<P><FONT size=2>Jason,<BR><BR>My bet is that you have a pretty high dT across
the fan (operating at > 5") causing your actually leaving air temperature off
the cooling coil to be less than 50F. I am pretty sure (although it has been a
while) that you can avoid this error and still maintain the same conditions
if you implement a reset schedule on your air temperature (even if you don't
actually reset it), rather than using the cool-min-temp
only.<BR><BR>Regards,<BR><BR></P>
<DIV class=Section1>
<P class=MsoNormal><B><SPAN style="FONT-FAMILY: 'GillSans Light'"><SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt">Jonathan
M. Curtin, EIT, LEED</SPAN></B><SUP><SPAN
style="FONT-FAMILY: 'GillSans Light'">®</SPAN></SUP><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt">
AP</SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'"><BR></SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt"><SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'">Mechanical
Engineer</SPAN></B><STRONG><SPAN
style="FONT-FAMILY: 'GillSans Light'"><?xml:namespace prefix = o ns =
"urn:schemas-microsoft-com:office:office" /><o:p></o:p></SPAN></STRONG></P>
<P class=MsoNormal><STRONG><SPAN style="FONT-FAMILY: 'GillSans Light'"><SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></STRONG><B><SPAN
style="FONT-FAMILY: 'GillSans Light'"><IMG height=159
src="cid:458315817@17122009-1E49" width=240
v:shapes="_x0000_i1025"><STRONG><o:p></o:p></STRONG></SPAN></B></P></DIV>
<P><BR>-----Original Message-----<BR>From:
equest-users-bounces@lists.onebuilding.org [<A
href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</A>]
On Behalf Of Jason Wendel<BR>Sent: Thursday, December 17, 2009 11:50 AM<BR>To:
'equest-users@lists.onebuilding.org'<BR>Subject: [Equest-users] Cooling Coil
Error<BR><BR>I have an error that says:<BR><BR>In S1 Sys (VAVS), Cooling coil
leaving temperature must be at least 6F higher than entering water
temp.<BR><BR>I have 44" entering CHW with a 12 degree delta T. Cold Air
for the system is set to 54F. I thought with a chiller with a 12 degree
delta T there shouldn't be the above error.<BR>Any
ideas?<BR><BR>-Jason<BR>_______________________________________________<BR>Equest-users
mailing list<BR><A
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuildingorg</A><BR>To
unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR></FONT></P>
<!--qsdbegin-->
<DIV><SPAN class=469015015-07012009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=469015015-07012009>
<DIV class=MsoNormal style="MARGIN: 0in 0in 0pt; TEXT-ALIGN: center"
align=center>
<HR align=center width="100%" SIZE=2>
</DIV><FONT color=#000000><U><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">Legal
Disclaimer:</SPAN></U><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">
</SPAN><STRONG><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">The
information contained in this communication is confidential and is
</SPAN></STRONG><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">covered
by the Electronic Communications Privacy Act, 18 U.S.C. §§ 2510-2521; it
</SPAN><STRONG><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">may
be privileged and is intended for the exclusive use of the above named
addressee(s). If you are not the intended recipient(s), you are expressly
prohibited from copying, distributing, disseminating, or in any other way using
any of the information contained within this communication. If you have received
this communication in error, please contact the sender by telephone at
(713) 781-2526 or by response via email and permanently delete the original
email (including attachments) and any copies. </SPAN></STRONG><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">
<BR><BR><SPAN
style="FONT-SIZE: 6.5pt; COLOR: #007213; FONT-FAMILY: Arial">Please consider the
environment before printing this email.</SPAN></I></SPAN></FONT></SPAN><B><SPAN
style="FONT-SIZE: 11pt; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 12.0pt"> <SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></B><B><SPAN
<!--qsdend-->
<br></BODY></HTML>