<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><DIV>Sherri:</DIV>
<DIV> </DIV>
<DIV>Get all your other items done that you do on the Wizard level. You need to get to the Detailed Edit, then into the .INP file to manually change those.</DIV>
<DIV> </DIV>
<DIV>I do not think there is a more straightforward (or any other) way.</DIV>
<DIV> </DIV>
<DIV>Maybe someday in a future version.</DIV>
<DIV> </DIV>
<DIV><BR>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><A name=_MailAutoSig><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">John R. Aulbach, PE, CEM<?xml:namespace prefix = o ns = "urn:schemas-microsoft-com:office:office" /><o:p></o:p></SPAN></A></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Senior Energy Engineer<o:p></o:p></SPAN></SPAN></P>
<DIV style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #17365d; mso-fareast-font-family: 'Times New Roman'; mso-no-proof: yes">
<HR style="COLOR: #17365d" align=left SIZE=2 width="30%" noShade>
</SPAN></SPAN></DIV>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: navy; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Partner</SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: green; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"> </SPAN></B></SPAN><SPAN style="mso-bookmark: _MailAutoSig"><B><SPAN style="FONT-VARIANT: small-caps; COLOR: #006600; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">Energy</SPAN><SPAN style="FONT-VARIANT: small-caps; COLOR: navy; mso-no-proof: yes"><o:p></o:p></SPAN></B></SPAN></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">1990 E. Grand Avenue, El Segundo, CA 90245<BR>W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745<o:p></o:p></SPAN></SPAN></P>
<P style="MARGIN: 0in 0in 0pt" class=MsoNormal><SPAN style="mso-bookmark: _MailAutoSig"></SPAN><A href="http://www.ptrenergy.com/"><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">www.ptrenergy.com</SPAN></SPAN><SPAN style="mso-bookmark: _MailAutoSig"></SPAN></A><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"> </SPAN></SPAN><A href="mailto:%7C%20jaulbach@ptrenergy.com"><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="mso-fareast-font-family: 'Times New Roman'; mso-fareast-theme-font: minor-fareast; mso-no-proof: yes">| jaulbach@ptrenergy.com</SPAN></SPAN><SPAN style="mso-bookmark: _MailAutoSig"></SPAN></A><SPAN style="mso-bookmark: _MailAutoSig"><SPAN style="COLOR: #1f497d; mso-fareast-font-family: 'Times New Roman';
mso-fareast-theme-font: minor-fareast; mso-no-proof: yes"><o:p></o:p></SPAN></SPAN></P></DIV>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><BR>
<DIV style="FONT-FAMILY: times new roman, new york, times, serif; FONT-SIZE: 12pt"><FONT size=2 face=Tahoma>
<HR SIZE=1>
<B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B> "Rocha, Sheri" <srocha@mkkeng.com><BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> "equest-users@lists.onebuilding.org" <equest-users@lists.onebuilding.org><BR><B><SPAN style="FONT-WEIGHT: bold">Sent:</SPAN></B> Wed, November 11, 2009 8:44:58 AM<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> [Equest-users] Adjacent Shells<BR></FONT><BR>
<STYLE>
<!--
_filtered {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}
_filtered {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;}
_filtered {font-family:Webdings;panose-1:5 3 1 2 1 5 9 6 7 3;}
_filtered {font-family:"Gill Sans MT";panose-1:2 11 5 2 2 1 4 2 2 3;}
_filtered {font-family:"Comic Sans MS";panose-1:3 15 7 2 3 3 2 2 2 4;}
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:"Calibri", "sans-serif";}
a:link, span.MsoHyperlink
        {color:blue;text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {margin:0in;margin-bottom:.0001pt;font-size:8.0pt;font-family:"Tahoma", "sans-serif";}
span.EmailStyle17
        {font-family:"Calibri", "sans-serif";color:windowtext;}
span.BalloonTextChar
        {font-family:"Tahoma", "sans-serif";}
.MsoChpDefault
