John,<div><br></div><div>Editing zones in detail mode is not as bad as it may initially seem.</div><div><br></div><div>The easiest way to do it is to go to 2D view, and then switch to polygon view so that you can see the polygons of all your zones on the screen at once.</div>
<div><br></div><div>Then, select the zone you want to edit in the tree to the left.</div><div><br></div><div>Select edit in the pop-up toolbar</div><div><br></div><div>now you can move vertexes and add vertexes just like you did when you created the zones, BUT a few things to be cautious of:</div>
<div><br></div><div>1.  If you move vertex 1, when you go back to regular 2D mode or 3D mode, you&#39;ll notice that your zone has moved.  If at all possible, leave vertex 1 in the same place.</div><div>2.  If you subtract vertexes, walls that refer to higher vertexes will lose a reference, and you will get an error.  Be careful when subtracting vertexes.</div>
<div>3.  When you add vertexes, you&#39;ll notice that your walls refer to vertexes by number and may shift positions.</div><div><br></div><div>When you edit polygons this way, the Smirror polygon is also automatically changed.</div>
<div><br></div><div>That said, when I started using eQuest, if I had major zone changes to make, I usually went back to the wizard mode, and re-entered all post-wizard stuff.</div><div><br></div><div>Hope this helps,</div>
<div><br></div><div>--</div><div>Karen Walkerman</div><div><br></div><div><br><div class="gmail_quote">On Thu, Nov 5, 2009 at 9:44 PM, John Smith <span dir="ltr">&lt;<a href="mailto:sturdy.smith@gmail.com">sturdy.smith@gmail.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">Hi all,<div><br></div><div>Its bit urgent....please reply me asap...</div><div><br></div><div>I am trying to edit zones in detail wizard for a particular floor. Can any one tell me is there any simple and quick way to edit zones in detail wizard??</div>

<div><br></div><div>For interior floors I can see that there is a space polygon with name E16 Space Polygon - SMirro and from the name I feel its a mirror for space polygons...Can anyone explain why is it creating a different space polygon for interior floors ??Is it necessary to create these space polygons along with other space polygons for interior floors....</div>

<div><br></div><div>Please guide me with step by step procedure to edit zones in detail wizard....</div><div><br></div><div>Thanks,</div><div>Smith.</div><font color="#888888"><div><br></div>
</font><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>