=3><b>Subject:</b></font></div>
<td><font size=3>[Equest-users] Multiple Floors with Multiple Roofs?</font></table>
<br><font size=2 color=#004080 face="Calibri">I am modeling a building
with 2-3 floors depending on where in the building you are. Each
of the floors are somewhat different so I created 3 models and stacked
them on top of each other. Once I got into the detailed mode I find
that the program put a roof on each floor. I had incorrectly assumed
that if I put one floor on top of another, then the program would recognize
that it’s “roof” is adjacent to another floor and make it adiabatic
while overhangs and extended roofs would keep their “roof label”. Do
I now need to go through and delete all the roofs from the 1<sup>st</sup>
and part of the 2<sup>nd</sup> floor? Or does eQuest not take them
in on the calculation because it knows that it should be adiabatic since
it has a floor above it?</font>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><img src=cid:_2_05C9C94405C9C638006473DD852576A2>
<br><font size=2 color=#004080 face="Calibri"> </font>
<br><font size=2 color=#004080 face="Calibri">-Jason</font><tt><font size=2>_______________________________________________<br>
Equest-users mailing list<br>
Equest-users@lists.onebuilding.org<br>
</font></tt><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"><tt><font size=2>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</font></tt></a><tt><font size=2><br>
</font></tt>
<br>