        {}
_filtered {margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {}
-->
</STYLE>
<DIV class=Section1>
<P class=MsoNormal>I am modeling a building with multiple wall types therefore I have 3 shells per floor. I am trying to figure out how to have the adjacent walls between shells be modeled as interior instead of exterior. In one of spot they came out as interior, but I am not sure how I did it. I am trying to do as much in the wizard as possible. Does anyone know how to do this??</P>
<P class=MsoNormal> </P>
<P class=MsoNormal>Thanks for your help.</P>
<P class=MsoNormal> </P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Comic Sans MS'; COLOR: blue; FONT-SIZE: 10pt">Sheri Rocha, P.E.</SPAN><SPAN style="FONT-FAMILY: 'Times New Roman', 'serif'; FONT-SIZE: 12pt"> </SPAN><SPAN style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 12pt">, </SPAN><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: #007a37; FONT-SIZE: 10pt">LEED<SUP>TM </SUP>AP</SPAN><SPAN style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 12pt"><BR></SPAN><SPAN style="FONT-FAMILY: 'Comic Sans MS'; COLOR: black; FONT-SIZE: 10pt">Senior Mechanical Engineer</SPAN><SPAN style="FONT-FAMILY: 'Times New Roman', 'serif'; FONT-SIZE: 12pt"> <BR></SPAN><SPAN style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 10pt"><A href="mailto:srocha@mkkeng.com" rel=nofollow target=_blank ymailto="mailto:srocha@mkkeng.com"><SPAN style="FONT-FAMILY: 'Times New Roman', 'serif'; COLOR: blue">srocha@mkkeng.com</SPAN></A></SPAN><SPAN style="FONT-FAMILY: 'Times New Roman', 'serif'; FONT-SIZE: 12pt">
<BR></SPAN><U><SPAN style="FONT-FAMILY: 'Comic Sans MS'; COLOR: blue; FONT-SIZE: 10pt"><A href="http://www.mkkeng.com/" rel=nofollow target=_blank><SPAN style="FONT-FAMILY: 'Times New Roman', 'serif'; COLOR: blue">www.mkkeng.com</SPAN></A></SPAN></U><SPAN style="FONT-FAMILY: 'Times New Roman', 'serif'; FONT-SIZE: 12pt"> </SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: Webdings; COLOR: green; FONT-SIZE: 18pt">P</SPAN><SPAN style="FONT-FAMILY: 'Gill Sans MT', 'sans-serif'; COLOR: green"> </SPAN><SPAN style="FONT-FAMILY: 'Gill Sans MT', 'sans-serif'; COLOR: green; FONT-SIZE: 8pt">Save a Tree. Don't print this e-mail unless necessary.</SPAN></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; FONT-SIZE: 10pt"> </SPAN></P>
<P class=MsoNormal><IMG id=Picture_x0020_1 border=0 src="cid:1.2105084858@web52810.mail.re2.yahoo.com" width=109 height=75></P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 10pt">7600 E. Orchard Road</SPAN> <BR><SPAN style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 10pt">Suite 250-S</SPAN> <BR><SPAN style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 10pt">Greenwood Village, CO. 80111</SPAN> <BR><SPAN style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 10pt">Direct: 303-796-6062</SPAN> <BR><SPAN style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 10pt">Main: 303-796-6000</SPAN> <BR><SPAN style="FONT-FAMILY: 'Comic Sans MS'; FONT-SIZE: 10pt">Fax: 303-796-6099</SPAN> </P>
<P class=MsoNormal> </P>
<P class=MsoNormal><SPAN style="FONT-FAMILY: 'Arial', 'sans-serif'; COLOR: gray; FONT-SIZE: 10pt">CONFIDENTIALITY NOTICE: This e-mail and any attached file(s) are intended only for the use of the individual or entity to whom or to which it is addressed and may contain information that is privileged, confidential, proprietary, and trade secret. If the reader of this message is not the intended recipient or an employee or agent responsible for delivering the message to the intended recipient, you are hereby notified that any dissemination, distribution, or reproduction of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately and discard the original message and any attachment(s).</SPAN></P>
<P class=MsoNormal> </P></DIV></DIV></DIV><!-- cg2.c2.mail.re1.yahoo.com compressed/chunked Thu Oct 29 17:19:26 PDT 2009 --></div><br>
</body></html>