<div>Oleksandra,</div>
<div> </div>
<div>This might help explain things:</div>
<div> </div>
<div>SV-A - System Design Parameters</div>
<div>This report is based on your inputs to the program for the selected Systems (in your case PVVT.)  </div>
<div> </div>
<div>Cooling Capacity & Heating Capacity values reported is either the value that you entered for your inputs at the system level, or it is computed by the SYSTEMS program from the peak cooling load.  (Peak = Sens + Lat)  If the capacity is input at the zone level then the value reported at the system level (top of report) will be zero.</div>

<div> </div>
<div>SS-A - System Monthly <strong>Loads</strong> Summary</div>
<div>The loads shown in this report are the <u>sum</u> of zone-level loads and the central air-handling-unit loads.  Zone level loads are not shown in this report.  This report is good for comparing monthly heating and cooling <u>needs </u>of the HVAC system (needs is the key word here, because it what the 'rooms are calling for' to the system to provide.)  The DX cooling loads for your PVVT system are reported in this report but these loads do not get passed on to the PLANT program.</div>

<div> </div>
<div>To answer your question you cannot compare the two reports to be equal, because one reports capacity values and the other (SS-A) reports load values.  Capacity and loads are two different things.  The two reports you are looking at should be used in support of each other for verification of your model, not in comparison to each other.  As far as your issue with the heating and cooling capacity being reported equal to each other in SV-A report, this is probably based on what you input for your equipment capacities.  </div>

<div> </div>
<div>if you have more questions feel free to contact me.</div>
<div> </div>
<div>Pasha</div>
<div> </div>
<div class="gmail_quote">On Wed, Nov 4, 2009 at 9:22 AM, Oleksandra Onisko <span dir="ltr"><<a href="mailto:OOnisko@mcw.com">OOnisko@mcw.com</a>></span> wrote:<br>
<blockquote style="BORDER-LEFT: #ccc 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex" class="gmail_quote">
<div lang="EN-US" vlink="purple" link="blue">
<div>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Hi All, </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">I am looking at the simulation output reports, specifically at the SS-A: System Loads Summary and SV-A System Design Parameters.  The peak heating and cooling loads are shown in the SS-A report and the system capacities are shown in the SV-A report. The SV-A report shows the heating capacity being equal to the cooling capacity which does not match the SS-A report and does not seems right.  Any ideas about this? I am looking at PVVT systems. </span></font></p>

<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"> </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt">Thanks, </span></font></p>
<p class="MsoNormal"><font size="2" face="Arial"><span style="FONT-FAMILY: Arial; FONT-SIZE: 10pt"> </span></font></p>
<p class="MsoNormal"><strong><b><font color="#4d4d4d" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: #4d4d4d; FONT-SIZE: 10pt">Oleksandra Onisko</span></font></b></strong><font color="#4d4d4d" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: #4d4d4d; FONT-SIZE: 8pt"> LEED AP </span></font></p>

<p class="MsoNormal"><i><font color="#4d4d4d" size="1" face="Arial"><span style="FONT-STYLE: italic; FONT-FAMILY: Arial; COLOR: #4d4d4d; FONT-SIZE: 9pt">EIT</span></font></i><font color="#4d4d4d" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: #4d4d4d; FONT-SIZE: 9pt"></span></font></p>

<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p>
<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"><a title="http://www.mcw.com/
Click here to visit www.mcw.com" href="http://www.mcw.com/" target="_blank"><em><b><i><font title="http://www.mcw.com/" color="green" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: green; FONT-SIZE: 10pt; FONT-WEIGHT: bold; TEXT-DECORATION: none">MCW Consultants Ltd. </span></font></i></b></em></a></span></font></p>

<p class="MsoNormal"><em><i><font color="#4d4d4d" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: #4d4d4d; FONT-SIZE: 10pt">600-156 Front Street</span></font></i></em><em><i><font color="#4d4d4d" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: #4d4d4d; FONT-SIZE: 10pt"> West <br>
Toronto, ON M5J 2L6</span></font></i></em><em><i><font color="#4d4d4d" size="2" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: #4d4d4d; FONT-SIZE: 10pt"> </span></font></i></em><i><font color="#4d4d4d" size="2" face="Arial"><span style="FONT-STYLE: italic; FONT-FAMILY: Arial; COLOR: #4d4d4d; FONT-SIZE: 10pt"><br>
<em><i><font face="Arial"><span style="FONT-FAMILY: Arial">Phone 416-598-2920 </span></font></i></em><br><em><i><font face="Arial"><span style="FONT-FAMILY: Arial">Fax 416-598-5394 </span></font></i></em></span></font></i></p>

<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p>
<p class="MsoNormal"><i><font color="#4d4d4d" size="1" face="Arial"><span style="FONT-STYLE: italic; FONT-FAMILY: Arial; COLOR: #4d4d4d; FONT-SIZE: 8pt">This e-mail may be privileged and confidential. Any unauthorized use is strictly prohibited. If you received this e-mail in error, please contact the sender directly. </span></font></i><font color="#4d4d4d" size="1" face="Arial"><span style="FONT-FAMILY: Arial; COLOR: #4d4d4d; FONT-SIZE: 8pt"></span></font></p>

<p class="MsoNormal"><font size="3" face="Times New Roman"><span style="FONT-SIZE: 12pt"> </span></font></p></div></div><br>_______________________________________________<br>Equest-users mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>