<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns="http://www.w3.org/TR/REC-html40">

<head>
<meta http-equiv=Content-Type content="text/html; charset=us-ascii">
<meta name=Generator content="Microsoft Word 12 (filtered medium)">
<style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
span.EmailStyle17
        {mso-style-type:personal-compose;
        font-family:"Calibri","sans-serif";
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {page:Section1;}
-->
</style>
<!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
</head>

<body lang=EN-US link=blue vlink=purple>

<div class=Section1>

<p class=MsoNormal>This is a re-peat question but I have not received an answer
or suggestions.<o:p></o:p></p>

<p class=MsoNormal><o:p> </o:p></p>

<p class=MsoNormal>I am having problems modeling an ice storage system. The
cost reduction savings seem realistic when I model ice storage but the cooling
load decreases by roughly 33% and pump energy also decreases by 25% when ice
storage is added. The cooling load should be slightly smaller because the
chiller is more efficient at night but not by 1/3. The pump energy should not
decrease by 25%. <o:p></o:p></p>

<p class=MsoNormal><o:p> </o:p></p>

<p class=MsoNormal>The cost savings are nearly identical to what CALMAC’s
cost savings spreadsheet calculates.<o:p></o:p></p>

<p class=MsoNormal><o:p> </o:p></p>

<p class=MsoNormal>If anyone has had success modeling ice storage please let me
know.<o:p></o:p></p>

<p class=MsoNormal><o:p> </o:p></p>

<p class=MsoNormal>If anyone knows how to subtract a lump sum of electrical cost
from eQUEST please let me know so I can use CALMAC’s spreadsheet and
simply subtract the savings from the electrical cost and label it “Thermal
Storage Savings”. <o:p></o:p></p>

<p class=MsoNormal><o:p> </o:p></p>

<p class=MsoNormal>Thanks,<o:p></o:p></p>

<p class=MsoNormal><o:p> </o:p></p>

<p class=MsoNormal>Otto Schwieterman<o:p></o:p></p>

<p class=MsoNormal><o:p> </o:p></p>

<p class=MsoNormal><o:p> </o:p></p>

</div>

</body>

</html>

<pre>________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
designated individual or entity.   If you received this message in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
electronic mail.  Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe unlawful.   Any information included in
this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance.